Posted: 2025-05-06 04:07 AM
Hello,
In the Geo SCADA Expert 2023 November 2024 version, I had a question about the data I received via Modbus TCP communication. I need to scale the analog input data I receive from the PLC in the field. For this, I use the scaling section in the signal's Properties-Analog Point and enter the scale values given to me as Fullscale and Zeroscale, but the value I read seems quite irrelevant to the value in the field. Is there anywhere else I should check regarding this situation?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-08 01:36 AM
Check the driver log to see the raw value.
See in the help for the secion 'Define the Point Scaling' in the Driver Reference | Modbus - Advanced | Configuring Analog Points.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-08 01:36 AM
Check the driver log to see the raw value.
See in the help for the secion 'Define the Point Scaling' in the Driver Reference | Modbus - Advanced | Configuring Analog Points.