Hello
In all customers where that installed DCE version 7.5 I have the same problem when I opened "Apply Firmware Updates" window.
No any devices areappears into windows where I need ro "Select Device Updates"
How I can fix it ?
Thanks
(CID:138811493)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 04:40 PM . Last Modified: 2024-04-03 04:25 AM
Dear Boris,
This means, that either the DCE-server does not have firmware updates for your devices, or your devices has the latest firmware.
A DCE-server (not a DCE-client) can obtain firmware updates for your devices in two ways.
If you have further questions, please ask.
With respect.
(CID:138811512)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 04:40 PM . Last Modified: 2024-04-03 04:25 AM
Dear Boris,
This means, that either the DCE-server does not have firmware updates for your devices, or your devices has the latest firmware.
A DCE-server (not a DCE-client) can obtain firmware updates for your devices in two ways.
If you have further questions, please ask.
With respect.
(CID:138811512)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 04:41 PM . Last Modified: 2024-04-03 04:25 AM
Hello
Many thanks for ypur answer I'll check .
Unfortunately the link of the download frimware is broken

(CID:138811546)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 04:41 PM . Last Modified: 2024-04-03 04:25 AM
Boris,
You can see in your URL that you are trying to directly access https://updates.apc.com via a web browser, which is not possible. You need to use the full link. To access and download the upgrades manually, it would be: https://download.schneider-electric.com/files?p_Archive_Name=DBUE-7H7NVA.zip&p_enDocType=Software+-+...
If you are unable to access that full link, most likely something on your network is changing the URL, such as a proxy, and preventing the access/download of the file. I have just tested the URL and the download works fine.
Kind Regards,
Cory
(CID:138811550)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 04:41 PM . Last Modified: 2024-04-03 04:25 AM
many thanks
I haven't problem with full link . My question how I get this full link ?
(CID:138811565)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 04:41 PM . Last Modified: 2024-04-03 04:24 AM
Video: How do I manually load APC and NetBotz device firmware to StruxureWare Data Center Expert?
https://www.apc.com/us/en/faqs/FA226042/
(CID:138811573)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 04:41 PM . Last Modified: 2024-04-03 04:24 AM
Dear Boris,
Tell us, please, did you solve your problem or not?
With respect.
(CID:139693913)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 04:41 PM . Last Modified: 2023-10-22 01:14 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.