DCE 7.3.1 Alarm action script/function

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE 7.3.1 Alarm action script/function
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:32 AM . Last Modified: ‎2024-04-08 11:56 PM

0 Likes
5
975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:32 AM . Last Modified: ‎2024-04-08 11:56 PM

DCE 7.3.1 Alarm action script/function

Have a DCE 7.3.1 system with Netbotz 570 in a small server room with 5 racks. The fire suppression system is water and can't be changed or modified. They want to use smoke detectors attached to the netbotz and to have alerts created that shut everything down in the event smoke is detected. Is this even possible? Can anyone point me in the direction of how this might be accomplished? Thanks.

(CID:106206543)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:32 AM . Last Modified: ‎2024-04-08 11:56 PM

0 Likes
3
975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:32 AM . Last Modified: ‎2024-04-08 11:56 PM

Hi Eric,

 

The NetBotz 570 can switch it's output relays based on any alert the NetBotz appliance sees. If you have a NetBotz smoke detector connected you can have that trigger an alarm which switches the output. This can be used to turn off just about any hardware or electrical output. If you have a system that already detects and has an output relay itself, you can connect a dry contact cable to the 570 and it can sense the system going into alert. It can then trigger it's output. This would seem redundant however as if the system already has an output, you don't need another on in the middle.

 

If you are monitoring the system with DCE, there is no option to script any output to any relays or to the NetBotz appliance. The DCE server can only output e-mails, traps, and messages of that sort. If you're monitoring DCE with some type of trap receiver, there are systems of that sort that can run a script based on a trap it has received.

 

Steve

(CID:106206546)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:32 AM . Last Modified: ‎2024-04-08 11:56 PM

0 Likes
3
976
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:32 AM . Last Modified: ‎2024-04-08 11:56 PM

Hi Eric,

 

The NetBotz 570 can switch it's output relays based on any alert the NetBotz appliance sees. If you have a NetBotz smoke detector connected you can have that trigger an alarm which switches the output. This can be used to turn off just about any hardware or electrical output. If you have a system that already detects and has an output relay itself, you can connect a dry contact cable to the 570 and it can sense the system going into alert. It can then trigger it's output. This would seem redundant however as if the system already has an output, you don't need another on in the middle.

 

If you are monitoring the system with DCE, there is no option to script any output to any relays or to the NetBotz appliance. The DCE server can only output e-mails, traps, and messages of that sort. If you're monitoring DCE with some type of trap receiver, there are systems of that sort that can run a script based on a trap it has received.

 

Steve

(CID:106206546)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:32 AM . Last Modified: ‎2024-04-08 11:56 PM

In response to DCIM_Support
0 Likes
0
975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:32 AM . Last Modified: ‎2024-04-08 11:56 PM

Thanks Steve. So if I put in a NetBotz smoke detector can that directly signal PDU's and the Symmetra UPS to shutdown? All the PDU's are either AP8941 or AP8953NA3. Also, are there any detailed manuals/guides on this? I have the Netbotz manual but I don't see it going into details about this area.

(CID:106206550)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:33 AM . Last Modified: ‎2024-04-08 11:56 PM

In response to DCIM_Support
0 Likes
0
975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:33 AM . Last Modified: ‎2024-04-08 11:56 PM

Hi Eric, The output relay can trigger anything with an input dry contact type sensor. It could be used for instance on the Symmetra LX. The manual here: http://www.apcmedia.com/salestools/ASTE-6Z8LS7/ASTE-6Z8LS7_R0_EN.pdf?sdirect=true This can be dry contact or 24V applied. I would be very careful in creating a specific alert action and profile specifically for the smoke sensor so nothing else triggers this. Please note that you will have to work with the default state of the relays. For instance if you manually change the state of a normally closed connection to normally open and reboot the appliance, it will change state momentarily (see k-base FA158337). I do not believe the PDU has this type of option but if they are connected to a UPS, shutting off the output of the UPS will also shut off the output from the PDU. Different PDUs may have different options. Steve

(CID:106206551)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:33 AM . Last Modified: ‎2024-04-08 11:56 PM

In response to DCIM_Support
0 Likes
0
975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:33 AM . Last Modified: ‎2024-04-08 11:56 PM

Thank you very much....

(CID:106206560)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:33 AM . Last Modified: ‎2023-10-31 10:24 PM

0 Likes
0
975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:33 AM . Last Modified: ‎2023-10-31 10:24 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore