DCE 7.4.1 restart "Error closing file %s: No space left on device"

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE 7.4.1 restart "Error closing file %s: No space left on device"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:07 PM . Last Modified: ‎2024-04-08 01:05 AM

0 Likes
7
1133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:07 PM . Last Modified: ‎2024-04-08 01:05 AM

DCE 7.4.1 restart "Error closing file %s: No space left on device"

Hi support Team,

This problem occurs during download Capturelogs,the DCE server crashes,restart the DCE server through the virtual machine management software,DCE service can not start," Starting Data Center Expert: Error closing file %s : No space left on device"

(CID:116919986)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:08 PM . Last Modified: ‎2024-04-08 01:05 AM

0 Likes
0
1133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:08 PM . Last Modified: ‎2024-04-08 01:05 AM

Hi mamacoo,

After DCE-server rebooting, you can login to the DCE Web-console?

How long have you been interested in the size of the available disk space on the DCE-server?

If this is DCE VM appliance, try adding one more virtual HDD of the size, for example, 50GB. Power off and power on the DCE VM appliance after that: if the server software is OK, then the newly added amount of free space will be added to the /data logical volume and the server software should start normally.

I am always glad to help.

(CID:116920008)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:08 PM . Last Modified: ‎2024-04-08 01:05 AM

0 Likes
0
1133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:08 PM . Last Modified: ‎2024-04-08 01:05 AM

You need to adjust the available harddisk space on the virtual machine in order to make more space available.

Attention: do not increase the size of an existing virtual HDD. This will not help you. It is necessary to add one more separate virtual HDD and restart the DCE-server. This rule applies to both the DCE VM appliance and the DCE hardware appliance. Look carefully at this topic: .

 With best regards.

(CID:116922529)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:08 PM . Last Modified: ‎2024-04-08 01:05 AM

0 Likes
0
1133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:08 PM . Last Modified: ‎2024-04-08 01:05 AM

Hi Spezialist,

the /data is 100% load,how to add free space to the /Data Folder?

(CID:116920127)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:08 PM . Last Modified: ‎2024-04-08 01:05 AM

0 Likes
0
1133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:08 PM . Last Modified: ‎2024-04-08 01:05 AM

mamacoo,

See my answer below:

  1. power off the VMware DCE VM;
  2. add second vHDD appropriate size to the DCE VM configuration;
  3. power on the VMware DCE VM;
  4. login to the DCE-client and check available local storage size.

I am always glad to help.

(CID:116922527)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:08 PM . Last Modified: ‎2024-04-08 01:04 AM

0 Likes
1
1133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:08 PM . Last Modified: ‎2024-04-08 01:04 AM

yes,i get it.,add a second vhdd or extend the /data can resolve it.Thanks

(CID:116924062)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:08 PM . Last Modified: ‎2024-04-08 01:04 AM

In response to DCIM_Support
0 Likes
0
1133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:08 PM . Last Modified: ‎2024-04-08 01:04 AM

Hi mamacoo,

By adding the second vhdd, you thereby expand the automatically /data partition.

 But simply extend an existing /data partition without adding a second vhdd is no longer so easy, since you either need the root password, or mount the DCE-server partitions offline with a Linux LiveCD 😀.

With best regadrs.

(CID:116924103)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:08 PM . Last Modified: ‎2023-10-22 01:10 AM

0 Likes
0
1133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:08 PM . Last Modified: ‎2023-10-22 01:10 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore