Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DCE SSL certificate

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE SSL certificate
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
Mohamed_Fahmy
Mohamed_Fahmy Explorer
Explorer

Posted: ‎2020-08-31 04:36 AM

0 Likes
1
3448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-31 04:36 AM

DCE SSL certificate

Dears,

 

In a project the customer prepare SSL certificate when we tried to add it it give us that the DCE does not support Chained certificates so we found a workaround on SE website as link below 

https://www.apc.com/us/en/faqs/FA225532/

we followed the steps but we an error on step number 6 as photo below

 

SSL Certificate.png

 

We tried to add it as *.pem file and as a text but we got the same error that the SSL certificate is invaled.

 

and the same problem with the NetBotz 450 as the screenshot below

 

SSL Certificate01.pngSSL Certificate02.png

 

Thanks,

Mohamed

Labels
  • Labels:
  • Data Center Expert
  • DCIM Support
  • NetBotz
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Cory_McDonald
Cory_McDonald Champion
Champion

Posted: ‎2020-09-11 06:18 AM

1 Like
0
3401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-11 06:18 AM

@Mohamed_Fahmy,

 

When adding into the trust store you do not need the private key of that certificate.  Private keys for the root and intermediary certs should never be imported into any other system for security reasons. You must use the CSR method from DCE to generate the certificate signing request and then get it signed by the CA.  There is no way to generate your own cert/private key combo and import them into DCE.  After getting the CSR signed, you should be provided with 1 or multiple files that contain the signed server certificate, intermediary certs (if applicable) and the root CA cert.

 

You should be importing the root cert and intermediary cert ONE at a time, repeating the process for each additional certificate:

 

-----BEGIN CERTIFICATE-----

....

-----END CERTIFICATE-----

 

Do not add the server certificate into the Server SSL Certificates section, as that needs to be added after the root and intermediary certs are added.  This is done within the desktop client under: System > Server Administration Settings > Web Server > Modify Certificate > Add Certificate.  You can then paste in the certificate and add it:

 

-----BEGIN CERTIFICATE-----

....

-----END CERTIFICATE-----

 

Regards,

Cory

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Cory_McDonald
Cory_McDonald Champion
Champion

Posted: ‎2020-09-11 06:18 AM

1 Like
0
3402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-11 06:18 AM

@Mohamed_Fahmy,

 

When adding into the trust store you do not need the private key of that certificate.  Private keys for the root and intermediary certs should never be imported into any other system for security reasons. You must use the CSR method from DCE to generate the certificate signing request and then get it signed by the CA.  There is no way to generate your own cert/private key combo and import them into DCE.  After getting the CSR signed, you should be provided with 1 or multiple files that contain the signed server certificate, intermediary certs (if applicable) and the root CA cert.

 

You should be importing the root cert and intermediary cert ONE at a time, repeating the process for each additional certificate:

 

-----BEGIN CERTIFICATE-----

....

-----END CERTIFICATE-----

 

Do not add the server certificate into the Server SSL Certificates section, as that needs to be added after the root and intermediary certs are added.  This is done within the desktop client under: System > Server Administration Settings > Web Server > Modify Certificate > Add Certificate.  You can then paste in the certificate and add it:

 

-----BEGIN CERTIFICATE-----

....

-----END CERTIFICATE-----

 

Regards,

Cory

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore