DCE SNMP AGENT OPTION IN SERVER ACCESS TAB

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE SNMP AGENT OPTION IN SERVER ACCESS TAB
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:04 PM . Last Modified: ‎2024-04-09 04:18 AM

0 Likes
9
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:04 PM . Last Modified: ‎2024-04-09 04:18 AM

DCE SNMP AGENT OPTION IN SERVER ACCESS TAB

I want to integrate the DCE server as snmp agent  with my server to get alarm and status query. Is it possible with the option shown in DCE server administrator setting>server access>snmp server. 

(CID:99156926)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:05 PM . Last Modified: ‎2024-04-09 04:18 AM

0 Likes
6
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:05 PM . Last Modified: ‎2024-04-09 04:18 AM

Hi Atul,

 

The SNMP option you're referencing simply enables the operating system's SNMP agent. You would be able to poll a few OIDs based on the CentOS operating system but you would get no data about the monitored nodes and you would get no alerts.

 

If you're looking to get alarms via SNMP or traps, you want to go to the Alarm Configuration menu, Network Management System Integration. You can set it up to send traps to any server you'd like. 

 

There are 2 ways to poll DCE for information about the nodes it is monitoring. There is a modbus output option if you purchase the AP95MODBUS license key. You can also use the web-API. Details available on the software downloads page at:

www.apcc.com/tools/download.

 

Steve

(CID:99156964)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:05 PM . Last Modified: ‎2024-04-09 04:18 AM

0 Likes
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:05 PM . Last Modified: ‎2024-04-09 04:18 AM

Hi Atul, thanks for posting. @community - any knowledge about that?

(CID:99156935)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:05 PM . Last Modified: ‎2024-04-09 04:18 AM

0 Likes
6
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:05 PM . Last Modified: ‎2024-04-09 04:18 AM

Hi Atul,

 

The SNMP option you're referencing simply enables the operating system's SNMP agent. You would be able to poll a few OIDs based on the CentOS operating system but you would get no data about the monitored nodes and you would get no alerts.

 

If you're looking to get alarms via SNMP or traps, you want to go to the Alarm Configuration menu, Network Management System Integration. You can set it up to send traps to any server you'd like. 

 

There are 2 ways to poll DCE for information about the nodes it is monitoring. There is a modbus output option if you purchase the AP95MODBUS license key. You can also use the web-API. Details available on the software downloads page at:

www.apcc.com/tools/download.

 

Steve

(CID:99156964)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:05 PM . Last Modified: ‎2024-04-09 04:18 AM

In response to DCIM_Support
0 Likes
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:05 PM . Last Modified: ‎2024-04-09 04:18 AM

Thanks Steve

(CID:99156972)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:05 PM . Last Modified: ‎2024-04-09 04:18 AM

In response to DCIM_Support
0 Likes
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:05 PM . Last Modified: ‎2024-04-09 04:18 AM

I checked for web service API and there download is not available for windows 7.

(CID:99156975)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:05 PM . Last Modified: ‎2024-04-09 04:18 AM

In response to DCIM_Support
0 Likes
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:05 PM . Last Modified: ‎2024-04-09 04:18 AM

Hi Atul, I'm not even sure why they have it based on different operating systems, I think it is a download page requirement. The API is not OS specific though, every download (for this anyway) is the same and contains info on how to write the code. Steve

(CID:99156976)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:05 PM . Last Modified: ‎2024-04-09 04:18 AM

In response to DCIM_Support
0 Likes
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:05 PM . Last Modified: ‎2024-04-09 04:18 AM

Hi Gents - i am having the same issue and i hope you guys can assist me. To latch onto Atul's comment, so if i need to monitor a server, what do i need to do? My understanding from your comments is that i need to discover it with DCE and then configure the alarm notifications ? Is there any link that i can read to better understand? Thank you so much for your support - much appreciated.

(CID:110006810)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:05 PM . Last Modified: ‎2024-04-09 04:18 AM

In response to DCIM_Support
0 Likes
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:05 PM . Last Modified: ‎2024-04-09 04:18 AM

Yusuf, This should probably have been a different thread as this thread is about monitoring DCE using SNMP and not about discovering another server using DCE. I can say however that DCE can monitor most anything using SNMP and assuming the server has SNMP enabled, you can simply discover it in DCE. This knowledge base document may halp if you need to know how to discover devices in DCE: http://www.apc.com/us/en/faqs/index?page=content&id=FA177081 Steve.

(CID:110006846)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:05 PM . Last Modified: ‎2024-04-09 04:18 AM

In response to DCIM_Support
0 Likes
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:05 PM . Last Modified: ‎2024-04-09 04:18 AM

My sincere apologies Steve - I will start a new thread. Kind regards Yusuf

(CID:110006921)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:06 PM . Last Modified: ‎2023-10-31 10:44 PM

0 Likes
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:06 PM . Last Modified: ‎2023-10-31 10:44 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.