Adding devices to an existing treshold alarm

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Adding devices to an existing treshold alarm
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:33 PM . Last Modified: ‎2024-04-05 02:55 AM

0 Likes
5
1040
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:33 PM . Last Modified: ‎2024-04-05 02:55 AM

Adding devices to an existing treshold alarm

Hi Team,

I have not be able to add a new device to an existing threshold alarm. When I define a threshold alarm I can select what devices are included in this alarm, for example all the temperature sensors of the rack PDUs of a room.

But if I discover new devices in a future, I cannot include these new sensors in the existing threshold alarm, I have to define new threshold alarm for each rack that I install.

Is there anyway to edit a threshold alarm to add new devices into it?

Regards.

(CID:128748911)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:33 PM . Last Modified: ‎2024-04-05 02:55 AM

0 Likes
3
1039
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:33 PM . Last Modified: ‎2024-04-05 02:55 AM

Hi Javier,

 

I'm not 100% sure I understand what your issue is. I have a number of cooling devices so I decided to use these for testing. I deleted one device. I created a policy and added an alarm to that policy. I then created a temperature threshold on 2 of the devices I have. It asked what policy (not alarm) that I wanted to add it to. I added the thresholds to the policy I created.

I then re-added the other cooling device (brand new device as far as the policy and DCE knows). I created a temperature threshold for that device and when it asked what policy to add it to, I chose the one I had just made moments earlier. 

 

Now if I have a threshold alarm configuration, there is no way to add a different device to that threshold. When you created the threshold(s), you actually created it for multiple devices at once. You don't add or remove them later on, you simply create a new threshold. It was initially a grouped creation but once done, there is no group identity to the thresholds, they are individual and you must create new thresholds to new devices. 

 

Steve

 

(CID:128748924)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:33 PM . Last Modified: ‎2024-04-05 02:55 AM

0 Likes
3
1040
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:33 PM . Last Modified: ‎2024-04-05 02:55 AM

Hi Javier,

 

I'm not 100% sure I understand what your issue is. I have a number of cooling devices so I decided to use these for testing. I deleted one device. I created a policy and added an alarm to that policy. I then created a temperature threshold on 2 of the devices I have. It asked what policy (not alarm) that I wanted to add it to. I added the thresholds to the policy I created.

I then re-added the other cooling device (brand new device as far as the policy and DCE knows). I created a temperature threshold for that device and when it asked what policy to add it to, I chose the one I had just made moments earlier. 

 

Now if I have a threshold alarm configuration, there is no way to add a different device to that threshold. When you created the threshold(s), you actually created it for multiple devices at once. You don't add or remove them later on, you simply create a new threshold. It was initially a grouped creation but once done, there is no group identity to the thresholds, they are individual and you must create new thresholds to new devices. 

 

Steve

 

(CID:128748924)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:33 PM . Last Modified: ‎2024-04-05 02:55 AM

In response to DCIM_Support
0 Likes
0
1039
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:33 PM . Last Modified: ‎2024-04-05 02:55 AM

Hi Steven,

yes, that was my question.

I think it would be much easier to add sensors to a previously defined threshold. For example, all the temperature sensors will have the same threshold, 15-30ºC.

We are now in a project with 33 data centers, and we are discovering devices little by little, and creating the room's maps.

In every new location we have to create new thresholds for temperature with new devices' sensors. If we could add these devices to a defined threshold alarm, for example from here allowing add new devices to this Range Temperature threshold:

(CID:128748963)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:33 PM . Last Modified: ‎2024-04-05 02:54 AM

In response to DCIM_Support
0 Likes
0
1039
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:33 PM . Last Modified: ‎2024-04-05 02:54 AM

Hi Javier,

I had already written most of what I did before I got your request. I know something similar has already been requested so I'm going to add this thread to that request. Please note this isn't something they're actively looking at so I can't say when or if this will actually make it into the product.

 

Steve

(CID:128748971)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:33 PM . Last Modified: ‎2024-04-05 02:54 AM

In response to DCIM_Support
0 Likes
0
1039
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:33 PM . Last Modified: ‎2024-04-05 02:54 AM

Thank you Steven.

(CID:128749465)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 01:33 PM . Last Modified: ‎2023-10-20 04:59 AM

0 Likes
0
1039
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 01:33 PM . Last Modified: ‎2023-10-20 04:59 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore