Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Central and DCE on same SNMP LAN

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Central and DCE on same SNMP LAN
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
79
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:05 PM . Last Modified: ‎2024-04-04 02:40 AM

0 Likes
7
2034
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:05 PM . Last Modified: ‎2024-04-04 02:40 AM

Central and DCE on same SNMP LAN

Hi,

I have got Central at the moment. I have installed DCE on the same LAN.

If I "discover" from DCE, am I likely to break Central speaking with the current nodes? 

Thanks

(CID:134029261)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:05 PM . Last Modified: ‎2024-04-04 02:40 AM

0 Likes
4
2035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:05 PM . Last Modified: ‎2024-04-04 02:40 AM

Hi Seun,

There is no specific issue with any 2 monitoring systems monitoring the same SNMP device. There are always chances that too much polling could cause conflicts but as long as the systems are polling at a reasonable rate and the devices are not constantly going into and out of alert, there should be no issue.

Standard polling rates are about once every 5 minutes and should cause no issue. If you do see devices lose comm more often than they do now, just increase timeouts and retries for those devices.

If they were to be sharing the same private or secondary LAN, you'd want to turn off DHCP on one of the systems so that doesn't conflict. I would suggest turning it off on the newly deployed system (before connecting it to that LAN) so devices don't all get new IPs and have to be rediscovered on the old Central server.


Steve

(CID:134029276)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:05 PM . Last Modified: ‎2024-04-04 02:40 AM

0 Likes
0
2035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:05 PM . Last Modified: ‎2024-04-04 02:40 AM

Any idea Steven Marchetti?

(CID:134029269)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:05 PM . Last Modified: ‎2024-04-04 02:40 AM

0 Likes
4
2035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:05 PM . Last Modified: ‎2024-04-04 02:40 AM

Hi Seun,

There is no specific issue with any 2 monitoring systems monitoring the same SNMP device. There are always chances that too much polling could cause conflicts but as long as the systems are polling at a reasonable rate and the devices are not constantly going into and out of alert, there should be no issue.

Standard polling rates are about once every 5 minutes and should cause no issue. If you do see devices lose comm more often than they do now, just increase timeouts and retries for those devices.

If they were to be sharing the same private or secondary LAN, you'd want to turn off DHCP on one of the systems so that doesn't conflict. I would suggest turning it off on the newly deployed system (before connecting it to that LAN) so devices don't all get new IPs and have to be rediscovered on the old Central server.


Steve

(CID:134029276)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:05 PM . Last Modified: ‎2024-04-04 02:40 AM

In response to DCIM_Support
0 Likes
0
2035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:05 PM . Last Modified: ‎2024-04-04 02:40 AM

Thanks Steve. Will give that a shot.

(CID:134029287)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:05 PM . Last Modified: ‎2024-04-04 02:40 AM

In response to DCIM_Support
0 Likes
0
2035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:05 PM . Last Modified: ‎2024-04-04 02:40 AM

Just an FYI, If you were doing (http/https) NetBotz , I don't recommend monitoring them with more than 1 DCE server...definitely not more than 2 especially if using surveillance.

(CID:134029296)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:05 PM . Last Modified: ‎2024-04-04 02:40 AM

In response to DCIM_Support
0 Likes
0
2035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:05 PM . Last Modified: ‎2024-04-04 02:40 AM

Thanks Steve.

Slightly unrelated follow-up question. Can I backup/export my historical data (and probably config/threshold settings) and import these into my new DCE appliance?

(CID:134029600)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:05 PM . Last Modified: ‎2024-04-04 02:39 AM

In response to DCIM_Support
0 Likes
0
2035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:05 PM . Last Modified: ‎2024-04-04 02:39 AM

Hi Seun,

 

No. Because of things like changes in design of the database in different versions, you can not import a backup of DCE that is not of the same version to which you are importing. That is to say if you have DCE 7.5, you can only import a backup from another 7.5 system. If you back up a 6.0 server, you can only import that into another 6.0 serer. The server won't even see the backup from another version.

 

Steve

(CID:134029692)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:06 PM . Last Modified: ‎2023-10-20 05:07 AM

0 Likes
0
2035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:06 PM . Last Modified: ‎2023-10-20 05:07 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore