Re-Evaluate Redirection Alarms from Logic (or other redirection)

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Re-Evaluate Redirection Alarms from Logic (or other redirection)
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
307
AndrewScott
Admiral AndrewScott
96
BevanWeiss
Spock BevanWeiss
90
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
36
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
MichaelAur
Ensign MichaelAur
Ensign

Posted: ‎2025-05-12 01:08 AM

0 Likes
2
91
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-12 01:08 AM

Re-Evaluate Redirection Alarms from Logic (or other redirection)

Hello all,

Is there some way to trigger a re-evaluation of alarm escalation on one point based on the change of state on another point? 

The reason I am trying to do this is that we have some points that are related in the field and we want escalations based on if the field states changed correctly. For example, we have Mains Failed and Genset Running points set up as below.

  • Mains Failure:

    • Triggers a low-level alarm by default

    • Has escalation 1 set to critical after 10min and enabled (trigger type 3)
    • Has escalation 2 & 3 set to high after 4 then critical 8 hours and enabled (trigger type 3)
  •  

  • Generator Running:

    • Triggers low-level alarm by default

    • Has escalation 1&2 set to high after 4 then critical after 8 hours and enabled (trigger type 3)
    • Has escalation 3 set to high after 30min and disabled (trigger type 0)

We disable escalation 1 of Mains Failure when the generator is running (as things have worked as meant and the generator turned on automatically) but problem comes when we try enable escalation 3 of generator running when mains is restored (as we want to know if the generator has stayed on after it should have turned off). While we can cause this escalation to be enabled it misses its trigger condition and therefore never triggers this earlier alarm escalation. I know you can trigger a re-evaluation on the same point when state changes (using alarm redirection> change priority action), but im unsure how to go about triggering it on one point based on the change of another point. 

If anyone knows how to do this or has some advice on an alternative/more effective way to trigger this behaviour i would love to hear. 

Labels
  • Labels:
  • Logic
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MichaelAur
Ensign MichaelAur
Ensign

Posted: ‎2025-05-13 12:56 AM . Last Modified: ‎2025-05-14 09:40 PM

1 Like
0
50
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-13 12:56 AM . Last Modified: ‎2025-05-14 09:40 PM

Hey Adam,

 

Thanks for your reply. Your right there is the RestartRedirection function which I overlooked the first time, thinking it was for only if you had stopped redirection. I found this Knowledge Base useful Restarting Alarm Redirection - Schneider Electric Community.
I ended up creating a script which I execute whenever mains available changes state, and in this I enable/disable the redirection. I made it so that all of the redirections that are enabled/disabled are in the 'Conditional' group allowing me to turn them on and off.

(*Triggered by change of state on Mains Available point 
 will enable the redirection on genset running for if both genset and mains are running*)
PROGRAM UpdateRedirectionsOnMainsSupplyChanges
	METHOD
		RestartGensetRunningRedirections AT %M(..Points.Digital Outputs.Genset Running.RestartRedirections):STRING;
		CancelGensetRunningRedirections AT %M(..Points.Digital Outputs.Genset Running.CancelRedirections):STRING;
	END_METHOD
	VAR
		mainsAvailable AT %I(..Points.Digital Outputs.Mains Supply Available): BOOL;
		gensetWithMainsRedirection AT %Q(..Points.Digital Outputs.Genset Running.AlarmRedirection.TriggerType7): SINT;
	END_VAR
	
	
	IF mainsAvailable THEN
		(*Whenever mains becomes available enable the redirection and then force all 'conditional' redirections to be re-enabled/reevaluated.*)
		gensetWithMainsRedirection:= 3;
		RestartGensetRunningRedirections('Conditional');
	ELSE
		(*Whenever mains is failed disable the redirection and force all 'conditional' redirections to be cancelled.*)
		gensetWithMainsRedirection:= 0;
		CancelGensetRunningRedirections('Conditional');
	END_IF;
	(*Note: This 'conditional' group for redirection is manually setup an will affect all redirecrtions of this group on a specific object*)
END_PROGRAM

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
Lt. Commander

Posted: ‎2025-05-12 08:42 PM . Last Modified: ‎2025-05-12 08:42 PM

1 Like
0
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-12 08:42 PM . Last Modified: ‎2025-05-12 08:42 PM

There is a RestartRedirections method on CAlarmObject that may do what you want but I haven't use it in a long time to see if there are nuances with it. You could can call this directly or from logic triggered as a redirection action when cleared rather than on change?

 

The issue will be the mapping of the source to target, i.e. which points need to clear to restart redirections on a target? Hard-coding it is one option but probably not scalable.

 

If RestartRedirections doesn't work, one less neat option is calling the reprioritise action twice, once -1 and once +1, and restart redirections from that shuffle

Reply

Link copied. Please paste this link to share this article on your social media post.

MichaelAur
Ensign MichaelAur
Ensign

Posted: ‎2025-05-13 12:56 AM . Last Modified: ‎2025-05-14 09:40 PM

1 Like
0
51
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-13 12:56 AM . Last Modified: ‎2025-05-14 09:40 PM

Hey Adam,

 

Thanks for your reply. Your right there is the RestartRedirection function which I overlooked the first time, thinking it was for only if you had stopped redirection. I found this Knowledge Base useful Restarting Alarm Redirection - Schneider Electric Community.
I ended up creating a script which I execute whenever mains available changes state, and in this I enable/disable the redirection. I made it so that all of the redirections that are enabled/disabled are in the 'Conditional' group allowing me to turn them on and off.

(*Triggered by change of state on Mains Available point 
 will enable the redirection on genset running for if both genset and mains are running*)
PROGRAM UpdateRedirectionsOnMainsSupplyChanges
	METHOD
		RestartGensetRunningRedirections AT %M(..Points.Digital Outputs.Genset Running.RestartRedirections):STRING;
		CancelGensetRunningRedirections AT %M(..Points.Digital Outputs.Genset Running.CancelRedirections):STRING;
	END_METHOD
	VAR
		mainsAvailable AT %I(..Points.Digital Outputs.Mains Supply Available): BOOL;
		gensetWithMainsRedirection AT %Q(..Points.Digital Outputs.Genset Running.AlarmRedirection.TriggerType7): SINT;
	END_VAR
	
	
	IF mainsAvailable THEN
		(*Whenever mains becomes available enable the redirection and then force all 'conditional' redirections to be re-enabled/reevaluated.*)
		gensetWithMainsRedirection:= 3;
		RestartGensetRunningRedirections('Conditional');
	ELSE
		(*Whenever mains is failed disable the redirection and force all 'conditional' redirections to be cancelled.*)
		gensetWithMainsRedirection:= 0;
		CancelGensetRunningRedirections('Conditional');
	END_IF;
	(*Note: This 'conditional' group for redirection is manually setup an will affect all redirecrtions of this group on a specific object*)
END_PROGRAM

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of