DCE 7.3.1 discovers devices but stays initializing

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE 7.3.1 discovers devices but stays initializing
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:53 AM . Last Modified: ‎2024-04-08 11:31 PM

0 Likes
2
781
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:53 AM . Last Modified: ‎2024-04-08 11:31 PM

DCE 7.3.1 discovers devices but stays initializing

Hi I have installed DCE 7.3.1 VM onto a campus network, I can trouble shoot the network and get a valid ping response however the device remains in initializing. this happening on all devices (cooling, ups, PDU, RPDU)

all are Schneider (APC) products and user names and PW all correct

TIA Mike

(CID:106892145)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:53 AM . Last Modified: ‎2024-04-08 11:31 PM

0 Likes
0
781
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:53 AM . Last Modified: ‎2024-04-08 11:31 PM

Dear Mike,

Struxureware Data Center Expert communicates to the devices via SNMP/Modbus over TCP protocols. 

I would suggest to ensure that the following:

  • Ensure SNMP Version 1 is enabled
  • Ensure that the devices are running with the latest firmware
  • You can do an SNMP walk by using SNMP Browser and see if you are able to poll the device via SNMP browser
  • Make sure SNMP version 1 port 161 is not blocked on your network. SNMP version 1 uses the following port: Port 161(UDP), 162 (TCP/UDP)- SNMP Communication from SNMP Agent 

 

Protocol

Transfer Protocol

Ports

Network

Comments

HTTP

TCP (SSL)

80 (443)

Network speed of minimum 100 Mbps is recommended. Bandwidth usage between client and server heavily depends on number of discovered devices, alarm configuration and operations carried out in the client e.g. report generation.

Communication from NetBotz Appliances / DCE Console/Web API and 3rd party integrations.

SNMP

UDP

161

The bandwidth needed heavily depends on number of discovered devices, polling interval configured and alarm activity in the system.

SNMP Communication between discovered devices and DCE

SNMP (Trap)

TCP/UDP

162

Specified in device SNMP configuration

SNMP Communication between discovered devices and DCE

SMTP

TCP

25

Network requirements are low. Email traffic from the DCE is depended on alarm policy configuration and number of alarms occurring.

Communication with e-mail server

FTP

TCP

21

Used when device is discovered and DDF file transferred. The network requirements are low.

Transfer DDF files between devices and DCE

SCP

TCP

22

Used when device is discovered and DDF file transferred. The network requirements are low.

Transfer DDF files between devices and DCE

DNS

TCP/UDP

53

Very limited traffic and bandwidth requirement

DNS server communication

For more info: http://dcimsupport.apc.com/display/UADCE725/StruxureWare+Data+Center+Expert+Security

 

I also request you to check the following K-base document: 

K-base name: How can I troubleshoot SNMP communications issues?

http://www.schneider-electric.co.in/en/faqs/FA226273/

 

I hope this helps. 

Regards,

Bala

(CID:106892281)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:54 AM . Last Modified: ‎2023-10-31 10:25 PM

0 Likes
0
781
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:54 AM . Last Modified: ‎2023-10-31 10:25 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore