Best Practices DCE private and public network

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Best Practices DCE private and public network
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:35 AM . Last Modified: ‎2024-04-05 04:05 AM

0 Likes
2
993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:35 AM . Last Modified: ‎2024-04-05 04:05 AM

Best Practices DCE private and public network

I have DCE and DCO products on VM platform.  Is there a document that describes the best practices for network implementation, or is it a per location type of question?

I want to have my datacenter end devices ( CDU's, thermal modules ) isolated from the rest of the network on an isolated building automation network, but accessible by DCE.  I want DCE to be able to accessible by my DCE client from a user network.  DCE and DCO need to talk to each other from the user network.

To do this, I assume that I'll need two network interfaces on DCE.  Does the Private network talk to the end devices, or to the user network?  Does the DCE server perform discovery on the Private or the User network?

Thank you for any helpful direction.

(CID:126171615)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:35 AM . Last Modified: ‎2024-04-05 04:05 AM

0 Likes
0
993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:35 AM . Last Modified: ‎2024-04-05 04:05 AM

Hi Brady,

 

When you set up a DCE server with a Private LAN, that LAN should indeed be isolated from the "Public LAN" There should be no routing between the 2 other than DCE itself. The devices then could reside on either the Public or Private LAN. Usually when you have a VM and have specifically created that Private LAN (as opposed to hardware where it already exists) your plan is to put the devices on that LAN. Keep in mind however that other systems not on that LAN will have no access to the devices other than users through DCE. Again, devices can be on either Public, Private, or both LANs, that's all dependent on how you want your network configured.

Users can connect to DCE from either the Public or Private LANs but it is usually the case where they are on the Public LAN along with DNS servers, SMTP servers, etc. DCO would likely be on the Public LAN as well but just consider that the users must be able to access it. If the users are public, so should DCO be public.

DCO doesn't communicate to SNMP or Modbus devices directly, it gets it's device info from DCE or other systems. If for instance you were getting server info with IT Optimize and users are on the DCE Public LAN, you'd need DCO on the Public LAN, ITO on the public LAN, and the servers ITO is communicating with on that same Public LAN.

 

Thanks,

Steve

(CID:126171633)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:35 AM . Last Modified: ‎2024-04-05 04:05 AM

0 Likes
0
994
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:35 AM . Last Modified: ‎2024-04-05 04:05 AM

Hi Brady,

 

When you set up a DCE server with a Private LAN, that LAN should indeed be isolated from the "Public LAN" There should be no routing between the 2 other than DCE itself. The devices then could reside on either the Public or Private LAN. Usually when you have a VM and have specifically created that Private LAN (as opposed to hardware where it already exists) your plan is to put the devices on that LAN. Keep in mind however that other systems not on that LAN will have no access to the devices other than users through DCE. Again, devices can be on either Public, Private, or both LANs, that's all dependent on how you want your network configured.

Users can connect to DCE from either the Public or Private LANs but it is usually the case where they are on the Public LAN along with DNS servers, SMTP servers, etc. DCO would likely be on the Public LAN as well but just consider that the users must be able to access it. If the users are public, so should DCO be public.

DCO doesn't communicate to SNMP or Modbus devices directly, it gets it's device info from DCE or other systems. If for instance you were getting server info with IT Optimize and users are on the DCE Public LAN, you'd need DCO on the Public LAN, ITO on the public LAN, and the servers ITO is communicating with on that same Public LAN.

 

Thanks,

Steve

(CID:126171633)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:36 AM . Last Modified: ‎2023-10-20 05:03 AM

0 Likes
0
993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:36 AM . Last Modified: ‎2023-10-20 05:03 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore