Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

Incorrect Help documentation for Active Deadband Setup in x70 outstation configuration form

EcoStruxure Geo SCADA Expert Forum

Find out how SCADA systems and networks, like EcoStruxure Geo SCADA Expert, help industrial organizations maintaining efficiency, processing data for smarter decision making with IoT, RTU and PLC devices.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Incorrect Help documentation for Active Deadband Setup in x70 outstation configuration form
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Janeway sbeadle Janeway
216
BevanWeiss
Spock BevanWeiss
81
AndrewScott
Captain AndrewScott
54
AdamWoodland
Commander AdamWoodland Commander
23
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert
product field
Schneider Electric
RemoteConnect for the SCADAPack x70

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
rlao
Lieutenant rlao
Lieutenant

Posted: ‎2023-04-21 12:41 AM . Last Modified: 4 weeks ago

0 Likes
4
145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2023-04-21 12:41 AM . Last Modified: 4 weeks ago

Incorrect Help documentation for Active Deadband Setup in x70 outstation configuration form

In the x70 outstation configuration object in Geo SCADA 2020, there is an active deadband setup configuration item:

 

rlao_0-1682061972072.png

 

The tooltip did not make it clear whether I was meant to check or uncheck the box to withhold Class 0 poll responses during an active time deadband. When I was going through the Geo SCADA help, I noticed that this item has a different description in all Geo SCADA versions of the help files, e.g. 2020 help and 2022 help. It is called 'Filter Class 0 Data' and mentions that ticking the checkbox withholds Class 0 data during an active deadband timer.

 

rlao_2-1682062545931.png

 

When I go onto RemoteConnect, the setting description matches what I see in my version of Geo SCADA ('Always Include Time Deadband in Class 0'). Furthermore, it specifically says that unticking the checkbox will withhold Class 0 data during the active time deadband.

 

rlao_1-1682062470946.png

 

Base on my testing, it looks like the Geo SCADA help documentation is incorrect and that the x70 SCADAPack follows what is described in RemoteConnect, i.e. you need to untick this for Class 0 data to be withheld. This was done specifically on a 470.

 

Is it possible for this to be fixed so that in future others can avoid the same confusion that I went through today?

Labels
  • Labels:
  • DNP3
  • drivers
  • RTU
  • SCADA
  • Telemetry
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Janeway sbeadle Janeway
Janeway

Posted: ‎2023-04-25 03:45 AM

0 Likes
1
112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2023-04-25 03:45 AM

Thank you very much, and sorry you found this the hard way. Doc update will be coming.

See Answer In Context

Reply
Share
Replies 4
sbeadle
Janeway sbeadle Janeway
Janeway

Posted: ‎2023-04-25 03:45 AM

0 Likes
1
113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2023-04-25 03:45 AM

Thank you very much, and sorry you found this the hard way. Doc update will be coming.

Reply
Share
rlao
Lieutenant rlao
Lieutenant

Posted: ‎2023-04-25 07:43 PM

In response to sbeadle
0 Likes
0
106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2023-04-25 07:43 PM

Thanks, much appreciated 👍

Reply
Share
SMountain
SMountain
Cadet

Posted: 2 weeks ago

0 Likes
1
60
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: 2 weeks ago

Thank you for pointing this out. The Geo SCADA Expert documentation has now been updated. The update will be available in the help in Geo SCADA Expert 2023/V86. We intend backporting the documentation update so that it will be available in a future Monthly Update of other supported versions of Geo SCADA Expert.

Reply
Share
rlao
Lieutenant rlao
Lieutenant

Posted: 2 weeks ago

In response to SMountain
0 Likes
0
44
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: 2 weeks ago

Thanks for update on this one, much appreciated

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc