DCE 7.2.2 Upgrade issue

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE 7.2.2 Upgrade issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:41 PM . Last Modified: ‎2024-04-09 01:42 AM

0 Likes
7
1432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:41 PM . Last Modified: ‎2024-04-09 01:42 AM

DCE 7.2.2 Upgrade issue

Hi,

  As shown in attached picture there is no installed version information. how to upgrade ? i already tried to import the file but procedure not succeed. one more thing happened in same server when i add any device like cooling , rack access the device icon converted into PDU automatically.

 

(CID:105459083)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:42 PM . Last Modified: ‎2024-04-09 01:42 AM

0 Likes
0
1432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:42 PM . Last Modified: ‎2024-04-09 01:42 AM

Hi Ali, As per my experience sometime that problem occurred after performing RESTORE for reinstall the StruxureWare Data Center Expert v7.2.2. If you has same problem then you need to make it again fresh Restore CD or USB and install. Hope your problem will be solved. BR, Rana Ajmal

(CID:105459231)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:41 PM . Last Modified: ‎2024-04-09 01:42 AM

0 Likes
2
1432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:41 PM . Last Modified: ‎2024-04-09 01:42 AM

Hi Ali,

If you have not done so already, you should contact your local Technical Support for the DCE upgrade links. They will be able to validate your Software Support Contract, and provide you with the required links. These links contain all the instructions for upgrading the server.

Regards

 

(CID:105459103)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:41 PM . Last Modified: ‎2024-04-09 01:42 AM

In response to DCIM_Support
0 Likes
0
1432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:41 PM . Last Modified: ‎2024-04-09 01:42 AM

Hi John, I know about how to upgrade and I have upgrade files, I just want to know what is the problem the DCE server is not showing the installed version.

(CID:105459107)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:42 PM . Last Modified: ‎2024-04-09 01:42 AM

In response to DCIM_Support
0 Likes
0
1432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:42 PM . Last Modified: ‎2024-04-09 01:42 AM

Ali, I am not sure why it is not showing the Installed Version on that screen, as I have not seen that happen before. Have you tried this with other DCE Clients on different machines. Also, have you tried a reboot of the server to see if that makes any difference? Can you send us a screenshot of the error you get when trying to import the 7.2.4 upgrade file. Thanks

(CID:105459116)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:42 PM . Last Modified: ‎2024-04-09 01:42 AM

0 Likes
0
1432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:42 PM . Last Modified: ‎2024-04-09 01:42 AM

Hi Ali,

As far as I am aware you cant apply an update without uploading the update files to the DCE server.

Once these files have been uploaded you then apply the update from the DCE server client.

It seems from the screenshot you have posted that when the software was configured the latest update or any update was not applied to your server. Having just checked mine it is showing as running 7.2.7.

Are you trying to apply the latest version? (7.2.7)

Martin

 

 

(CID:105459126)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:42 PM . Last Modified: ‎2024-04-09 01:42 AM

0 Likes
0
1433
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:42 PM . Last Modified: ‎2024-04-09 01:42 AM

Hi Ali, As per my experience sometime that problem occurred after performing RESTORE for reinstall the StruxureWare Data Center Expert v7.2.2. If you has same problem then you need to make it again fresh Restore CD or USB and install. Hope your problem will be solved. BR, Rana Ajmal

(CID:105459231)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:42 PM . Last Modified: ‎2024-04-09 01:42 AM

0 Likes
0
1432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:42 PM . Last Modified: ‎2024-04-09 01:42 AM

Thanks to all , after install restore the problem has been solved.

(CID:105459713)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:42 PM . Last Modified: ‎2023-10-31 10:24 PM

0 Likes
0
1432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:42 PM . Last Modified: ‎2023-10-31 10:24 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore