ViewX Crashing
Hi appear to having issues with ViewX crashing after Ive logged into it. Running the latest May 2020 version.
.Net Runtime error appeared
The process was terminated to unhandled exception
Any thoughts on what would cause this type of error? VIewX runs fine on server just gives issues on the client side. WebX version is working fine.
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-08-28 02:43 AM
There is a Geo SCADA 2019 June 2020, and a Geo SCADA 2019 July 2020 update 😉 So you're not quite the 'latest'...
If you have a .NET Runtime error then my thoughts are that someone has uninstalled one of the required .NET versions after having installed ViewX.
My recommendation would be to uninstall ViewX from this client, and re-install ViewX (only). It should re-install the .NET prerequisites also.
If it still causes a repeatable error, then you will want to raise it as a support ticket with your local Tech Support. The logs etc may reveal some more information, and you can potentially work around the issue if you can identify it as being something about a particular mimic etc, but raising it with tech support to get investigated and fixed long term is the way forward.
Lead Control Systems Engineer for Alliance Automation (VIC).