Persistence on SCADA Point State Alarms on Analogs

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Persistence on SCADA Point State Alarms on Analogs
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
307
AndrewScott
Admiral AndrewScott
95
BevanWeiss
Spock BevanWeiss
89
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
36
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
rlao
Lt. Commander rlao
Lt. Commander

Posted: ‎2020-07-14 12:06 AM . Last Modified: ‎2023-05-03 12:12 AM

0 Likes
6
3823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-14 12:06 AM . Last Modified: ‎2023-05-03 12:12 AM

Persistence on SCADA Point State Alarms on Analogs

So this has been an issue I'm trying to tackle for a good part of the year, and one I've tried a few solutions for but ultimately none of which I've been completely satisfied with yet. So I'm asking for some guidance from those of you more experienced than I am.

 

Basically I'm looking to implement persistence on point state alarms from analog points. For example, if I have a well level reported by a SCADAPack (ranged 0-100%) and it has an alarm on the '1 Low' state of say 30% with an Enabled Unsolicited RTU event. I want to be able to set a persistence time on it for say 5 minutes. This means if the well level goes from 33% to 28% and does not rise back up past 30% within the next 5 minutes, I want ClearSCADA to raise an alarm. However, if the well level goes from 33%->28%->32% within the span of say 2 minutes, I don't want ClearSCADA to raise an alarm on that point at all.

 

Some solutions I have explored:

 

Setting Persistence Into Alarm

 

My understanding is this delays the RTU from generating an event for the point state change from 'Normal' to '1 Low' and if the point returns to the normal state within the persistence delay, it does not even generate the point state change event at all.

 

My experience with this is that it seems to work great for binary points (after getting some forum help) but not so much for analog points. The reason is the change in analog value that triggers the alarm is usually large enough to surpass the event deviation. So the RTU will generate an unsolicited event regardless, not for the actual state change but for the value change. ClearSCADA processes this value change event and updates the point value, immediately raising an alarm despite the delay on 'Persistence Into Alarm'.

 

I've abandoned this approach for now but if there is a way to make it work, I'm all ears.

 

 

Implement persistence as RTU code and the actual alarm as a separate binary point

 

Probably the most robust solution, however I am concerned about the increase in point count as this would mean every analog point will need to be accompanied by one or multiple digital points to store each alarm. If it is to be integrated in a SCADA template, it would mean a lot of extra digital points that need to be created for each possible alarm that could appear on the analog.

 

 

Using 'pending severities' and alarm redirection

 

This is currently where I'm at. I've made some dummy 'pending alarm' severities and used alarm redirection to escalate them (after a delay) to actual alarm severities that the operators can visibly see and act upon.

 

The main issue with this is the pending alarm needs to be somehow acknowledged if it doesn't get escalated into an actual alarm, otherwise the point will just stay in an unack-cleared state. The only way I can see to fix this is to write some logic that's called via redirection on alarm clear to auto-acknowledge that pending alarm.

 

However, my roadblock here is that there does not appear to be an easy way to selectively acknowledge alarms on a CAlarmObject. So if I call the Accept() method via logic, it will acknowledge every alarm on that point rather than only the pending alarm. I think setting a dedicated alarm condition for the pending alarm might be the way to fix this?

 

However I just want to check if this whole approach is really recommended for what I'm trying to achieve here before I put more effort into refining it.

Labels
  • Labels:
  • DNP3
  • Logic
  • SCADA
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-07-16 11:29 PM

0 Likes
0
3786
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-16 11:29 PM

@rlao The way that I normally implement this is using separate RTU/PLC logic for the Analog inputs, since often there is additional logic that applies anyway (e.g. a low flow alarm should only be generated when a pump is running, likewise with a low current alarm etc etc).

If it's possible that such an alarm will perform a site control action also (e.g. Low Low Flow will likely result in the pump being considered faulted after some time, High High Level will likely be an interlock against pumping into the tank etc etc), then you would need to have such alarm generation within the RTU/PLC anyway.

 

I'm with you in regards to the point count increase unfortunately, and I do often generate alarms purely in the SCADA (I really like Time Profiles configured against Alarm Limits for certain 'derived alarms'... like for excessive/insufficient pump runs).  But for standard High / Low alarms where I'm relatively certain that a time delay will be needed then I do this entirely within the RTU and disable the alarms on the Analog Point itself.

It does take the point count from 1 (Analog value) -> lots (Analog value, Transmitter fault, Low Alarm, Low SP, Low Delay SP, Low Low Alarm, Low Low SP, Low Low Delay SP, High Alarm, High SP, High Delay SP, High High Alarm, High High SP, High High Delay SP).. but there's not much that can be done about that.  Having a collection of templates for each 'type' can be helpful to keep the point count a little lower... e.g. often things like Turbidity won't need Low / Low Low alarms, so they can be removed.  Often times there won't be a need for High High / Low Low, and just High / Low will suffice..

 

Using alarm severities for delaying alarms in this manner is likely going to be incredibly difficult to maintain.

Even things like Animations will be tougher, since you won't just be able to look at AlarmState to see if an alarm is active, since it will be, so you'll always need to look at the AlarmSeverity also.

And doing audits on Alarm Severities will be even harder than it currently is, since not only will you need to look at all the different possible Alarm Severity fields on the different objects, but you'll need to look at the alarm redirections, since the as configured severities would only be placeholders for the real severity.

 

I believe an upcoming version of GeoSCADA was going to have some additional settings around delaying alarms.  But I'm unsure how this will be implemented, and I suspect it will be driver dependent also... which might introduce additional weird behaviour like for the SCADAPack points (where doing a Class 0 integrity poll renders any delayed reporting of 'alarm state' moot).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Hardin4019
Lieutenant Hardin4019
Lieutenant

Posted: ‎2020-07-14 06:51 AM

0 Likes
0
3814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-14 06:51 AM

I think you are on the right path with using a Redirection.

 

A few thoughts. 

 

"The main issue with this is the pending alarm needs to be somehow acknowledged if it doesn't get escalated into an actual alarm, otherwise the point will just stay in an unack-cleared state. The only way I can see to fix this is to write some logic that's called via redirection on alarm clear to auto-acknowledge that pending alarm."

 

For Trigger State, are you using "Uncleared - Unacknowledged" ? You could try using just "Uncleared" with an Abort State of "Cleared".

 

"However, my roadblock here is that there does not appear to be an easy way to selectively acknowledge alarms on a CAlarmObject. So if I call the Accept() method via logic, it will acknowledge every alarm on that point rather than only the pending alarm. I think setting a dedicated alarm condition for the pending alarm might be the way to fix this?"

 

It is possible to make a redirection that Acknowledges an alarm condition using a "Alarm Redirection Method Action" and passing along the %ASource% or %OFullName%. Example: Execute( '%ASource%', '%ACondName%', '%ASeverity%') . I use %ASeverity% in mine to make sure that my Redirections can only Acknowledge one particular severity of "pre-alarm" that my operators cannot see.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-07-16 11:29 PM

0 Likes
0
3787
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-16 11:29 PM

@rlao The way that I normally implement this is using separate RTU/PLC logic for the Analog inputs, since often there is additional logic that applies anyway (e.g. a low flow alarm should only be generated when a pump is running, likewise with a low current alarm etc etc).

If it's possible that such an alarm will perform a site control action also (e.g. Low Low Flow will likely result in the pump being considered faulted after some time, High High Level will likely be an interlock against pumping into the tank etc etc), then you would need to have such alarm generation within the RTU/PLC anyway.

 

I'm with you in regards to the point count increase unfortunately, and I do often generate alarms purely in the SCADA (I really like Time Profiles configured against Alarm Limits for certain 'derived alarms'... like for excessive/insufficient pump runs).  But for standard High / Low alarms where I'm relatively certain that a time delay will be needed then I do this entirely within the RTU and disable the alarms on the Analog Point itself.

It does take the point count from 1 (Analog value) -> lots (Analog value, Transmitter fault, Low Alarm, Low SP, Low Delay SP, Low Low Alarm, Low Low SP, Low Low Delay SP, High Alarm, High SP, High Delay SP, High High Alarm, High High SP, High High Delay SP).. but there's not much that can be done about that.  Having a collection of templates for each 'type' can be helpful to keep the point count a little lower... e.g. often things like Turbidity won't need Low / Low Low alarms, so they can be removed.  Often times there won't be a need for High High / Low Low, and just High / Low will suffice..

 

Using alarm severities for delaying alarms in this manner is likely going to be incredibly difficult to maintain.

Even things like Animations will be tougher, since you won't just be able to look at AlarmState to see if an alarm is active, since it will be, so you'll always need to look at the AlarmSeverity also.

And doing audits on Alarm Severities will be even harder than it currently is, since not only will you need to look at all the different possible Alarm Severity fields on the different objects, but you'll need to look at the alarm redirections, since the as configured severities would only be placeholders for the real severity.

 

I believe an upcoming version of GeoSCADA was going to have some additional settings around delaying alarms.  But I'm unsure how this will be implemented, and I suspect it will be driver dependent also... which might introduce additional weird behaviour like for the SCADAPack points (where doing a Class 0 integrity poll renders any delayed reporting of 'alarm state' moot).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

du5tin
Lt. Commander du5tin
Lt. Commander

Posted: ‎2020-08-04 04:38 PM

0 Likes
3
3706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-04 04:38 PM

If you are looking for votes on the solution to use I suggest the RTU logic method... will be the most robust and doesn't rely on data getting to or not getting to ClearSCADA. 

 

I have done the pending alarm severity method before and it isn't great.... To "auto-ack" the alarms you can create a Method object, set it to acknowledge the alarm on the point. Then attach a delayed redirection on the point that will run the method if the alarm isn't escalated after some time. e.g. Auto redirect to accept method object if severity = pending, delay for 15M, only act on Unack'd, Uncleared. It is a bit klugey though and may not be very robust. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-08-04 05:36 PM

In response to du5tin
1 Like
2
3702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-04 05:36 PM

@du5tin Do you run into issues with the point license aspect?

I often see it being a problem, since it really multiplies the point numbers quickly.

i.e. for 20 analog inputs you end up with 280 licensed points... 20x(Value, Tx Fault, High High SP, High High Delay SP, High High Alarm, High SP, High Delay SP, High Alarm, Low SP, Low Delay SP, Low Alarm, Low Low SP, Low Low Delay SP, Low Low Alarm).

 

The Pending Alarm Severity system is pretty terrible though.

Once an alarm is raised in Geo SCADA, I think it's handling of it is pretty good, the alarm raise conditioning needs a little work however (and I think alarm persistence, to mask out rapid spurious alarms, is already upcoming).

I also think that a realignment of certain terminology (and perhaps tweaks to behaviour) might be warranted.

e.g. alarm Disable likely warrants a renaming (or aliasing) to include the term 'shelf'/'shelve' to better align with the ISA-18.2 requirements.  And some counterpoint for the Remove Alarms function.  Like if I accidentally 'remove' the wrong alarm... how do I undo that action?

 

They probably also want to contact the process type people.. like exida, and start getting some more visibility into the Process Industry... I note GeoSCADA Expert isn't referenced here... it could have been good 'advertising'

https://www.exida.com/ebooks/alarm-shelving-exida-ebook.pdf

 


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

du5tin
Lt. Commander du5tin
Lt. Commander

Posted: ‎2020-08-04 05:51 PM

In response to BevanWeiss
0 Likes
1
3700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-04 05:51 PM

We absolutely hit that limit all the time. Clients that do this type of setup are into the 10,000+ point license count on a regular basis for even small systems. 

 

We recently did a project that worked with Allen Bradley Plant PAX and the point list is exactly what you describe. A single analog in the PLC could be over a hundred points in Geo SCADA if we brought over everything. We got our template dialed in to under 30 points. Different mentality designed for a different platform and different data transfer. The alarming is a pain though. You cannot alarm on the analog process variable anymore inside ClearSCADA. You have to use the PLC derived alarms only otherwise it causes operator confusion. 

 

In this case, because the alarm action is so specific and it sounds like persistence isn't doing the trick using on site logic might be a good route.  

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-08-04 06:02 PM

In response to du5tin
0 Likes
0
3698
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-04 06:02 PM

10k points license... you're living the dream.  I'm doing a project with a 5k point license right now... I have a sphincter tightening experience everytime I add a single point that it might be the straw that breaks the camel's back...

 

Things like... 'ohh we want the monthly runtime and starts for each pump' (and we want low / high alarms on them).. just two points... but then across like 60 pumps... they're big multiples when you're only a few hundred points from your license limit.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of