Is there a way to automatically log off a user at a certain time? Or can i automatically log off a user after 12 hours regardless of activity?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-03-08 08:14 PM
Not really. There are a few inactivity timeouts that you can configure, but these are all based on inactivity, not a fixed time.
One option if you are keeping current with the latest version of Geo SCADA Expert would be to disable the user account using Logic or similar for a short period of time (perhaps a minute) at the time that you want. With latter versions of Geo SCADA Expert, when a user account is disabled, it also does the appropriate thing and log them out.
It's probably important to note however that this does NOT free up a floating ViewX licence if in use by that client, since ViewX itself will still be connected to the system.
I thought there may have been an System Admin level LogOffUser type of method, but I can't find it in the schema, so it looks like such doesn't exist (unless someone else corrects me)