Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

APC Modular Remote Power Panel (PDPM277H) kW indication

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • APC Modular Remote Power Panel (PDPM277H) kW indication
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 03:53 PM . Last Modified: ‎2024-04-08 12:49 AM

0 Likes
3
1243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:53 PM . Last Modified: ‎2024-04-08 12:49 AM

APC Modular Remote Power Panel (PDPM277H) kW indication

Hello!

Can someone answer me, please, why such difference in APC Modular Remote Power Panel (PDPM277H) kW indication appears:

 

5.30 kW > 5.0 kW and 5.90 kW > 5.5 kW. So the difference of those two indications are respectively 0.3 kW and 0.4 kW. I thought the "System Output Total Power" should be equal to sum of "Module Output Power".

 

Best regards,

Janis Magazeinis

(CID:118001986)

Labels
  • Labels:
  • Data Center Expert
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 03:53 PM . Last Modified: ‎2024-04-08 12:49 AM

0 Likes
1
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:53 PM . Last Modified: ‎2024-04-08 12:49 AM

Hi Janis,

 

Assuming the values that are being summed are coming directly from the device and assuming that the "System Output Total Power" is coming from the device as well, it would appear to be a device accuracy issue.

Can you verify the output of the device? I'm assuming this is a modbus device so polling this from a gateway or 3rd party system should be able to tell you if the numbers shown for the modules are accurate or if the DDF is rounding the numbers. If it is SNMP, the same can be done with a 3rd party SNMP utility.

 

If when polling the device externally the numbers show up as 0.7 , 0.8, and 0.4 or even 7, 8, and 4. then the device is likely limiting the accuracy itself. If it is showing as something more like 72, 85, and 44, then it would appear to be the DDF rounding down. 

 

The DDF team may have a better idea if the DDF itself is set up that way and hopefully they'll take a look at this too.

 

Thanks,

Steve

(CID:118002002)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 03:53 PM . Last Modified: ‎2024-04-08 12:49 AM

0 Likes
1
1245
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:53 PM . Last Modified: ‎2024-04-08 12:49 AM

Hi Janis,

 

Assuming the values that are being summed are coming directly from the device and assuming that the "System Output Total Power" is coming from the device as well, it would appear to be a device accuracy issue.

Can you verify the output of the device? I'm assuming this is a modbus device so polling this from a gateway or 3rd party system should be able to tell you if the numbers shown for the modules are accurate or if the DDF is rounding the numbers. If it is SNMP, the same can be done with a 3rd party SNMP utility.

 

If when polling the device externally the numbers show up as 0.7 , 0.8, and 0.4 or even 7, 8, and 4. then the device is likely limiting the accuracy itself. If it is showing as something more like 72, 85, and 44, then it would appear to be the DDF rounding down. 

 

The DDF team may have a better idea if the DDF itself is set up that way and hopefully they'll take a look at this too.

 

Thanks,

Steve

(CID:118002002)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 03:53 PM . Last Modified: ‎2024-04-08 12:48 AM

In response to DCIM_Support
0 Likes
0
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:53 PM . Last Modified: ‎2024-04-08 12:48 AM

Hi Steven Marchetti and Janis Magazeinis,

I can supplement the question of Janis Magazeinis with the details that Steven Marchetti asks, i.e.:

Can you verify the output of the device? ...

Since I have to use a certain amount of PDPM277H and every year during the next visit of Schneider Electric service personnel, I ask them the same question very similar to the question Janis Magazeinis.

For clarity, I divided the SNMP output into several parts. All parts, i.e. SNMP requests were made for the same PDPM277H device for all inserted modules and at the same time (about 3...5sec).

textPDPM277H Total System OutputsSystem Output Voltage Phase to Neutral - /10V: SNMPv2-SMI::enterprises.318.1.1.22.4.1.15.1.3.1 = INTEGER: 2279 SNMPv2-SMI::enterprises.318.1.1.22.4.1.15.1.3.2 = INTEGER: 2282 SNMPv2-SMI::enterprises.318.1.1.22.4.1.15.1.3.3 = INTEGER: 2283 System Output Voltage Phase to Phase - /10V: SNMPv2-SMI::enterprises.318.1.1.22.4.1.15.1.4.1 = INTEGER: 3937 SNMPv2-SMI::enterprises.318.1.1.22.4.1.15.1.4.2 = INTEGER: 3937 SNMPv2-SMI::enterprises.318.1.1.22.4.1.15.1.4.3 = INTEGER: 3937 System Output Current per Phases - /10A: SNMPv2-SMI::enterprises.318.1.1.22.4.2.11.1.3.1 = INTEGER: 121 SNMPv2-SMI::enterprises.318.1.1.22.4.2.11.1.3.2 = INTEGER: 222 SNMPv2-SMI::enterprises.318.1.1.22.4.2.11.1.3.3 = INTEGER: 141 System Output Power per Phases - /10kW: SNMPv2-SMI::enterprises.318.1.1.22.4.3.5.1.2.1 = INTEGER: 26 SNMPv2-SMI::enterprises.318.1.1.22.4.3.5.1.2.2 = INTEGER: 47 SNMPv2-SMI::enterprises.318.1.1.22.4.3.5.1.2.3 = INTEGER: 30 Total System Output Power - /10kW: SNMPv2-SMI::enterprises.318.1.1.22.4.3.1.0 = INTEGER: 104textPDPM277H Breakers Output Current per Phases and per ModulesBreakers Output Current per Phases and per Modules - /10A: SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.1.1 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.1.2 = INTEGER: 6 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.1.3 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.2.1 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.2.2 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.2.3 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.3.1 = INTEGER: 5 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.3.2 = INTEGER: 20 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.3.3 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.4.1 = INTEGER: 18 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.4.2 = INTEGER: 18 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.4.3 = INTEGER: 17 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.5.1 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.5.2 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.5.3 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.6.1 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.6.2 = INTEGER: 8 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.6.3 = INTEGER: 14 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.9.1 = INTEGER: 13 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.9.2 = INTEGER: 39 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.9.3 = INTEGER: 14 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.10.1 = INTEGER: 6 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.10.2 = INTEGER: 6 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.10.3 = INTEGER: 45 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.11.1 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.11.2 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.11.3 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.12.1 = INTEGER: 26 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.12.2 = INTEGER: 19 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.12.3 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.13.1 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.13.2 = INTEGER: 12 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.13.3 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.14.1 = INTEGER: 21 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.14.2 = INTEGER: 32 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.14.3 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.15.1 = INTEGER: 24 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.15.2 = INTEGER: 36 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.15.3 = INTEGER: 21 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.16.1 = INTEGER: 8 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.16.2 = INTEGER: 29 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.9.16.3 = INTEGER: 30textPDPM277H Breakers Output Power per Phases and per ModulesBreakers Output Power per Phases and per Modules - /10kW: SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.1.1 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.1.2 = INTEGER: 1 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.1.3 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.2.1 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.2.2 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.2.3 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.3.1 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.3.2 = INTEGER: 3 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.3.3 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.4.1 = INTEGER: 3 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.4.2 = INTEGER: 3 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.4.3 = INTEGER: 3 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.5.1 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.5.2 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.5.3 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.6.1 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.6.2 = INTEGER: 1 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.6.3 = INTEGER: 3 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.9.1 = INTEGER: 2 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.9.2 = INTEGER: 8 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.9.3 = INTEGER: 2 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.10.1 = INTEGER: 1 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.10.2 = INTEGER: 1 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.10.3 = INTEGER: 9 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.11.1 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.11.2 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.11.3 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.12.1 = INTEGER: 5 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.12.2 = INTEGER: 4 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.12.3 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.13.1 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.13.2 = INTEGER: 2 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.13.3 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.14.1 = INTEGER: 4 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.14.2 = INTEGER: 6 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.14.3 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.15.1 = INTEGER: 4 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.15.2 = INTEGER: 7 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.15.3 = INTEGER: 4 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.16.1 = INTEGER: 1 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.16.2 = INTEGER: 6 SNMPv2-SMI::enterprises.318.1.1.22.2.4.1.11.16.3 = INTEGER: 6textPDPM277H Modules Output Power (3ph mod - summ, 1-ph mod - per lines)Modules Output Power (3ph mod - summ, 1-ph mod - per lines) - /10kW: SNMPv2-SMI::enterprises.318.1.1.22.2.6.1.20.1.1 = INTEGER: 1 SNMPv2-SMI::enterprises.318.1.1.22.2.6.1.20.2.1 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.6.1.20.3.1 = INTEGER: 5 SNMPv2-SMI::enterprises.318.1.1.22.2.6.1.20.4.1 = INTEGER: 11 SNMPv2-SMI::enterprises.318.1.1.22.2.6.1.20.5.1 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.6.1.20.6.1 = INTEGER: 5 SNMPv2-SMI::enterprises.318.1.1.22.2.6.1.20.9.1 = INTEGER: 2 SNMPv2-SMI::enterprises.318.1.1.22.2.6.1.20.9.2 = INTEGER: 8 SNMPv2-SMI::enterprises.318.1.1.22.2.6.1.20.9.3 = INTEGER: 2 SNMPv2-SMI::enterprises.318.1.1.22.2.6.1.20.10.1 = INTEGER: 1 SNMPv2-SMI::enterprises.318.1.1.22.2.6.1.20.10.2 = INTEGER: 1 SNMPv2-SMI::enterprises.318.1.1.22.2.6.1.20.10.3 = INTEGER: 10 SNMPv2-SMI::enterprises.318.1.1.22.2.6.1.20.11.1 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.1.22.2.6.1.20.12.1 = INTEGER: 9 SNMPv2-SMI::enterprises.318.1.1.22.2.6.1.20.13.1 = INTEGER: 2 SNMPv2-SMI::enterprises.318.1.1.22.2.6.1.20.14.1 = INTEGER: 11 SNMPv2-SMI::enterprises.318.1.1.22.2.6.1.20.15.1 = INTEGER: 16 SNMPv2-SMI::enterprises.318.1.1.22.2.6.1.20.16.1 = INTEGER: 14

Thus, by following some simple math, you can see a lot of "inconsistencies".

For example, for a three-phase module number 16, assuming that we have a purely active load (power factor = 1), the total real power should be:

227.9V*0.8A+228.2V*2.9A+228.3V*3.0A=0.18232kW+0.66178kW+0.6849kW=1.529kW

And instead we have according to SNMP output for module number 16:

0.1kW, 0.6kW and 0.6kW respectively (summ 1.3kW) and total power 1.4kW

And such rounding inside the device can be found pretty much from the level of a separate breaker, and ending with the level of the entire device as a whole.

Thus, you can verify, that the above inaccuracy does not apply to either the DCE-server or its DDF-files, but only to the PDPM277H device. I.e., as people usually say in such cases: "working as designed" 😀.

With respect.

(CID:118002982)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 03:54 PM . Last Modified: ‎2023-10-20 04:56 AM

0 Likes
0
1244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:54 PM . Last Modified: ‎2023-10-20 04:56 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore