Update query for Digital points

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Update query for Digital points
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxureโ„ข Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Anonymous user
Not applicable

Posted: โ€Ž2020-01-24 05:07 AM . Last Modified: โ€Ž2023-05-03 12:18 AM

0 Likes
7
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-01-24 05:07 AM . Last Modified: โ€Ž2023-05-03 12:18 AM

Update query for Digital points

Is it possible to use Update query to Update one of the Identification property of a Digital point.

But I am not able to do it

 

I used

UPDATE CDBOUTSTATION

SET Description = Newsite

WHERE

ID='10000'

 

The error i get is The query statement is malfunctioned or invalid. Column Newsite not found..... Equality operation '=' cannot be used with Integer and String.

 

Is it possible to use Update for Strings ?

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
AndrewScott
Admiral AndrewScott
Admiral

Posted: โ€Ž2020-01-24 05:19 AM

0 Likes
6
3240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-01-24 05:19 AM

The first error "Column Newsite not found." is occurring because Newsite is missing the enclosing single quotes to make it a string literal (assuming Description is a string field).

The second error "Equality operation '=' cannot be used with Integer and String." is occurring because the ID column is an integer but the value it is being compared with is a string literal (it is enclosed in quotes).

The updated query is:

 

UPDATE CDBOUTSTATION
SET Description = 'Newsite'
WHERE
ID=10000

 

 


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2020-01-24 05:40 AM

In response to AndrewScott
0 Likes
5
3237
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-01-24 05:40 AM

I tried other way as well.

The error i get for that is

The results cannot be displayed. 

DML statements not supported from lists

Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: โ€Ž2020-01-24 05:49 AM

In response to Anonymous user
0 Likes
4
3233
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-01-24 05:49 AM

A list in ViewX (or WebX) is used to display the result set from a query so requires a SELECT statement.

 

To execute DML statements (UPDATE, CREATE or DELETE) you need to use a different application. The Query Pad tool that comes with ClearSCADA can be used for this purpose.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: โ€Ž2020-01-24 05:59 AM

In response to AndrewScott
0 Likes
3
3230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-01-24 05:59 AM

Look up QueryPad in the help.

Enter query in the lower pane.

Hint - hold Ctrl key down when pressing Enter to execute a query.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2020-02-12 08:28 AM

In response to sbeadle
0 Likes
2
3159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-02-12 08:28 AM

It does work but I used Point ID to update. I wanted to update the Description of a point, But  it had cleared other point descriptions on the same template except the one which I wanted to update. I tried several ways to check it but nothing helped and now I have to manually or use update query to update other points on the same template. And it does not throw up any error.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Hardin4019
Lieutenant Hardin4019
Lieutenant

Posted: โ€Ž2020-02-12 09:18 AM

In response to Anonymous user
0 Likes
0
3150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-02-12 09:18 AM

If the Point you are trying to update is in an Instance of a Template, is the Attribute of that Point you are trying to update included in the Property Overrides of the Template? If not, you could change the attribute in the template to say "Newsite", then it will be set to all of the instances.

 

If the Point Attribute is already included in the Property Overrides of the Template, then only new Instances of the original Template would say this. Which is likely part of what you would like to happen.

 

To go back and fill in the attribute on Instances of the Template where the Property Override for the Attribute is already turned on and the Attribute is blank for many of the Instances, you likely need to take a slightly different approach.

 

One way I have updated Point.objDescription attributes is to setup a Function Block Diagram set to an interval of 0 seconds in the Template, then map out somewhere that has the objDescription I desire, or even a Constant in the FBD, to the Point.objDescription. Then there are two ways to execute all of the FBD's, either manually one at a time, or by creating a Structured Text program that finds all of the FBD's of a particular name and executing them.

 

The second way is much like the ST program mentioned just above for executing a FBD with the time interval set to 0 seconds. Write a ST program with a Query in it that will find all of the Instances of a particular template, and will update the Point.Attribute. Of course some care needs to be taken in setting up the query to not update Instances of the Template you don't want it to. For instance having the ST Query only return results where the Point.Attribute is empty, or in a specific Group, etc.

Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: โ€Ž2020-02-12 01:42 PM

In response to Anonymous user
0 Likes
0
3142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-02-12 01:42 PM

I think you should just tell us what it is you're ultimately trying to do.

Only giving us a small part of the puzzle results in us giving you the wrong puzzle solution.

 

 

If I were to guess, you want to update all instances of a point (which derives from a template site/device) so that some aspect of the point description will relate back to the site in which it is actually contained.  Correct?

 

So the way that I would do this is:  QueryPad

 

If you have your template like

SiteTemplate

 -> Devices

   -> Pump 1

     -> Running

 

and you want the Running point Description to be updated to say 'Site Name - Pump 1 - Running'

Then you could do this as (@sbeadle no SQL code entry ๐Ÿ˜ž )

UPDATE CDBPoint

SET Description = ParentGroupId->ParentGroupId->ParentGroupId->Name || ' - ' || ParentGroupId->Name || ' - ' || Name

WHERE Name='Running'

AND ParentGroupId->ParentGroupId->ParentGroupId->TemplateId=[MAGIC NUMBER]


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore