Logs showing evidence of use of HISINFO or HISSTRIP function execution

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Logs showing evidence of use of HISINFO or HISSTRIP function execution
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
NAT
Crewman NAT
Crewman

Posted: ‎2024-09-25 07:14 AM

0 Likes
2
718
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-25 07:14 AM

Logs showing evidence of use of HISINFO or HISSTRIP function execution

Hello,

We are investigating the removal of duplicate data points in the historic data tables which was not performed intentionally by system administrators. We have learned of the functions HISINFO and HISSTRIP.

1. Is there a SCADA log somewhere which will show when the software automatically performed these functions?

2. Is there a subroutine that calls these functions that we can search for in the logs instead?

 

Thanks for any assistance. 

Labels
  • Labels:
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-10-02 03:17 AM

0 Likes
0
655
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-02 03:17 AM

ScxCmd HISSTRIP (and HISINFO) must never be used whilst the server is running. The server must be shutdown before using either of these commands as they can interfere with the operation of the historian, e.g. locking files and blocking access by the historian or more seriously changing files so they don't match the historian's view of the file (granule). You could break main-standby synchronisation by interfering with the files.

 

Historic data optimisation can also be applied by a system administrator to the whole database using the "StartHisOptimisation" method on the "Historian" aggregate of the root group. This can be cancelled using the "CancelHisOptimisation" method. Both of these methods log event journal messages and are recorded in the DB server logs.


Andrew Scott, R&D Principal Technologist, AVEVA

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
Lt. Commander

Posted: ‎2024-10-01 07:41 PM . Last Modified: ‎2024-10-01 07:46 PM

0 Likes
0
675
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-01 07:41 PM . Last Modified: ‎2024-10-01 07:46 PM

There is also the OptimiseData method on CHistoryBase that "removes duplicate records and re-orders data to optimize read operations", which requires the System Admin permission on the object. This doesn't appear to record an event in the Event Journal but does into the DB logs, i.e.:

 

02-OCT-2024 02:27:28.191 03F4 [DBHIS] Object 1: Optimise historic data from granule 22106 to 22111
02-OCT-2024 02:27:28.191 03F4 [DBHIS] Object 1: removed 0 deleted and 0 duplicated records, re-ordered 0 records (1 record total)

 

"Object 1" refers to the object in the database with an id of 1 (it was a blank database I started with), and granule 22106 to 22111 is the number of weeks from 1st Jan 1970 (22110 is the current week, that's how the weekly granules are stored on disk) so you should see corresponding files.

 

Some script (without error checking or permissions checking!) to run the OptmiseData method if it helps:

 

Option Explicit
Public Sub DoSomething
Dim ScxObj
Set ScxObj = Server.FindObject("AI") ' Set to fullname of a point with historic enabled
ScxObj.Interface.Historic.OptimiseData()
End Sub

It would be fairly trivial to write a some script or logic to run this optimise data method on all points, although might be quite disruptive to users depending on how much data and how out of order the data is in the granules/files on disk.

 

scxcmd's HISSTRIP command doesn't seem to generate any event journal or DB log entry. Any Windows auditing you might have enabled such as sysmon might, depending on how that is configured. Does need write permissions to the hrd files rather than authenticate against the Geo SCADA database, so typically limited to Windows administrators, but check the ACLs.

 

The issue with HISSTRIP is that it will need a server restart for the changes to be read by DBServer.exe (unlike the OptmiseData which is done online), and if you have a hot-standby setup then the files on the main will be copied back when you restart. If you have a hot-standby setup you would really need to do a cold restart of the system for the changes to take effect (and if you have duty-duty enabled even more involved!). If it is a standalone server, would just need a restart.

Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-10-02 03:17 AM

0 Likes
0
656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-02 03:17 AM

ScxCmd HISSTRIP (and HISINFO) must never be used whilst the server is running. The server must be shutdown before using either of these commands as they can interfere with the operation of the historian, e.g. locking files and blocking access by the historian or more seriously changing files so they don't match the historian's view of the file (granule). You could break main-standby synchronisation by interfering with the files.

 

Historic data optimisation can also be applied by a system administrator to the whole database using the "StartHisOptimisation" method on the "Historian" aggregate of the root group. This can be cancelled using the "CancelHisOptimisation" method. Both of these methods log event journal messages and are recorded in the DB server logs.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore