I came across an issue while installing DCO in VMware, where no network adaptor was found regardless of the adaptor type ie NAT, Bridge.
The solution was to edit the .vmx configuration file and add the following line.
ethernet0.virtualDev = "e1000"
Hope this helps anyone with the same issue