DCE and AP7821 Communication Lost

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE and AP7821 Communication Lost
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:56 AM . Last Modified: ‎2024-04-08 11:30 PM

0 Likes
10
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:56 AM . Last Modified: ‎2024-04-08 11:30 PM

DCE and AP7821 Communication Lost

Hi Team, 

Just want to gather some suggestion for the question as listed above.

Setup:

DCE 7.2.5 polling around 100 device. 

Rack PDU AP7821 was using firmware version v3.7.3 connect through customer network

There are no frequent communication lost from these PDUs before this.

 

Problem description: 

DCE having lost communication with 4 of the PDU units, and restore itself. The issue repeat on and off many times in a day

 

Action taken:

-reboot rack PDU

-reboot DCE server

-check rack PDU log, no suspicious error found, but having few error like "System: Detected an unauthorized user attempting to access the SNMP interface.."

-able to ping and access Web interface for the PDU.

 

Any ideas?

Thanks,

Law

 

 

(CID:106892297)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:56 AM . Last Modified: ‎2024-04-08 11:30 PM

0 Likes
2
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:56 AM . Last Modified: ‎2024-04-08 11:30 PM

I would suggest updating the units firmware to the latest revision which is 3.9.2 and can be found at http://www.apc.com/shop/us/en/products/Switched-Metered-Rack-Power-Distribution-Unit-Firmware-Revisi...

(CID:106892300)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:56 AM . Last Modified: ‎2024-04-08 11:30 PM

In response to DCIM_Support
0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:56 AM . Last Modified: ‎2024-04-08 11:30 PM

I also now noticed your DCE vision is 7.2.5 and the latest is 7.3.1 and you can contact the support group to get the update.

(CID:106892303)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:56 AM . Last Modified: ‎2024-04-08 11:30 PM

In response to DCIM_Support
0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:56 AM . Last Modified: ‎2024-04-08 11:30 PM

Hi Maybe updating the firmware will be the last resort to solve the problem.. Thanks for the suggestion. Cheers

(CID:106892331)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:56 AM . Last Modified: ‎2024-04-08 11:30 PM

0 Likes
1
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:56 AM . Last Modified: ‎2024-04-08 11:30 PM

Hi Law,

 

When the PDU is in this state, are you able to poll it using other SNMP utilities (preferably from the same subnet as DCE)? 

Are you using SNMP version 1 or version 3?

 

You noted the error:

"System: Detected an unauthorized user attempting to access the SNMP interface.."

Does this occur every time the system loses communications? 

The error is usually accompanied by an IP or hostname. If this is not DCE's hostname, can you find that system and stop it from polling the device?

What has changed on the PDU if anything (firmware etc)?

Has anything changed on the DCE server? New discoveries that run often...possibly with different community names?


This k-base may be helpful in troubleshooting SNMP communications issues.


Steve

 

(CID:106892302)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:56 AM . Last Modified: ‎2024-04-08 11:30 PM

In response to DCIM_Support
0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:56 AM . Last Modified: ‎2024-04-08 11:30 PM

Hi Steve, 1. Didn't try with other snmp polling program or mib browser yet. Will see if it works. 2 There's an ip trying to access, but the retries from this ip is far less than the number of time of lost communication.. Will try to check which device it is. 3. No firmware update has been performed. Will check on the k base suggestions and try out. Thanks

(CID:106892330)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:56 AM . Last Modified: ‎2024-04-08 11:30 PM

0 Likes
1
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:56 AM . Last Modified: ‎2024-04-08 11:30 PM

Hi,

Are the PDU on the same network on DCE ?

Sometime is happen when DCE scan devices across wan due network latency.

You can try adjusting the SNMP Device Scan Setting ( Menu Device > SNMP device communication setting > Devices Scan Settings ) and then increase Timeout and Retries.

Hope it help you resolving the issue.

Regards

Stefano

(CID:106892308)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:57 AM . Last Modified: ‎2024-04-08 11:30 PM

In response to DCIM_Support
0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:57 AM . Last Modified: ‎2024-04-08 11:30 PM

Hi, Both DCE and pdu are in the same network. I will try on the time out and retries adjustment to check the results. Thanks

(CID:106892329)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:57 AM . Last Modified: ‎2024-04-08 11:30 PM

0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:57 AM . Last Modified: ‎2024-04-08 11:30 PM

Hi Law, I had similar problem in the past with this PDU model. Upgrading the PDU firmware to the latest firmware resolved the intermittent loss of communication issue. 

Regards,

Bala

(CID:106892345)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:57 AM . Last Modified: ‎2024-04-08 11:30 PM

0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:57 AM . Last Modified: ‎2024-04-08 11:30 PM

Hi Law!

Did you try to change ports on the switch?

I have similar issue when several devices lost communication due broken switch. We localize the problem by changing ports with other devices and then change switch to resolve problem.

(CID:106892478)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:57 AM . Last Modified: ‎2023-10-31 10:25 PM

0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:57 AM . Last Modified: ‎2023-10-31 10:25 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore