In DCE 7.2.0 Alert Configuration > due to electric In / Out, we got too many device communication lost emails. We setup 300 seconds (05 minutes) delay in Communication Status / Link Status using 'Return to Normal Delay' Setting.
This is in case of a device failure, DCE will check device status for 05 minutes if device discovery fails DCE will send email, Unfortunately it is not happening.
Your support is requested to overcome with the situation.
(CID:108824744)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 05:53 AM . Last Modified: β2024-04-08 11:12 PM
(CID:108825190)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 05:53 AM . Last Modified: β2024-04-08 11:12 PM
Hi m.shahid, thanks for posting. Lets see who can be of assistance here. @community any ideas? Kind regards Ditte
(CID:108825044)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 05:53 AM . Last Modified: β2024-04-08 11:12 PM
Hi Muhammad!
You need to change your settings. Return to Normal Delay is used when you need to be sure that alert condition is gone. In this case DCE wait 300 seconds and than send email if there is no alert conditions for the sensor.
For your case you should use another threshold type State For Time or State Mismatch For Time. Unfortunately there is no such settings for Communication Lost alerts, but you can workaround it with device state sensors which present on almost all devices.
You need:



Now, when device status changed from Normal to something else, DCE will send email after 5 minutes.
(CID:108825148)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 05:53 AM . Last Modified: β2024-04-08 11:12 PM
(CID:108825190)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 05:54 AM . Last Modified: β2024-04-08 11:12 PM
Implemented solution from Valentin Kozlov. Waiting for result. Thanks for support π
(CID:108825534)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 05:54 AM . Last Modified: β2023-10-31 10:24 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Youβve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.