Hi Support / All,
We are seeing a strange issue with discovery of a Smart-UPS 3000 with embedded NMC into DCE, coming back with the 'Device Definition File Transfer Failed' alert in DCE.
All the usual suspects are checked ok:
In addition the network has been checked:
I have even disabled all NMC users and created just the one admin user 'apc' - with FTP access and matching DCE credentials.
The below network trace has been carried out between DCE and NMC during DCE discovery process (IP addresses and username / password obfuscated):

Note the 'Command Unrecognised / Command Not Implemented' response from the NMC after DCE requests SYST and the file ddf.zip
The UPS NMC logs indicate the DCE server successfully logging in, and then back out, of the UPS NMC.
DCE version 7.3.1
UPS: Smart-UPS SRT 5000
SKU: SRT5KRMXLW-HW
UPS Firmware Rev: 04.0 (ID1013)
NMC Model: AP9537SUM
Firmware: aos and sumx version 6.0.7, bootmon v1.0.2
Any known firmware issues with this model, or other suggestions on this one as I am out of ideas?
Many Thanks,
David
(CID:106207995)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:55 AM . Last Modified: 2024-04-08 11:49 PM
There is a much better/newer firmware revision available for that NMC. I would suggest manually updating it via the firmware's installer and once updated to the current revision then try adding it into your DCE.
Edit. The newest revision of firmware for this model of NMC is 6.4.0 and uses the same firmware as APC AP9630/9631 cards (the AP9537 is just a built in variant of them)
(CID:106208000)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:55 AM . Last Modified: 2024-04-08 11:49 PM
Thanks Michael - I'll give that a try and see if it makes any difference
(CID:106208207)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:55 AM . Last Modified: 2024-04-08 11:49 PM
I have the same issue, brand new Symmetra 250kW, I am waiting for my network team to perform the network scan.
(CID:106208241)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:55 AM . Last Modified: 2023-10-31 10:26 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.