Does Mass Configuration on DCE for APC devices require the FTP or SCP port? If a customer is only using SNMP V3 do they lose the ability to mass configure?
(CID:129410149)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:36 PM . Last Modified: 2024-04-05 12:31 AM
Yes, apc snmp device config creates a custom config.ini and uploads it to the device via FTP or SCP protocol, they could possibly use a different port though.
DCE cannot use SNMP or any other method to make config changes to the device. The only exception to this is Outlet Control on APC pdus which uses an snmp write to change the state of the outlet.
(CID:129410161)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:36 PM . Last Modified: 2023-10-22 01:17 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.