Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

APC Rack PDU 9000 Series ITA and DCE compatibility

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • APC Rack PDU 9000 Series ITA and DCE compatibility
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
0g
0g
Contributor

Posted: ‎2023-03-28 02:11 PM

1 Like
7
2107
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-28 02:11 PM

APC Rack PDU 9000 Series ITA and DCE compatibility

Hello,

 

Can someone please confirm if the 9000 series rack PDUs work with Data Center Expert and IT Advisor?

We are looking at the APDU9966 model and I would like to ensure it works seamlessly with DCE and ITA.

 

For DCE, I refer to being able to perform mass configurations and mass firmware upgrades.

For ITA, I refer to seeing the measured power data per phase from DCE.

 

We are looking to acquire PDUs soon so I would appreciate if someone can look into this in a timely manner.

 

Thanks

 

 

Labels
  • Labels:
  • Data Center Expert
  • DCIM Support
  • IT Advisor
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
Shaun
Shaun Leader
Leader

Posted: ‎2023-03-29 01:23 AM

0 Likes
4
2094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-29 01:23 AM

Hi @0g ,

 

The 9000 series has full feature parity in DCE.  I can't promise for ITA, but based on on my understanding of the components involved, I'd assume the same.

Reply

Link copied. Please paste this link to share this article on your social media post.

0g
0g
Contributor

Posted: ‎2023-03-29 08:21 AM

In response to Shaun
0 Likes
3
2085
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-29 08:21 AM

Thanks @Shaun, I know when the 9000 series was initially released the mass config and upgrades was not an option in DCE, most likely due to the firmware version so I wanted to make sure that was addressed.

 

@gsterling I was looking in ITA 9.3.10 and there are no genomes for the 9000 series PDUs.

Any idea when APDU9966 might be added so that the outlet mapping works?

I believe that's part of the genome extended information.

Reply

Link copied. Please paste this link to share this article on your social media post.

gsterling
gsterling Mentor
Mentor

Posted: ‎2023-03-29 12:27 PM

In response to 0g
0 Likes
2
2075
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-29 12:27 PM

Hello. There are at least some of the APDU9xxx models in the ITA genome library, perhaps your library is out of date? The below image is from my ITA 9.3.x server.

 

APDUs.JPG

The APDU9966 in my library is a standard genome and not extended so it does not allow outlet level connections in ITA. If that is required we should request extended genome properties be added to that rack pdu model.

 

Regards

 

Greg Sterling

Reply

Link copied. Please paste this link to share this article on your social media post.

0g
0g
Contributor

Posted: ‎2023-03-30 08:23 AM

In response to gsterling
0 Likes
1
2063
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-30 08:23 AM

Hi Greg, thanks for the fast response.

After further looking into it I see that Rack PDU 9966 was part of the genome library version 10-21
In the ITA about window I saw Current genome library generated: 3/17/23 9:34 AM and I assumed it was up to date.  I downloaded the latest genome package from the entitlements website and I saw that model along others listed as new.  I was under the impression that an upgrade would also upgrade the genomes but I guess that's not the case.  I will request APDU9966 to get the extended genome properties.

Reply

Link copied. Please paste this link to share this article on your social media post.

gsterling
gsterling Mentor
Mentor

Posted: ‎2023-03-30 10:51 AM

In response to 0g
0 Likes
0
2057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-30 10:51 AM

Upgrades should update the library if a genome update has occurred since the version you are running. If you provisioned a new ITA server and restored a backup file, the restore will restore the version of the genome database from the backup file and overwrite a newer genome database if that was present before the restore.

 

From what version of ITA did you upgrade to 9.3.10?

 

Regards

 

Greg Sterling

Reply

Link copied. Please paste this link to share this article on your social media post.

0g
0g
Contributor

Posted: ‎2023-04-06 10:26 AM

0 Likes
1
1990
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-06 10:26 AM

we upgraded from 9.04.

Reply

Link copied. Please paste this link to share this article on your social media post.

gsterling
gsterling Mentor
Mentor

Posted: ‎2023-04-06 11:30 AM

In response to 0g
0 Likes
0
1986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-06 11:30 AM

Its likely then you changed servers to move from CentOS 7.x to Rocky Linux 8.x. To move from 9.0.4 to 9.3.10 did you have to provision a new ITA server and restore the older ITA backup on the new server?

 

If yes, then the 9.0.4 genome database you had was restored onto 9.3.10.

 

Regards

 

Greg Sterling

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore