Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).
Search in
Please select a country to continue with beta search.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-06 04:07 AM
Hello,
In the Geo SCADA Expert 2023 November 2024 version, I had a question about the data I received via Modbus TCP communication. I need to scale the analog input data I receive from the PLC in the field. For this, I use the scaling section in the signal's Properties-Analog Point and enter the scale values given to me as Fullscale and Zeroscale, but the value I read seems quite irrelevant to the value in the field. Is there anywhere else I should check regarding this situation?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-08 01:36 AM
Check the driver log to see the raw value.
See in the help for the secion 'Define the Point Scaling' in the Driver Reference | Modbus - Advanced | Configuring Analog Points.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-08 01:36 AM
Check the driver log to see the raw value.
See in the help for the secion 'Define the Point Scaling' in the Driver Reference | Modbus - Advanced | Configuring Analog Points.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.