Hello,
I tried to integrate an Uniflair downflow CRAC as a SNMP device with Carel pCOWeb card into DCE but i have only U when i read into the CRAC :



Can you telle me what to do, i have the same problem on 3 other sites?
Best regards
Nassim
(CID:106210489)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 04:25 AM . Last Modified: 2024-04-08 11:39 PM
Hello,
The was was with un PCO, i put the right baud rate and it's ok now thank you
(CID:106210666)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 04:25 AM . Last Modified: 2024-04-08 11:39 PM
Hi Nasim,
It looked your PCO not configure yet. You only console into the pco web only not into PCO Controller.
It could you not syncronized baud rate in the PCO web and baud rate controller (from unit display).
By default PCO web baud rate is 19200, and baud rate of PCO controller 1200.
(CID:106210514)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 04:25 AM . Last Modified: 2024-04-08 11:39 PM
Hi Nassim,
You need to upload the uniflair webpages on PCO Web card then you can able to see the status.(see the below sample picture) for more options like thresholds and email alerting you need to upload DDF into DCE then you can able to get email alert from unit. For web pages and DDF you need to contact your local tech support.

Regards,
Rana Ajmal
(CID:106210530)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 04:25 AM . Last Modified: 2024-04-08 11:39 PM
Hello,
The was was with un PCO, i put the right baud rate and it's ok now thank you
(CID:106210666)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 04:25 AM . Last Modified: 2023-10-31 10:20 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.