Querying compressed historic values for per minute values
We are attempting to get per minute historic results using a SQL query. The queried point uses historic compression during storage. Since compression is abled for "significant change", there are minutes that do not have a value in the result set. How do we get a result set with a value per minute, regardless of whether the there is a stored historic value (i.e. data changed significantly or not)?
- Labels:
-
SCADA
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-23 01:37 AM
You may find it convenient to configure a Historic View - a new virtual SQL table. This can be set to a 1 minute interval, and you can pick the type of summarisation, e.g. End Last. The View will give you a column with a quality number, telling you if that 1 minute sample was derived from adjacent values or one/more vales in each 1 minute window. Search for 'Create a Historic View' in F1 help.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-22 01:32 AM
Which algorithm are you using to process the historic data?
An interpolated algorithm will give you values for periods where there is no data.
For example: Average Interpolated
Andrew Scott, R&D Principal Technologist, AVEVA
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-23 01:37 AM
You may find it convenient to configure a Historic View - a new virtual SQL table. This can be set to a 1 minute interval, and you can pick the type of summarisation, e.g. End Last. The View will give you a column with a quality number, telling you if that 1 minute sample was derived from adjacent values or one/more vales in each 1 minute window. Search for 'Create a Historic View' in F1 help.