Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DCE 7.9.3 - Trap severity information

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE 7.9.3 - Trap severity information
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
tjlaw
tjlaw Mentor
Mentor

Posted: ‎2024-06-10 06:49 AM

1 Like
2
1508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-10 06:49 AM

DCE 7.9.3 - Trap severity information

Dear Support, 

 

We have a question from our customer recently when they integrated DCE to send SNMP Traps to their NMS system via "Network Management Systems Integration" under DCE. According to https://www.apc.com/us/en/faqs/FA231439/ the trap sent supposed to have Alarm Severity information sent with the trap. However, no severity information was found from the trap and the trap received under the oid tree ".1.3.6.1.4.1.318.2.3"

tjlaw_0-1718027203827.png

Can anyone confirm this information is true? (No severity under trap sent). The sample received trap as follows: 

Jun 9 03:53:52 vbcpnocprdwb301 snmptrapd[16911]: 2024-06-09 03:53:52 x.x.x.x(via UDP: [x.x.x.x]:5483->[x.x.x.x]:162) TRAP, SNMP v1, community public#012#011SNMPv2-SMI::enterprises.318 Enterprise Specific Trap (746) Uptime: 212 days, 15:22:29.95#012#011SNMPv2-SMI::enterprises.318.2.3.10.0 = STRING: "Bbf5499_nbErrorCond_12940872"#011SNMPv2-SMI::enterprises.318.2.3.23.0 = STRING: "Value Too High for Too Long"#011SNMPv2-SMI::enterprises.318.2.3.1.0 = INTEGER: 6#011SNMPv2-SMI::enterprises.318.2.3.11.0 = STRING: "Bbf5499_nbSNMPEnc2C202808"#011SNMPv2-SMI::enterprises.318.2.3.24.0 = STRING: "L7-x-x-NB (x.x.x.x)"#011SNMPv2-SMI::enterprises.318.2.3.16.0 = ""#011SNMPv2-SMI::enterprises.318.2.3.25.0 = STRING: "Environmental Monitor"#011SNMPv2-SMI::enterprises.318.2.3.17.0 = STRING: "QA1818170363"#011SNMPv2-SMI::enterprises.318.2.3.20.0 = STRING: "NetBotz Rack Monitor 250"#011SNMPv2-SMI::enterprises.318.2.3.21.0 = STRING: "x.x.x.x"#011SNMPv2-SMI::enterprises.318.2.3.26.0 = STRING: "L7 SF-3"#011SNMPv2-SMI::enterprises.318.2.3.27.0 = STRING: "DCO Team"#011SNMPv2-SMI::enterprises.318.2.3.22.0 = STRING: "Bbf5499_nbSNMPEnc2C202808_MEM_HUMIDITY_5_4"#011SNMPv2-SMI::enterprises.318.2.3.28.0 = STRING: "Humidity - L7-NR-K4-TH"#011SNMPv2-SMI::enterprises.318.2.3.29.0 = STRING: "61 % RH"#011SNMPv2-SMI::enterprises.318.2.3.6.0 = INTEGER: 1717876427#011SNMPv2-SMI::enterprises.318.2.3.7.0 = INTEGER: 0#011SNMPv2-SMI::enterprises.318.2.3.30.0 = STRING: "The value of 'Humidity - L7-X-X-TH' (61 % RH) has been too high for too long."

 

BR, 

 

TJ

 

 

Labels
  • Labels:
  • Data Center Expert
  • DCIM Support
  • Product Feedback
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Cory_McDonald
Cory_McDonald Champion
Champion

Posted: ‎2024-06-12 05:41 AM

2 Likes
1
1471
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-12 05:41 AM

Hi @tjlaw,

 

The alarm severity information is not a parameter within the trap, but is the trap OID itself.  Here is some examples of the different ones:

  • 740: Informational  (741 clearing)
  • 742: Warning (743 clearing)
  • 744: Error (745 clearing)
  • 746: Critical (747 clearing)
  • 748: Failure (749 clearing)

Here is data from example alarms that I generated that you can see utilize the different trap OIDs for the different severities (in reverse of the list above):

Cory_McDonald_0-1718195535881.png

 

Within your trap data, you will need to look at the "Enterprise Specific Trap" of "746" which would correlate to a Critical alarm.

 

Jun 9 03:53:52 vbcpnocprdwb301 snmptrapd[16911]: 2024-06-09 03:53:52 x.x.x.x(via UDP: [x.x.x.x]:5483->[x.x.x.x]:162) TRAP, SNMP v1, community public#012#011SNMPv2-SMI::enterprises.318 Enterprise Specific Trap (746) Uptime: 212 days, 15:22:29.95#012#011SNMPv2-SMI::enterprises.318.2.3.10.0 = STRING: "Bbf5499_nbErrorCond_12940872"#011SNMPv2-SMI::enterprises.318.2.3.23.0 = STRING: "Value Too High for....

 

The rest of the data points (variable bindings)are pulled from other locations as defined in your example data:

 

Jun 9 03:53:52 vbcpnocprdwb301 snmptrapd[16911]: 2024-06-09 03:53:52 x.x.x.x(via UDP: [x.x.x.x]:5483->[x.x.x.x]:162) TRAP, SNMP v1, community public#012#011SNMPv2-SMI::enterprises.318 Enterprise Specific Trap (746) Uptime: 212 days, 15:22:29.95#012#011SNMPv2-SMI::enterprises.318.2.3.10.0 = STRING: "Bbf5499_nbErrorCond_12940872"#011SNMPv2-SMI::enterprises.318.2.3.23.0 = STRING: "Value Too High for Too Long"#011SNMPv2-SMI::enterprises.318.2.3.1.0 = INTEGER: 6#011SNMPv2-SMI::enterprises.318.2.3.11.0 = STRING: "Bbf5499_nbSNMPEnc2C202808"#011SNMPv2-SMI::enterprises.318.2.3.24.0 = STRING: "L7-x-x-NB (x.x.x.x)"#011SNMPv2-SMI::enterprises.318.2.3.16.0 = ""#011SNMPv2-SMI::enterprises.318.2.3.25.0 = STRING: "Environmental Monitor"#011SNMPv2-SMI::enterprises.318.2.3.17.0 = STRING: "QA1818170363"#011SNMPv2-SMI::enterprises.318.2.3.20.0 = STRING: "NetBotz Rack Monitor 250"#011SNMPv2-SMI::enterprises.318.2.3.21.0 = STRING: "x.x.x.x"#011SNMPv2-SMI::enterprises.318.2.3.26.0 = STRING: "L7 SF-3"#011SNMPv2-SMI::enterprises.318.2.3.27.0 = STRING: "DCO Team"#011SNMPv2-SMI::enterprises.318.2.3.22.0 = STRING: "Bbf5499_nbSNMPEnc2C202808_MEM_HUMIDITY_5_4"#011SNMPv2-SMI::enterprises.318.2.3.28.0 = STRING: "Humidity - L7-NR-K4-TH"#011SNMPv2-SMI::enterprises.318.2.3.29.0 = STRING: "61 % RH"#011SNMPv2-SMI::enterprises.318.2.3.6.0 = INTEGER: 1717876427#011SNMPv2-SMI::enterprises.318.2.3.7.0 = INTEGER: 0#011SNMPv2-SMI::enterprises.318.2.3.30.0 = STRING: "The value of 'Humidity - L7-X-X-TH' (61 % RH) has been too high for too long."

 

Kind Regards,

Cory

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Cory_McDonald
Cory_McDonald Champion
Champion

Posted: ‎2024-06-12 05:41 AM

2 Likes
1
1472
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-12 05:41 AM

Hi @tjlaw,

 

The alarm severity information is not a parameter within the trap, but is the trap OID itself.  Here is some examples of the different ones:

  • 740: Informational  (741 clearing)
  • 742: Warning (743 clearing)
  • 744: Error (745 clearing)
  • 746: Critical (747 clearing)
  • 748: Failure (749 clearing)

Here is data from example alarms that I generated that you can see utilize the different trap OIDs for the different severities (in reverse of the list above):

Cory_McDonald_0-1718195535881.png

 

Within your trap data, you will need to look at the "Enterprise Specific Trap" of "746" which would correlate to a Critical alarm.

 

Jun 9 03:53:52 vbcpnocprdwb301 snmptrapd[16911]: 2024-06-09 03:53:52 x.x.x.x(via UDP: [x.x.x.x]:5483->[x.x.x.x]:162) TRAP, SNMP v1, community public#012#011SNMPv2-SMI::enterprises.318 Enterprise Specific Trap (746) Uptime: 212 days, 15:22:29.95#012#011SNMPv2-SMI::enterprises.318.2.3.10.0 = STRING: "Bbf5499_nbErrorCond_12940872"#011SNMPv2-SMI::enterprises.318.2.3.23.0 = STRING: "Value Too High for....

 

The rest of the data points (variable bindings)are pulled from other locations as defined in your example data:

 

Jun 9 03:53:52 vbcpnocprdwb301 snmptrapd[16911]: 2024-06-09 03:53:52 x.x.x.x(via UDP: [x.x.x.x]:5483->[x.x.x.x]:162) TRAP, SNMP v1, community public#012#011SNMPv2-SMI::enterprises.318 Enterprise Specific Trap (746) Uptime: 212 days, 15:22:29.95#012#011SNMPv2-SMI::enterprises.318.2.3.10.0 = STRING: "Bbf5499_nbErrorCond_12940872"#011SNMPv2-SMI::enterprises.318.2.3.23.0 = STRING: "Value Too High for Too Long"#011SNMPv2-SMI::enterprises.318.2.3.1.0 = INTEGER: 6#011SNMPv2-SMI::enterprises.318.2.3.11.0 = STRING: "Bbf5499_nbSNMPEnc2C202808"#011SNMPv2-SMI::enterprises.318.2.3.24.0 = STRING: "L7-x-x-NB (x.x.x.x)"#011SNMPv2-SMI::enterprises.318.2.3.16.0 = ""#011SNMPv2-SMI::enterprises.318.2.3.25.0 = STRING: "Environmental Monitor"#011SNMPv2-SMI::enterprises.318.2.3.17.0 = STRING: "QA1818170363"#011SNMPv2-SMI::enterprises.318.2.3.20.0 = STRING: "NetBotz Rack Monitor 250"#011SNMPv2-SMI::enterprises.318.2.3.21.0 = STRING: "x.x.x.x"#011SNMPv2-SMI::enterprises.318.2.3.26.0 = STRING: "L7 SF-3"#011SNMPv2-SMI::enterprises.318.2.3.27.0 = STRING: "DCO Team"#011SNMPv2-SMI::enterprises.318.2.3.22.0 = STRING: "Bbf5499_nbSNMPEnc2C202808_MEM_HUMIDITY_5_4"#011SNMPv2-SMI::enterprises.318.2.3.28.0 = STRING: "Humidity - L7-NR-K4-TH"#011SNMPv2-SMI::enterprises.318.2.3.29.0 = STRING: "61 % RH"#011SNMPv2-SMI::enterprises.318.2.3.6.0 = INTEGER: 1717876427#011SNMPv2-SMI::enterprises.318.2.3.7.0 = INTEGER: 0#011SNMPv2-SMI::enterprises.318.2.3.30.0 = STRING: "The value of 'Humidity - L7-X-X-TH' (61 % RH) has been too high for too long."

 

Kind Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

tjlaw
tjlaw Mentor
Mentor

Posted: ‎2024-06-12 06:06 AM

In response to Cory_McDonald
1 Like
0
1462
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-12 06:06 AM

Hi @Cory_McDonald, 

 

Thank you very much for the very informative response. I finally got to understand all the trap information👍.   

 

 

BR, 

 

TJ

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore