DCE Backup Mount fails

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE Backup Mount fails
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
112
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:35 PM . Last Modified: β€Ž2024-04-05 04:52 AM

0 Likes
7
1510
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:35 PM . Last Modified: β€Ž2024-04-05 04:52 AM

DCE Backup Mount fails

After several months of success I can no longer mount a network share for DCE backups. The server does have GPO requiring NTLMv2 and 128 bit security. I am using 7.4.3.26 which gives me NTLMv2 as a protocol option.

I downloaded the logs as suggested in another thread. They show:

cifs_mount failed w/return code = -112

I have confirmed that the credentials specified are correct and that the user can access the share outside of DCE. In addition modifying the previously functional backup I have tried creating a new one.

Unable to find what return code -112 may be. Any assistance is appreciated.

 

Ed

(CID:125209683)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:35 PM . Last Modified: β€Ž2024-04-05 04:52 AM

0 Likes
2
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:35 PM . Last Modified: β€Ž2024-04-05 04:52 AM

pretty sure this is related to SMB v1 being disabled in microsoft server OS' recently.  if this is the case, your only option is to find a server with smb v1 still enabled or use a NFS mount instead.   

 

hopefully a fix on the DCE end will be available in a future release.

(CID:125209702)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:36 PM . Last Modified: β€Ž2024-04-05 04:52 AM

In response to DCIM_Support
0 Likes
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:36 PM . Last Modified: β€Ž2024-04-05 04:52 AM

Good Call Andrew, 

 

Ed, if you can verify they're using SMB2, I do have an enhancement request in the system and will add this post to the request.

 

Thanks,

Steve 

(CID:125210005)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:36 PM . Last Modified: β€Ž2024-04-05 04:52 AM

In response to DCIM_Support
0 Likes
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:36 PM . Last Modified: β€Ž2024-04-05 04:52 AM

Awesome. Thanks. I'm going to proceed with attempting an NFS mount until an update is available.

 

Ed

(CID:125212618)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:36 PM . Last Modified: β€Ž2024-04-05 04:52 AM

0 Likes
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:36 PM . Last Modified: β€Ž2024-04-05 04:52 AM

Hi Ed Krimmer,

See similar discussions on this topic , which have already been discussed repeatedly at DCIM Support.

With respect.

(CID:125209772)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:36 PM . Last Modified: β€Ž2024-04-05 04:52 AM

0 Likes
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:36 PM . Last Modified: β€Ž2024-04-05 04:52 AM

Yes I had read the other threads but saw no reference to the error return code I dug out of the logs. Hence my "fresh" query. 

Ed

(CID:125210129)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:36 PM . Last Modified: β€Ž2024-04-05 04:52 AM

0 Likes
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:36 PM . Last Modified: β€Ž2024-04-05 04:52 AM

Hi Ed Krimmer,

I downloaded the logs as suggested in another thread. They show:

cifs_mount failed w/return code = -112

I have confirmed that the credentials specified are correct and that the user can access the share outside of DCE. In addition modifying the previously functional backup I have tried creating a new one.

Unable to find what return code -112 may be. Any assistance is appreciated.

This is a question from the *nix world, which I will simply answer πŸ˜€. The DCE-server tries to mount your Windows resource using the mount command. According to Linux man page mount (8) this command has the following numbering of exit codes:

RETURN CODES
mount has the following return codes (the bits can be ORed):
0 success
1 incorrect invocation or permissions
2 system error (out of memory, cannot fork, no more loop devices)
4 internal mount bug
8 user interrupt
16 problems writing or locking /etc/mtab
32 mount failure
64 some mount succeeded

I.e., your mount return code -112 is a set of three errors:

112 = 64+32+16

Not very informative πŸ˜€, but to solve your problem with mounting NTLMv2 Windows resources, the DCE-server for the mount command should use the additional parameter -o sec=ntlmv2. But since the DCE-server is a closed black box, it remains only to wait for the developers to do this and publish a new DCE-release for customers.

Always glad to answer your questions.

(CID:125210147)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:36 PM . Last Modified: β€Ž2023-10-22 01:14 AM

0 Likes
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:36 PM . Last Modified: β€Ž2023-10-22 01:14 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore