Accuracy of AP7152 / AP7155 / AP7175 power meters

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Accuracy of AP7152 / AP7155 / AP7175 power meters
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:13 AM . Last Modified: β€Ž2024-04-05 04:39 AM

0 Likes
3
1450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:13 AM . Last Modified: β€Ž2024-04-05 04:39 AM

Accuracy of AP7152 / AP7155 / AP7175 power meters

Hello,

I have a question about the accuracy of AP7152(B) / AP7155(B) / AP7175(B) power meters. We would like to measure our colocated costumer power consumption and allow them access to these power meters. My question is how sensitive or accurate are they ? Are we able to use them for this purpose or do we have to buy something else from Schneider / APC ? 

 

PS: We want to measure instant power and energy used over a period of time.

 

Thanks a lot,

Peter

(CID:126159838)

Labels
  • Labels:
  • Building Operations
  • Data Center Expert
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:13 AM . Last Modified: β€Ž2024-04-05 04:39 AM

0 Likes
0
1450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:13 AM . Last Modified: β€Ž2024-04-05 04:39 AM

Hi petru bunea,

In continuation of your old theme , I can answer: I was also interested in this issue recently, i.e. accuracy of measurements, and could not find any official documentation. Therefore, I made practical measurements and now I get such interesting information.

Regarding old power meters AP7152, AP7155 and AP7175: I repeat, this power meters is already discontinued. This discontinued power meters has the latest firmware is rpdu v3.9.2, therefore, we have the following measurement characteristics:

  • current consumption measurement: YES
  • minimum measured current consumption: 1A
  • accuracy of measuring the current consumption (in the range >1A): 0.1A
  • measuring the input voltage: NO (the nominal voltage constant is stored in the ROM of the power meter, for example, 231V)
  • power consumption measurement: software (by multiplying the measured current consumption by the constant of the nominal voltage)
  • measurement of consumed electrical energy: NO

Therefore, these old power meters can not be used if:

  • the power of the customer equipment is less than 231V * 1A = 231W (for powerlines with a nominal voltage of 231V);

  • the input voltage is not exactly the nominal voltage of the power meter, for example, instead of 231V (for powerlines with a nominal voltage of 231V) is supplied 220V. Then the calculated power will be absolutely wrong.

Therefore, if the power of the customer equipment exceeds 231W (for powerlines with a nominal voltage of 231V), then the accuracy of power calculation will be 231V * 0.1A = 23W.

And at last, it will be necessary to calculate the consumed electrical energy by third-party software. Moreover, the accuracy of the calculation will be higher the more often the measurements are performed (for example, for a DCE-server - this is not more often than once per minute).

Regarding new power meters AP7152B, AP7155B and AP7175B: this power meters has the latest firmware is rpdu2g v6.4.4, therefore, we have the following measurement characteristics:

  • current consumption measurement: YES
  • minimum measured current consumption: 0.5A
  • accuracy of measuring the current consumption (in the range >0.5A): 0.1A
  • measuring the input voltage: YES
  • accuracy of measuring the input voltage (in the range of nominal voltage): 1V
  • power consumption measurement: YES
  • accuracy of measuring the power consumption (in the range >100W): 10W
  • measurement of consumed electrical energy: YES
  • accuracy of measuring the electrical energy (in the range >100W): 0.1kW*h

Therefore, these new power meters can not be used only if:

  • the power of the customer equipment is less than 100W (for powerlines with a nominal voltage of 231V).

Therefore, if the power of the customer equipment exceeds 100W (for powerlines with a nominal voltage of 231V), then the accuracy of power measurement will be 10W and the accuracy of electrical energy will be 0.1kW*h.

I hope I answered your question and it will help you.

P.S.: also I hope that I fully answered your previous question  πŸ˜€.

(CID:126160061)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:13 AM . Last Modified: β€Ž2024-04-05 04:39 AM

0 Likes
0
1450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:13 AM . Last Modified: β€Ž2024-04-05 04:39 AM

Hi petru bunea,

Have you been able to solve this issue or not?

With respect.

(CID:126163999)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 12:13 AM . Last Modified: β€Ž2023-10-20 04:58 AM

0 Likes
0
1450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 12:13 AM . Last Modified: β€Ž2023-10-20 04:58 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore