Incorrect Help documentation for Active Deadband Setup in x70 outstation configuration form

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Incorrect Help documentation for Active Deadband Setup in x70 outstation configuration form
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxureโ„ข Geo SCADA Expert
product field
Schneider Electric
RemoteConnect for the SCADAPack x70

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
rlao
Lt. Commander rlao
Lt. Commander

Posted: โ€Ž2023-04-21 12:41 AM . Last Modified: โ€Ž2023-05-02 11:44 PM

0 Likes
4
1565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2023-04-21 12:41 AM . Last Modified: โ€Ž2023-05-02 11:44 PM

Incorrect Help documentation for Active Deadband Setup in x70 outstation configuration form

In the x70 outstation configuration object in Geo SCADA 2020, there is an active deadband setup configuration item:

 

rlao_0-1682061972072.png

 

The tooltip did not make it clear whether I was meant to check or uncheck the box to withhold Class 0 poll responses during an active time deadband. When I was going through the Geo SCADA help, I noticed that this item has a different description in all Geo SCADA versions of the help files, e.g. 2020 help and 2022 help. It is called 'Filter Class 0 Data' and mentions that ticking the checkbox withholds Class 0 data during an active deadband timer.

 

rlao_2-1682062545931.png

 

When I go onto RemoteConnect, the setting description matches what I see in my version of Geo SCADA ('Always Include Time Deadband in Class 0'). Furthermore, it specifically says that unticking the checkbox will withhold Class 0 data during the active time deadband.

 

rlao_1-1682062470946.png

 

Base on my testing, it looks like the Geo SCADA help documentation is incorrect and that the x70 SCADAPack follows what is described in RemoteConnect, i.e. you need to untick this for Class 0 data to be withheld. This was done specifically on a 470.

 

Is it possible for this to be fixed so that in future others can avoid the same confusion that I went through today?

Labels
  • Labels:
  • DNP3
  • Drivers
  • RTU
  • SCADA
  • Telemetry
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: โ€Ž2023-04-25 03:45 AM

0 Likes
1
1532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2023-04-25 03:45 AM

Thank you very much, and sorry you found this the hard way. Doc update will be coming.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: โ€Ž2023-04-25 03:45 AM

0 Likes
1
1533
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2023-04-25 03:45 AM

Thank you very much, and sorry you found this the hard way. Doc update will be coming.

Reply

Link copied. Please paste this link to share this article on your social media post.

rlao
Lt. Commander rlao
Lt. Commander

Posted: โ€Ž2023-04-25 07:43 PM

In response to sbeadle
0 Likes
0
1526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2023-04-25 07:43 PM

Thanks, much appreciated ๐Ÿ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

SMountain
SMountain
Cadet

Posted: โ€Ž2023-05-12 03:45 AM

0 Likes
1
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2023-05-12 03:45 AM

Thank you for pointing this out. The Geo SCADA Expert documentation has now been updated. The update will be available in the help in Geo SCADA Expert 2023/V86. We intend backporting the documentation update so that it will be available in a future Monthly Update of other supported versions of Geo SCADA Expert.

Reply

Link copied. Please paste this link to share this article on your social media post.

rlao
Lt. Commander rlao
Lt. Commander

Posted: โ€Ž2023-05-15 12:16 AM

In response to SMountain
0 Likes
0
1464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2023-05-15 12:16 AM

Thanks for update on this one, much appreciated

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore