SOAP XML - Method Override CDBPoint

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • SOAP XML - Method Override CDBPoint
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
319
AndrewScott
Admiral AndrewScott
114
BevanWeiss
Spock BevanWeiss
97
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-11-02 07:17 AM . Last Modified: ‎2023-05-03 12:00 AM

0 Likes
4
2213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-02 07:17 AM . Last Modified: ‎2023-05-03 12:00 AM

SOAP XML - Method Override CDBPoint

I am testing the XML SOAP of Geo SCADA Expert. The software used is SOAPUI 5.6.

I would like to execute "Override" method through SOAP.

I am able to execute this method without argument (here below the syntax of the SOAP xml query).

 

 

 

<soapenv:Envelope xmlns:soapenv="http://schemas.xmlsoap.org/soap/envelope/" xmlns:scx6="http://serck-controls.com/webservices/SCX6/">
   <soapenv:Header/>
   <soapenv:Body>
      <scx6:ExecuteMethod>
         <scx6:Object>_TESTS.PointAnalogTest</scx6:Object>
         <scx6:Method>Override</scx6:Method>
         <!--Optional:-->
         <scx6:Arguments>
            <!--1 or more repetitions:-->
            <scx6:Argument></scx6:Argument>
         </scx6:Arguments>
      </scx6:ExecuteMethod>
   </soapenv:Body>
</soapenv:Envelope>

 

 

 

The reply is OK.

 

However, when I set an argument such as 2 (here below), error occurs.

 

 

 

<soapenv:Envelope xmlns:soapenv="http://schemas.xmlsoap.org/soap/envelope/" xmlns:scx6="http://serck-controls.com/webservices/SCX6/">
   <soapenv:Header/>
   <soapenv:Body>
      <scx6:ExecuteMethod>
         <scx6:Object>_TESTS.PointAnalogTest</scx6:Object>
         <scx6:Method>Override</scx6:Method>
         <!--Optional:-->
         <scx6:Arguments>
            <!--1 or more repetitions:-->
            <scx6:Argument>2</scx6:Argument>
         </scx6:Arguments>
      </scx6:ExecuteMethod>
   </soapenv:Body>
</soapenv:Envelope>

 

 

 

Does somebody have any idea how to send argument through the method in SOAP ? which syntax is needed ?

Thank by advance,

Labels
  • Labels:
  • SCADA
  • Telemetry
  • WebX
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2021-11-03 06:12 AM

In response to Anonymous user
0 Likes
1
2182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-03 06:12 AM

Sorry, I forgot to mention that you also need to define the xsi namespace for the xsi:type attribute:

 

<soapenv:Envelope xmlns:soapenv="http://schemas.xmlsoap.org/soap/envelope/" xmlns:scx6="http://serck-controls.com/webservices/SCX6/" xmlns:xsi="http://www.w3.org/2001/XMLSchema-instance">
   <soapenv:Header/>
   <soapenv:Body>
      <scx6:ExecuteMethod>
         <scx6:Object>_TESTS.PointAnalogTest</scx6:Object>
         <scx6:Method>Override</scx6:Method>
         <!--Optional:-->
         <scx6:Arguments>
            <!--1 or more repetitions:-->
            <scx6:Argument xsi:type="xsd:double">12</scx6:Argument>
         </scx6:Arguments>
      </scx6:ExecuteMethod>
   </soapenv:Body>
</soapenv:Envelope>

 


Andrew Scott, R&D Principal Technologist, AVEVA

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2021-11-03 02:50 AM

0 Likes
3
2194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-03 02:50 AM

The <scx6:Argument> element is missing the xsi:type attribute to define what kind of value the argument is.

For example, for an analogue point override using double precision floating point value:

<scx6:Argument xsi:type="xsd:double">12.34</scx6:Argument>

 


Andrew Scott, R&D Principal Technologist, AVEVA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-11-03 04:07 AM

In response to AndrewScott
0 Likes
2
2191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-03 04:07 AM

Justed checked.

The reply of the scada is unfortunately NOK: "the request body was not valid" whatever the xsd type (like int, float, double, short, long, etc.). Here below the print screen.

 

reply.png

 

It becomes better when "xsi" and the value are removed...

 

reply2.png

 

event logs.png

It seem working properly, however no value is sent...

Any idea ? Are you sure of the syntax ? Is there no error message from the soap server when the type is wrong ?

Attachments
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2021-11-03 06:12 AM

In response to Anonymous user
0 Likes
1
2183
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-03 06:12 AM

Sorry, I forgot to mention that you also need to define the xsi namespace for the xsi:type attribute:

 

<soapenv:Envelope xmlns:soapenv="http://schemas.xmlsoap.org/soap/envelope/" xmlns:scx6="http://serck-controls.com/webservices/SCX6/" xmlns:xsi="http://www.w3.org/2001/XMLSchema-instance">
   <soapenv:Header/>
   <soapenv:Body>
      <scx6:ExecuteMethod>
         <scx6:Object>_TESTS.PointAnalogTest</scx6:Object>
         <scx6:Method>Override</scx6:Method>
         <!--Optional:-->
         <scx6:Arguments>
            <!--1 or more repetitions:-->
            <scx6:Argument xsi:type="xsd:double">12</scx6:Argument>
         </scx6:Arguments>
      </scx6:ExecuteMethod>
   </soapenv:Body>
</soapenv:Envelope>

 


Andrew Scott, R&D Principal Technologist, AVEVA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-11-03 06:28 AM

In response to AndrewScott
0 Likes
0
2178
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-03 06:28 AM

Hi,

It is working now.

Good job. Thank you so much.

Cheers,

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore