DCE: SNMP Trap Direct Polling

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE: SNMP Trap Direct Polling
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:17 AM . Last Modified: ‎2024-04-10 12:36 AM

0 Likes
6
1116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:17 AM . Last Modified: ‎2024-04-10 12:36 AM

DCE: SNMP Trap Direct Polling

Hi,

I'd like to receive immediate notification via DCE in case of threshold violation allowing the StruxureWare Data Center Expert server to immediately poll an APC SNMP device in response to a trap, rather than waiting to poll the device during the normal scanning interval.... I've "flagged" "Register for Priority Scanning" in DCE and activated TRAPS on NMC: could you help me to double check if I'm right in these configuration settings or I'm missing something ?

Thx&Brgds,

Massimo

   

(CID:94602939)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:17 AM . Last Modified: ‎2024-04-10 12:36 AM

0 Likes
0
1116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:17 AM . Last Modified: ‎2024-04-10 12:36 AM

Hi Massimo, we will have a look, stay tuned!

(CID:94602998)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:17 AM . Last Modified: ‎2024-04-10 12:36 AM

0 Likes
2
1116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:17 AM . Last Modified: ‎2024-04-10 12:36 AM

Hi Massimo,

It sounds like you are on the right track. However I cannot tell where you have set the "priority scanning flag"?.

1) It must be set on the APC Lan of the DCE server. Some information can be found Private (LAN2) DHCP Discovery tab

In the documentation you will see that the flag must be set before the device is discovered in DCE. If the device is already in DCE you would have to discover it again after setting the flag.

Then make sure to have the right "Write community" name set on both DCE and device.

2) It must also be set on the device itself. More information can be found Device Scan Settings option 8052735a

 

 

(CID:94603034)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:18 AM . Last Modified: ‎2024-04-10 12:36 AM

In response to DCIM_Support
0 Likes
0
1116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:18 AM . Last Modified: ‎2024-04-10 12:36 AM

That first link would seem to indicate you need a second NIC and enable it for trap reception, is that correct? The second link only talk about APC devices sending traps, are other non APC device traps applicable?

(CID:95355735)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:18 AM . Last Modified: ‎2024-04-10 12:36 AM

In response to DCIM_Support
0 Likes
0
1116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:18 AM . Last Modified: ‎2024-04-10 12:36 AM

Hi Chad, You are right. You would need a second NIC to function as APC Lan which is a separate management LAN that is used for e.g. management device Currently there is not support for other traps than traps coming from APC devices. This has also been discussed earlier in this thread: http://dcimsupport.apc.com/questions/93915440

(CID:95355742)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:18 AM . Last Modified: ‎2024-04-10 12:36 AM

0 Likes
0
1116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:18 AM . Last Modified: ‎2024-04-10 12:36 AM

Hi Massimo,

As long as you're dealing with an APC device and NMC firmware above 2.7.4 I believe it is, Setting priority scanning will set a hidden trap receiver within the NMC and that card should then send a trap to DCE which in turn polls the device immediately. It is not required that the device is on the private LAN. You do not have to enable SNMP or traps specifically. This works on both NIC cards as long as ports are open and the threshold you're referring to is on the device and NOT a threshold set on DCE. Any thresholds set specifically in DCE must wait for a poll. Please note that this does not refer to thresholds set by using the APC mass configuration option.

The only way to be sure it is configured properly is to test. If the NMC you're using has a temperature probe or dry contacts, set a threshold that is already broken. If it's 75 degrees, set a high threshold on the card for 65 degrees. If it is not a critical system, maybe a smaller UPS, pull the plug to force it to battery. 

(CID:96043073)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:18 AM . Last Modified: ‎2023-10-31 10:44 PM

0 Likes
0
1116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:18 AM . Last Modified: ‎2023-10-31 10:44 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore