DCE 7.4.1 vs pCOweb and Uniflair TDAV0721A and NEXT EVO CW S U 032 F3

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE 7.4.1 vs pCOweb and Uniflair TDAV0721A and NEXT EVO CW S U 032 F3
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:27 AM

0 Likes
21
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:27 AM

DCE 7.4.1 vs pCOweb and Uniflair TDAV0721A and NEXT EVO CW S U 032 F3

Hello,

Im trying to add our old coolers and new coolers into our DCE 7.4.3

The data on the pCOweb on the new (NEXT) coolers are ok and set from the regulator, the uniflairs only report data on digital, analog and integer as U.

However when i try to add the next coolers with snmp i get no sensors, trying to add the oids manually gives screwed data, the number returned 192 is 19.2 degrees but struxureware reads it as 192 degrees.  I look around and It looks like its supported, but im wondering if im doing something wrong.

 

Regards,

-Kent Inge.

(CID:126165503)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:27 AM

0 Likes
2
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:27 AM

Hi Kent,

Just let me start with the supplemental OID issue. There is no option for a multiplier when adding the OID. I have an enhancement request in the system but I'm not sure that's going anywhere.

As for the devices themselves and the DDFs in use, are they all pCOweb cards? Are they all SNMP? I have seen issues with Uniflair units with the old pCOweb cards where they don't properly identify the device type in SNMP. They also re-use OIDs so an OID for temp in one unit could be the same OID for fan speed in another unit. If you have multiple DDFs for pCOweb cards on the same DCE system, you can run into issues.

 

Thanks,

Steve

(CID:126165521)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 21
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:27 AM

0 Likes
2
3193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:27 AM

Hi Kent,

Just let me start with the supplemental OID issue. There is no option for a multiplier when adding the OID. I have an enhancement request in the system but I'm not sure that's going anywhere.

As for the devices themselves and the DDFs in use, are they all pCOweb cards? Are they all SNMP? I have seen issues with Uniflair units with the old pCOweb cards where they don't properly identify the device type in SNMP. They also re-use OIDs so an OID for temp in one unit could be the same OID for fan speed in another unit. If you have multiple DDFs for pCOweb cards on the same DCE system, you can run into issues.

 

Thanks,

Steve

(CID:126165521)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:26 AM

In response to DCIM_Support
0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:26 AM

Hello STeve,

Thank you, one way or an other I want to get my data into the DCE, so trying the DDF file first.  Tho if I could crackt he oids and DCE that would work to.

 

root@iz-toolbox01:/var# snmpwalk -v1 -cpublic 10.41.16.34 1.3.6.1.4.1.9839.2.1.2
iso.3.6.1.4.1.9839.2.1.2.1.0 = INTEGER: 0
iso.3.6.1.4.1.9839.2.1.2.2.0 = INTEGER: 175
iso.3.6.1.4.1.9839.2.1.2.3.0 = INTEGER: 82
iso.3.6.1.4.1.9839.2.1.2.4.0 = INTEGER: 193
iso.3.6.1.4.1.9839.2.1.2.5.0 = INTEGER: 0
iso.3.6.1.4.1.9839.2.1.2.6.0 = INTEGER: 0

82 = 8.2 degrees water temperature in

193 = 19.3 degree water temperature out

When I try to add these in DCE i get 82 degrees and 193 degrees πŸ˜€ 

Regards,

-Kent INge

(CID:126165556)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:26 AM

In response to DCIM_Support
0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:26 AM

Hi Kent,

 

Absolutely go that route. My answer was already assuming you had added the DDF for your device. As for the supplemental OIDs, like you said, the OID returns a value

iso.3.6.1.4.1.9839.2.1.2.4.0 = INTEGER: 193

You need a multiplier of 0.1 to turn 193 into 19.3. That's the issue with supplemental OIDs, there is no place to add that multiplier so you have to know that the value 193 is 19.3.


Steve

(CID:126165589)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:26 AM

0 Likes
16
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:26 AM

Hi Kent Inge Otterstad,

I look around and It looks like its supported, but im wondering if im doing something wrong.

I think it's better to use for your case DDF-files specially designed for your new cooler. For example, here's what you can find on page Device Support:

Not the fact that it will work with your new cooler, but it is necessary to try.

With respect.

(CID:126165531)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:26 AM

In response to DCIM_Support
0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:26 AM

Hello,

 

Thank you for this, but how do I get the file? πŸ˜€ Ive been looking for that.

-Kent Inge.

(CID:126165537)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:26 AM

In response to DCIM_Support
0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:26 AM

To do this, select the desired device on the above page and click the "I WANT IT TOO" button πŸ˜€. During the day, a link to download the DDF-file(s) will be sent to you.

With respect.

(CID:126165545)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:26 AM

In response to DCIM_Support
0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:26 AM

Thank you, 

I guess ive already pressed the button as I cant find anything.

But it can take time I guess.

(CID:126165550)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:26 AM

In response to DCIM_Support
0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:50 AM . Last Modified: β€Ž2024-04-05 04:26 AM

Hi Kent Inge Otterstad,

Did you complete the login on HELP CENTER EcoStruxure IT? Or maybe you are a very new user and registered with HELP CENTER EcoStruxure IT recently?

For me, for example, the above button is available. I have even already fulfilled the request for downloading the three above-mentioned DDF-files for NeXt coolers. It is only necessary to wait a day...

With respect.

(CID:126165559)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:51 AM . Last Modified: β€Ž2024-04-05 04:26 AM

In response to DCIM_Support
0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:51 AM . Last Modified: β€Ž2024-04-05 04:26 AM

Hello,

Ive been registered a while, tho first time I logged into this, Ill check.

I know Ive seen I want this to button before today.

-Kent Inge.

(CID:126165564)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:51 AM . Last Modified: β€Ž2024-04-05 04:26 AM

In response to DCIM_Support
0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:51 AM . Last Modified: β€Ž2024-04-05 04:26 AM

I have this:

Maybe its included in that, I can see the I want it too on differenet products.

(CID:126165569)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:51 AM . Last Modified: β€Ž2024-04-05 04:26 AM

In response to DCIM_Support
0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:51 AM . Last Modified: β€Ž2024-04-05 04:26 AM

Yep, Its requested already πŸ˜€ thank you very much. πŸ˜€

(CID:126165572)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:51 AM . Last Modified: β€Ž2024-04-05 04:26 AM

In response to DCIM_Support
0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:51 AM . Last Modified: β€Ž2024-04-05 04:26 AM

In case you can not get a DDF-file, I agree to send it to you as soon as I download it myself πŸ˜€.

With respect.

(CID:126165574)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:51 AM . Last Modified: β€Ž2024-04-05 04:26 AM

In response to DCIM_Support
0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:51 AM . Last Modified: β€Ž2024-04-05 04:26 AM

Thank you very much πŸ˜€ 

(CID:126165577)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:51 AM . Last Modified: β€Ž2024-04-05 04:26 AM

In response to DCIM_Support
0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:51 AM . Last Modified: β€Ž2024-04-05 04:26 AM

Ok, as soon as you try the new DDF-file for your new cooler, please give feedback here.

With respect.

(CID:126165582)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:51 AM . Last Modified: β€Ž2024-04-05 04:26 AM

In response to DCIM_Support
0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:51 AM . Last Modified: β€Ž2024-04-05 04:26 AM

Hi Kent Inge Otterstad,

I have already downloaded the three above DDF-files from support and I can tell you, that only one of them will work for you: this DDF-file for cooler NeXt DX U 052 P2 H6 RC Group. But, it may be necessary for it to be slightly modified for your device, i.e. make Request modification.

With respect.

(CID:126166157)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:51 AM . Last Modified: β€Ž2024-04-05 04:26 AM

In response to DCIM_Support
0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:51 AM . Last Modified: β€Ž2024-04-05 04:26 AM

Hello,

I downloaded another one and it got results, however something wrong, I'll try this one.

And if so try requesting  a mod if needed.

Thank you again.

Regards,

-Kent

(CID:126166236)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:51 AM . Last Modified: β€Ž2024-04-05 04:26 AM

In response to DCIM_Support
0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:51 AM . Last Modified: β€Ž2024-04-05 04:26 AM

Hello spezialist,

What I got working was by editing the xml file contained in neXt.CW.K RC Group.

And thats fine with me, tho I need to add a few more sensors manually that way, so I need to identify what oids are related to everything.

I have problems with the humididity tho, its not showing so im probably doing something worng with that one.

Its probably the lines mult, op i added, that makes it not show, but if not having a multiplier it shows the value in 100s.


humidity
ROOM_HUMID



.1.3.6.1.4.1.9839.2.1.2.10.0

0.1



Temperature/Humidity Values

One more thing, do you know of a way to change DCE so I can get Celcius inside it?  Now everything shows as F but not on the web.

Regards,

-Kent Inge.

(CID:126166544)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:52 AM . Last Modified: β€Ž2024-04-05 04:26 AM

In response to DCIM_Support
0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:52 AM . Last Modified: β€Ž2024-04-05 04:26 AM

Hi Kent Inge Otterstad,

I'm glad that you did it πŸ˜€.

Now about the humidity sensor, you have an error that needs to be corrected like this:

humidity ROOM_HUMID .1.3.6.1.4.1.9839.2.1.2.10.0 0.1 Temperature/Humidity Values

I hope you understand your mistake.

Now about the units in the DCE-client, try changing the language settings in it, for example like this:

I hope this helps you πŸ˜€.

With respect.

(CID:126166592)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:52 AM . Last Modified: β€Ž2024-04-05 04:26 AM

In response to DCIM_Support
0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:52 AM . Last Modified: β€Ž2024-04-05 04:26 AM

Spot on πŸ˜€ 

Thank you so much for your help.

Now to find the rest of the sensors I need for monitoring. πŸ˜€

 

-Kent Inge

(CID:126166610)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:52 AM . Last Modified: β€Ž2024-04-05 04:26 AM

In response to DCIM_Support
0 Likes
0
3191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:52 AM . Last Modified: β€Ž2024-04-05 04:26 AM

Always glad to help πŸ˜€.

(CID:126166640)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:52 AM . Last Modified: β€Ž2023-10-22 01:10 AM

0 Likes
0
3191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:52 AM . Last Modified: β€Ž2023-10-22 01:10 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore