Dears,
Regarding the SOAP APIs of DCE, Specially for Sensor web service.
I Know that using Sensor web service methods we can get any sensor value/measurement.
The question is, Does this service work also for virtual sensors created on DCE or only work for sensors which represent an actual device?
Thanks,
Ahmed Ashraf
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-26 06:37 AM . Last Modified: 2020-04-26 06:45 AM
Ahmed,
You should be able to pull historical data for virtual sensors in the following manner:
<soapenv:Envelope xmlns:soapenv="http://schemas.xmlsoap.org/soap/envelope/" xmlns:isx="http://www.apc.com/stdws/xsd/ISXCentralDevices-v2">
<soapenv:Header/>
<soapenv:Body>
<isx:getAllDevicesRequest>
<!--Optional:-->
<isx:locale>?</isx:locale>
</isx:getAllDevicesRequest>
</soapenv:Body>
</soapenv:Envelope>PARTIAL RESULTS (limited to only the virtual device due to length of results)<ns2:ISXCDevice xmlns:ns2="http://www.apc.com/stdws/xsd/ISXCentral/2009/10">
<ns2:ISXCNamedElement>
<ns2:ISXCElement>
<ns2:ISXCElementType>DEVICE</ns2:ISXCElementType>
<ns2:id>B1db239_nbCustomSensorEncEBAB9071</ns2:id>
</ns2:ISXCElement>
<ns2:name>Test-2</ns2:name>
</ns2:ISXCNamedElement>
<ns2:ISXCCommState>OFFLINE</ns2:ISXCCommState>
<ns2:ISXCDeviceType>UNKNOWN</ns2:ISXCDeviceType>
<ns2:hostName/>
<ns2:ipAddress/>
<ns2:location/>
<ns2:modelName>Virtual Device</ns2:modelName>
<ns2:modelNumber/>
<ns2:parentID>B1db239</ns2:parentID>
<ns2:serialNumber/>
<ns2:ISXCDeviceState>NONE</ns2:ISXCDeviceState>
<ns2:supplemental xsi:nil="true"/>
</ns2:ISXCDevice><soapenv:Envelope xmlns:soapenv="http://schemas.xmlsoap.org/soap/envelope/" xmlns:isx="http://www.apc.com/stdws/xsd/ISXCentralSensors-v2">
<soapenv:Header/>
<soapenv:Body>
<isx:getSensorsForDeviceRequest>
<isx:ISXCElementID>B1db239_nbCustomSensorEncEBAB9071</isx:ISXCElementID>
</isx:getSensorsForDeviceRequest>
</soapenv:Body>
</soapenv:Envelope>RESULTS<ns2:ISXCNamedElement>
<ns2:ISXCElement>
<ns2:ISXCElementType>SENSOR</ns2:ISXCElementType>
<ns2:id>B1db239_nbCustomSensorEncEBAB9071_CUSTOMSENSOR_40F5AB4D</ns2:id>
</ns2:ISXCElement>
<ns2:name>Test-2</ns2:name>
</ns2:ISXCNamedElement><ns2:ISXCNamedElement>
<ns2:ISXCElement>
<ns2:ISXCElementType>SENSOR</ns2:ISXCElementType>
<ns2:id>B1db239_nbCustomSensorEncEBAB9071_CUSTOMSENSOR_40F5AB4D</ns2:id>
</ns2:ISXCElement>
<ns2:name>Test-2</ns2:name>
</ns2:ISXCNamedElement><soapenv:Envelope xmlns:soapenv="http://schemas.xmlsoap.org/soap/envelope/" xmlns:isx="http://www.apc.com/stdws/xsd/ISXCentralSensors-v2">
<soapenv:Header/>
<soapenv:Body>
<isx:getHistoricalSensorDataRequest>
<!--Optional:-->
<isx:endDate>2019-10-23T03:54:37.894-04:00</isx:endDate>
<!--Optional:-->
<isx:locale></isx:locale>
<!--Optional:-->
<isx:maxDataPoints>100</isx:maxDataPoints>
<isx:ISXCElementID>B1db239_nbCustomSensorEncEBAB9071_CUSTOMSENSOR_40F5AB4D</isx:ISXCElementID>
<!--Optional:-->
<isx:startDate>2019-10-20T03:54:37.894-04:00</isx:startDate>
</isx:getHistoricalSensorDataRequest>
</soapenv:Body>
</soapenv:Envelope>RESULTS<soap:Envelope xmlns:soap="http://schemas.xmlsoap.org/soap/envelope/" xmlns:xsd="http://www.w3.org/2001/XMLSchema" xmlns:xsi="http://www.w3.org/2001/XMLSchema-instance">
<soap:Body xmlns:ns1="http://www.apc.com/stdws/xsd/ISXCentralSensors-v2">
<ns1:getHistoricalSensorDataResponse>
<ns1:ArrayOfISXCSensorData>
<ns2:ISXCSensorData xmlns:ns2="http://www.apc.com/stdws/xsd/ISXCentral/2009/10">
<ns2:timeStamp>2019-10-20T20:01:30.347-04:00</ns2:timeStamp>
<ns2:units>W</ns2:units>
<ns2:value>36.70000076293945</ns2:value>
<ns2:ISXCValueType>UNKNOWN</ns2:ISXCValueType>
</ns2:ISXCSensorData>
<ns2:ISXCSensorData xmlns:ns2="http://www.apc.com/stdws/xsd/ISXCentral/2009/10">
<ns2:timeStamp>2019-10-20T20:06:10.913-04:00</ns2:timeStamp>
<ns2:units>W</ns2:units>
<ns2:value>33.20000076293945</ns2:value>
<ns2:ISXCValueType>UNKNOWN</ns2:ISXCValueType>
</ns2:ISXCSensorData>
<ns2:ISXCSensorData xmlns:ns2="http://www.apc.com/stdws/xsd/ISXCentral/2009/10">
<ns2:timeStamp>2019-10-20T20:11:09.244-04:00</ns2:timeStamp>
<ns2:units>W</ns2:units>
<ns2:value>39.0</ns2:value>
<ns2:ISXCValueType>UNKNOWN</ns2:ISXCValueType>
</ns2:ISXCSensorData>
...100 results in total...
Kind Regards,
Cory
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-26 06:37 AM . Last Modified: 2020-04-26 06:45 AM
Ahmed,
You should be able to pull historical data for virtual sensors in the following manner:
<soapenv:Envelope xmlns:soapenv="http://schemas.xmlsoap.org/soap/envelope/" xmlns:isx="http://www.apc.com/stdws/xsd/ISXCentralDevices-v2">
<soapenv:Header/>
<soapenv:Body>
<isx:getAllDevicesRequest>
<!--Optional:-->
<isx:locale>?</isx:locale>
</isx:getAllDevicesRequest>
</soapenv:Body>
</soapenv:Envelope>PARTIAL RESULTS (limited to only the virtual device due to length of results)<ns2:ISXCDevice xmlns:ns2="http://www.apc.com/stdws/xsd/ISXCentral/2009/10">
<ns2:ISXCNamedElement>
<ns2:ISXCElement>
<ns2:ISXCElementType>DEVICE</ns2:ISXCElementType>
<ns2:id>B1db239_nbCustomSensorEncEBAB9071</ns2:id>
</ns2:ISXCElement>
<ns2:name>Test-2</ns2:name>
</ns2:ISXCNamedElement>
<ns2:ISXCCommState>OFFLINE</ns2:ISXCCommState>
<ns2:ISXCDeviceType>UNKNOWN</ns2:ISXCDeviceType>
<ns2:hostName/>
<ns2:ipAddress/>
<ns2:location/>
<ns2:modelName>Virtual Device</ns2:modelName>
<ns2:modelNumber/>
<ns2:parentID>B1db239</ns2:parentID>
<ns2:serialNumber/>
<ns2:ISXCDeviceState>NONE</ns2:ISXCDeviceState>
<ns2:supplemental xsi:nil="true"/>
</ns2:ISXCDevice><soapenv:Envelope xmlns:soapenv="http://schemas.xmlsoap.org/soap/envelope/" xmlns:isx="http://www.apc.com/stdws/xsd/ISXCentralSensors-v2">
<soapenv:Header/>
<soapenv:Body>
<isx:getSensorsForDeviceRequest>
<isx:ISXCElementID>B1db239_nbCustomSensorEncEBAB9071</isx:ISXCElementID>
</isx:getSensorsForDeviceRequest>
</soapenv:Body>
</soapenv:Envelope>RESULTS<ns2:ISXCNamedElement>
<ns2:ISXCElement>
<ns2:ISXCElementType>SENSOR</ns2:ISXCElementType>
<ns2:id>B1db239_nbCustomSensorEncEBAB9071_CUSTOMSENSOR_40F5AB4D</ns2:id>
</ns2:ISXCElement>
<ns2:name>Test-2</ns2:name>
</ns2:ISXCNamedElement><ns2:ISXCNamedElement>
<ns2:ISXCElement>
<ns2:ISXCElementType>SENSOR</ns2:ISXCElementType>
<ns2:id>B1db239_nbCustomSensorEncEBAB9071_CUSTOMSENSOR_40F5AB4D</ns2:id>
</ns2:ISXCElement>
<ns2:name>Test-2</ns2:name>
</ns2:ISXCNamedElement><soapenv:Envelope xmlns:soapenv="http://schemas.xmlsoap.org/soap/envelope/" xmlns:isx="http://www.apc.com/stdws/xsd/ISXCentralSensors-v2">
<soapenv:Header/>
<soapenv:Body>
<isx:getHistoricalSensorDataRequest>
<!--Optional:-->
<isx:endDate>2019-10-23T03:54:37.894-04:00</isx:endDate>
<!--Optional:-->
<isx:locale></isx:locale>
<!--Optional:-->
<isx:maxDataPoints>100</isx:maxDataPoints>
<isx:ISXCElementID>B1db239_nbCustomSensorEncEBAB9071_CUSTOMSENSOR_40F5AB4D</isx:ISXCElementID>
<!--Optional:-->
<isx:startDate>2019-10-20T03:54:37.894-04:00</isx:startDate>
</isx:getHistoricalSensorDataRequest>
</soapenv:Body>
</soapenv:Envelope>RESULTS<soap:Envelope xmlns:soap="http://schemas.xmlsoap.org/soap/envelope/" xmlns:xsd="http://www.w3.org/2001/XMLSchema" xmlns:xsi="http://www.w3.org/2001/XMLSchema-instance">
<soap:Body xmlns:ns1="http://www.apc.com/stdws/xsd/ISXCentralSensors-v2">
<ns1:getHistoricalSensorDataResponse>
<ns1:ArrayOfISXCSensorData>
<ns2:ISXCSensorData xmlns:ns2="http://www.apc.com/stdws/xsd/ISXCentral/2009/10">
<ns2:timeStamp>2019-10-20T20:01:30.347-04:00</ns2:timeStamp>
<ns2:units>W</ns2:units>
<ns2:value>36.70000076293945</ns2:value>
<ns2:ISXCValueType>UNKNOWN</ns2:ISXCValueType>
</ns2:ISXCSensorData>
<ns2:ISXCSensorData xmlns:ns2="http://www.apc.com/stdws/xsd/ISXCentral/2009/10">
<ns2:timeStamp>2019-10-20T20:06:10.913-04:00</ns2:timeStamp>
<ns2:units>W</ns2:units>
<ns2:value>33.20000076293945</ns2:value>
<ns2:ISXCValueType>UNKNOWN</ns2:ISXCValueType>
</ns2:ISXCSensorData>
<ns2:ISXCSensorData xmlns:ns2="http://www.apc.com/stdws/xsd/ISXCentral/2009/10">
<ns2:timeStamp>2019-10-20T20:11:09.244-04:00</ns2:timeStamp>
<ns2:units>W</ns2:units>
<ns2:value>39.0</ns2:value>
<ns2:ISXCValueType>UNKNOWN</ns2:ISXCValueType>
</ns2:ISXCSensorData>
...100 results in total...
Kind Regards,
Cory