Change battery age in DCE?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Change battery age in DCE?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:18 AM . Last Modified: ‎2024-04-05 04:37 AM

0 Likes
6
1544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:18 AM . Last Modified: ‎2024-04-05 04:37 AM

Change battery age in DCE?

A few of my UPSs (Symmetra LX models) are reporting a different age than what their batteries actually are. Is there a way to change the battery age through DCE? For example, if a battery was replaced?

I was shown this once, but don't recall the steps to take care of this.

(CID:126162042)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:18 AM . Last Modified: ‎2024-04-05 04:37 AM

0 Likes
4
1544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:18 AM . Last Modified: ‎2024-04-05 04:37 AM

Hi Austin,

The value is derived from the UPS so you can always change the last battery replacement date on the UPS directly. That actually may be the easiest/quickest route. You can however change the battery age of an APC UPS by going to the Device menu–>APC SNMP Device Configuration (standard configuration) -->Configure devices. You may want to retrieve the current device configurations for the specific devices. Hit Next and choose the device. Hit Next.

Scroll to "Advanced Options" and look for the UPS. I have a PX here for an example:

Double click that entry and you can enter a date. Use one similar to what is shown in your system (not sure if it changes format for different regions). Hit Finish and as long as the DCE system has the proper FTP/SCP configuration and passwords, it should push the config to the device.

 

Thanks,
Steve 

(CID:126162067)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:18 AM . Last Modified: ‎2024-04-05 04:37 AM

0 Likes
4
1545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:18 AM . Last Modified: ‎2024-04-05 04:37 AM

Hi Austin,

The value is derived from the UPS so you can always change the last battery replacement date on the UPS directly. That actually may be the easiest/quickest route. You can however change the battery age of an APC UPS by going to the Device menu–>APC SNMP Device Configuration (standard configuration) -->Configure devices. You may want to retrieve the current device configurations for the specific devices. Hit Next and choose the device. Hit Next.

Scroll to "Advanced Options" and look for the UPS. I have a PX here for an example:

Double click that entry and you can enter a date. Use one similar to what is shown in your system (not sure if it changes format for different regions). Hit Finish and as long as the DCE system has the proper FTP/SCP configuration and passwords, it should push the config to the device.

 

Thanks,
Steve 

(CID:126162067)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:19 AM . Last Modified: ‎2024-04-05 04:37 AM

In response to DCIM_Support
0 Likes
0
1544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:19 AM . Last Modified: ‎2024-04-05 04:37 AM

Thanks Steve, I incorrectly remembered how to change the age and it was through the UPS itself.

Would the method above work for non-APC UPSs? I've got several UPSs that cannot report their age, but it looks like the above can be a good workaround to manually enter it.

(CID:126162147)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:19 AM . Last Modified: ‎2024-04-05 04:37 AM

In response to DCIM_Support
0 Likes
0
1544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:19 AM . Last Modified: ‎2024-04-05 04:37 AM

Hi Austin,

 

Sorry no, this is specific to APC devices. 3rd party devices each have their own options and their own way of doing things and protocols to do this. It's not an SNMP setting, we actually use FTP to send a config.ini to the device.

 

Steve

(CID:126162150)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:19 AM . Last Modified: ‎2024-04-05 04:37 AM

In response to DCIM_Support
0 Likes
0
1544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:19 AM . Last Modified: ‎2024-04-05 04:37 AM

Just a side note, if the device does not have a battery age sensor, check to see if it is available via SNMP. If it is, see if you can get the DDF updated. If not, you can create a custom property. Using these, you can associate any data you'd like to a device in DCE. It will be a manual addition. The following k-base can help walk you through it:

http://www.apc.com/us/en/faqs/index?page=content&id=FA299535

 

Steve

(CID:126162154)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:19 AM . Last Modified: ‎2024-04-05 04:37 AM

In response to DCIM_Support
0 Likes
0
1544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:19 AM . Last Modified: ‎2024-04-05 04:37 AM

Thanks Steve, that's a huge help for my end!

(CID:126162163)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:19 AM . Last Modified: ‎2023-10-20 05:08 AM

0 Likes
0
1544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:19 AM . Last Modified: ‎2023-10-20 05:08 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore