Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Cyberpower UPS Sensors - Showing Unplugged

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Cyberpower UPS Sensors - Showing Unplugged
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:53 PM . Last Modified: ‎2024-04-03 11:44 PM

0 Likes
10
1701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:53 PM . Last Modified: ‎2024-04-03 11:44 PM

Cyberpower UPS Sensors - Showing Unplugged

HI 

When I first discover this UPS (SNMP device)I have all the sensor values. See below image

After a few minutes. I assume after it is polled again they show as unplugged. see below.

 

Any explanation for this ?

I am assuming the poll is being rejected by the UPS somehow? If I delete this device in DCE and rediscover it nothing is discovered. I have to stop/start SNMP on the UPS and reboot the NMC (RMCARD202). It can now be discovered again in DCE. 

I am using CyberPower DDF file and other CyberPower UPS are ok.

 

I was suspecting faulty card however. I have tested using a CyberPower motioning software using the same snmp protocol and keys without issue to see if it can be discovered it works fine  and sensors have values all the time (Though u would expect there tool to be compatible)

I can SNMPwalk to it as well via DCE and tools ok.

 

Any suggestions?

cheers

Bruce

(CID:137106582)

Labels
  • Labels:
  • Data Center Expert
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:53 PM . Last Modified: ‎2024-04-03 11:44 PM

0 Likes
0
1701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:53 PM . Last Modified: ‎2024-04-03 11:44 PM

Dear Bruce Phillips,

Tell us please, did you solve this problem or not?

With respect.

(CID:137109198)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:53 PM . Last Modified: ‎2024-04-03 11:44 PM

0 Likes
0
1701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:53 PM . Last Modified: ‎2024-04-03 11:44 PM

No not yet.  have just had a DDF created specific to this UPS so I will load that into DCE and rediscover device . Will try today and see how we go

(CID:137109456)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:53 PM . Last Modified: ‎2024-04-03 11:44 PM

0 Likes
0
1703
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:53 PM . Last Modified: ‎2024-04-03 11:44 PM

Ok, I would be interested to know the result.

With respect.

(CID:137109520)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:53 PM . Last Modified: ‎2024-04-03 11:44 PM

0 Likes
0
1703
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:53 PM . Last Modified: ‎2024-04-03 11:44 PM

There was no change. I installed new DDF in to DCE. Then rebooted card, stopped and started snmp on card. Rediscovered the device in DCE however sensors are still showing unplugged.

(CID:137110645)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:53 PM . Last Modified: ‎2024-04-03 11:44 PM

0 Likes
0
1703
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:53 PM . Last Modified: ‎2024-04-03 11:44 PM

Dear Bruce Phillips,

That is, you wanted to say: first, your UPS is normally discovered in DCE software with all its sensors. And then after ~5 minutes, all your UPS sensors in DCE software go into Unplugged state. It's right?

What is the name of the DDF-file you use and what is its version?

With respect.

(CID:137110872)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:53 PM . Last Modified: ‎2024-04-03 11:44 PM

0 Likes
0
1703
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:53 PM . Last Modified: ‎2024-04-03 11:44 PM

Hi there

Yes that is correct. 

DDF is cyberpower.xml Version 3

Other CyberPower devices are fine in DCE. Just this one. 

I am suspecting it must be faulty card.

 

cheers

Bruce

 

 

 

 

 

 

(CID:137111453)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:53 PM . Last Modified: ‎2024-04-03 11:44 PM

0 Likes
0
1703
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:53 PM . Last Modified: ‎2024-04-03 11:44 PM

Dear Bruce Phillips,

From your comments:

Other CyberPower devices are fine in DCE. Just this one. 

I am suspecting it must be faulty card.

If all your UPS's you specified are the same series (the same model), and only with one you have such strange problems, then the problem is not in the DCE-server. It is very likely, that the problem is either in the NMC of this UPS, or on the network. In this case, of course, you better first ask the help of the vendor of this UPS.

Hope this helps you.

With respect.

(CID:137111639)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:54 PM . Last Modified: ‎2024-04-03 11:44 PM

0 Likes
0
1703
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:54 PM . Last Modified: ‎2024-04-03 11:44 PM

Yep I agree. I am waiting on a replacement card. And will put that in when  I get a chance

(CID:137112221)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:54 PM . Last Modified: ‎2024-04-03 11:44 PM

0 Likes
0
1703
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:54 PM . Last Modified: ‎2024-04-03 11:44 PM

Ok, in any case I would be interested to know the details.

With respect.

(CID:137112323)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 02:54 PM . Last Modified: ‎2023-10-22 01:09 AM

0 Likes
0
1703
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:54 PM . Last Modified: ‎2023-10-22 01:09 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore