Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

DCE appliance attempting to login to SNMP interfaces on APC UPS & PDUs

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE appliance attempting to login to SNMP interfaces on APC UPS & PDUs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:57 PM . Last Modified: ‎2024-04-07 11:15 PM

0 Likes
5
2270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:57 PM . Last Modified: ‎2024-04-07 11:15 PM

DCE appliance attempting to login to SNMP interfaces on APC UPS & PDUs

The logs on our APC UPS' & PDUs are showing failed login attempts every hour originating from our DCE appliance. 
The devices are all providing correct sensor data  and there are no scheduled device discoveries - I 'm really curious what process on the DCE appliance is attempting  to connect. any ideas?

08/17/2017 08:36:57 System: Detected an unauthorized user attempting to access the SNMP interface from  < IP of DCE server>
08/17/2017 08:36:57 System: Detected an unauthorized user attempting to access the SNMP interface from  < IP of DCE server>
08/17/2017 08:36:55 System: Detected an unauthorized user attempting to access the SNMP interface from  < IP of DCE server>
08/17/2017 08:36:55 System: Detected an unauthorized user attempting to access the SNMP interface from  < IP of DCE server>
08/17/2017 08:36:53 System: Detected an unauthorized user attempting to access the SNMP interface from  < IP of DCE server>
08/17/2017 08:36:53 System: Detected an unauthorized user attempting to access the SNMP interface from  < IP of DCE server>
08/17/2017 08:36:51 System: Detected an unauthorized user attempting to access the SNMP interface from  < IP of DCE server>
08/17/2017 08:36:51 System: Detected an unauthorized user attempting to access the SNMP interface from < IP of DCE server>
08/17/2017 07:36:54

System: Detected an unauthorized user attempting to access the SNMP interface from < IP of DCE server>

etc.....

(CID:123349285)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:58 PM . Last Modified: ‎2024-04-07 11:15 PM

0 Likes
0
2272
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:58 PM . Last Modified: ‎2024-04-07 11:15 PM

John,

Thank you for providing a log of the events.  Since this is occurring every hour, this would be priority scanning trying to take place.  Priority scanning needs WRITE snmp access to be able to set the Data Center Expert server as the priority scanning trap receiver (not visible via NMC GUI) on the NMC.

Please check the following:

Ensure that priority scanning is causing this: Data Center Expert Desktop Client > Device > SNMP Device Communication Settings > Device Scan Settings > Check the box for the device > Edit Device Scan Settings.  The priority scanning checkbox should be checked.

On this same screen you can see the write community string that is defined.  Ensure that this is matching a write community string that is defined on the device.

Additional information on priority scanning can be found in the knowledge base: http://www.apc.com/us/en/faqs/FA271584/

Best Regards,

Cory

(CID:123349313)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:57 PM . Last Modified: ‎2024-04-07 11:15 PM

0 Likes
1
2272
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:57 PM . Last Modified: ‎2024-04-07 11:15 PM

Hi John,

 

DCE should only use incorrect community names if it was provided with them. Working on just this device to start, take a look at the SNMPdevice communications settings and make sure both read and write community names are correct and match that of the card:

Assuming your normal scans are 5 minutes or so and if this is only happening once an hour, it is possible that the priority scanning option which may try to re-write itself every hour is unable to do so. On the device itself, make sure the community name is not specifically associated with an IP. Perhaps test here as well by unchecking the priority scanning option for a period of an hour or 2 to see if the issue remains.

What version of DCE are you using?

What firmware revision is on this device?

What is this particular device?

How many community names are in use?

Is this SNMP V1 or V3?

 

Thanks,

Steve

 

 

 

(CID:123349307)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:57 PM . Last Modified: ‎2024-04-07 11:15 PM

In response to DCIM_Support
0 Likes
0
2272
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:57 PM . Last Modified: ‎2024-04-07 11:15 PM

P.S., turning off priority scanning will only allow DCE to alert when it scans the device and not immediately when an issue on the device occurs. That's why it should only be for a test period.

(CID:123349324)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:58 PM . Last Modified: ‎2024-04-07 11:15 PM

0 Likes
0
2273
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:58 PM . Last Modified: ‎2024-04-07 11:15 PM

John,

Thank you for providing a log of the events.  Since this is occurring every hour, this would be priority scanning trying to take place.  Priority scanning needs WRITE snmp access to be able to set the Data Center Expert server as the priority scanning trap receiver (not visible via NMC GUI) on the NMC.

Please check the following:

Ensure that priority scanning is causing this: Data Center Expert Desktop Client > Device > SNMP Device Communication Settings > Device Scan Settings > Check the box for the device > Edit Device Scan Settings.  The priority scanning checkbox should be checked.

On this same screen you can see the write community string that is defined.  Ensure that this is matching a write community string that is defined on the device.

Additional information on priority scanning can be found in the knowledge base: http://www.apc.com/us/en/faqs/FA271584/

Best Regards,

Cory

(CID:123349313)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:58 PM . Last Modified: ‎2024-04-07 11:15 PM

0 Likes
0
2272
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:58 PM . Last Modified: ‎2024-04-07 11:15 PM

Thanks all - priority scanning and incorrect SNMP permissions on the devices was the cause.

(CID:123997025)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:58 PM . Last Modified: ‎2023-10-22 01:22 AM

0 Likes
0
2272
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:58 PM . Last Modified: ‎2023-10-22 01:22 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore