DCE Server Build: 8.2.0.239 and TLS violation
EcoStruxure IT Forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
There is no option in current DCE versions to disable specific versions of TLS. If you go to "System"-->"Server Administration Settings"-->"Server Access"-->"Security Policy",
You have a few options for security. The most stringent of which being "Future". With this setting, 1.0 and 1.1 are disabled.
Please keep in mind that if you have older APC network management cards, they may require the older versions of TLS. This is the main reason some older protocols are still available as older cards may not have the ability to be updated to use the newer protocols.
P.S. FIPS is actually the most secure but the server must be initially deployed with that setting. If you've upgraded from earlier versions, this is not an option.