[Imported] obtaining update key for clearscada trial version

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] obtaining update key for clearscada trial version
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
319
AndrewScott
Admiral AndrewScott
114
BevanWeiss
Spock BevanWeiss
97
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
39
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-07 05:50 AM . Last Modified: ‎2023-05-03 12:22 AM

0 Likes
1
1497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-07 05:50 AM . Last Modified: ‎2023-05-03 12:22 AM

[Imported] obtaining update key for clearscada trial version

>>Message imported from previous forum - Category:ClearSCADA Software<<
User: ahmaddiab1, originally posted: 2019-10-21 16:24:16 Id:591
Dear all,
I want to configure an FTP service for sending data to clearscada as a test,
I configured a "New Direct Outstation" from the "SCADAPackE" of the "DNP3" and I applied the required configuration by assigning the default IP address 127.0.0.1, selecting FTP server service and enabling the service.

After creating the "New Direct Outstation", I got a message which says that an update key is required in order to activate the "New Direct Outstation". Is there a way to obtain an update key for the trial version of the clearscada?

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-07 05:58 AM

0 Likes
0
1495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-07 05:58 AM

Comments

adamwoodlandadamwoodland
October 21 Flag165.225.114.71
Hmm, not quite sure what update key would be in this case.

DNP3Secure has an update key, assuming you're not using that feature then you should be able to disable that on the Security tab and it should be ok to continue assuming its not enabled at the RTU too.

The only other thing I can think of is you're installed the DNP3-WITS driver which will stop any DNP3 from working. If you have installed that driver, you'll need to uninstall the DNP3-WITS driver and the generic DNP3 driver then should jump into life for the trial.

 

ahmaddiab1ahmaddiab1
October 31 Flag83.110.92.57
It is already disabled in the security tab and I still get a configuration error as per the attached screenshot. Could you please advise?

Thanks.
image.png
164.3K


adamwoodlandadamwoodland
October 31 Flag165.225.114.71
That error relates to the RTU address already assigned to another RTU on the set. Nothing to do with DNP3Secure.

If you double-click the error it takes you to (or should!) the field which is causing the problem.

 

ahmaddiab1ahmaddiab1
November 2 Flag94.97.125.117
What I am trying to test is to set an FTP service in the ClearSCADA and send data from an email to the email assigned to the ClearSCADA. Can this be tested from the trial version of ClearSCADA? If yes, could you guide me through the steps?

 

adamwoodlandadamwoodland
November 3 Flag165.225.114.71
Ok, that DNP3 FTP configuration is the functionality to configure at the RTU, nothing to do with ClearSCADA other than using it to define the configuration.

ClearSCADA doesn't have an FTP server, you'll need to use Windows IIS or some third party provider of FTP.

If you need to send emails look at alarm redirections, or Crystal Reports used to be able to send emails (I haven't checked recently to ensure it still can).

Could you clarify the link between FTP and sending emails? They're different protocols using different services so I'm a little confused as to what exactly you're trying to do.

 

ahmaddiab1ahmaddiab1
November 4 Flag94.97.125.117
I'm referring to the below link to enable FTP in ClearSCADA:

https://www.citect.schneider-electric.com/scada/clearscada/help/2015r2/Content/DNP3SCADAPackDriverGu...

Now you are saying there is no way to enable this on ClearSCADA alone and it needs to be configured on a third-party device and the configuration on clearSCADA needs to match the configuration on a third-party device, am I right?

 

adamwoodlandadamwoodland
November 4 edited November 5 Flag165.225.114.71
That is what I'm clarifying. That configuration you point to is to define the configuration of the SCADPack RTU centrally and allow that configuration to be downloaded to the RTU. Once downloaded the SCADAPack RTU will be an FTP server allowing FTP clients to connect.

That configuration you reference has no impact to the services provided by the ClearSCADA server to its connecting clients, which appears to be what you're trying to do based on your comments, such as:

"I want to configure an FTP service for sending data to clearscada as a test"

"What I am trying to test is to set an FTP service in the ClearSCADA and send data from an email to the email assigned to the ClearSCADA"

If you are trying to send emails to a SCADAPack then it has no email client so that won't work. You can send files to the SCADAPack RTU via FTP but then you have to do something with them within the scope of functionality on the SCADAPack RTU, which is limited.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-07 05:58 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-07 05:58 AM

Comments

adamwoodlandadamwoodland
October 21 Flag165.225.114.71
Hmm, not quite sure what update key would be in this case.

DNP3Secure has an update key, assuming you're not using that feature then you should be able to disable that on the Security tab and it should be ok to continue assuming its not enabled at the RTU too.

The only other thing I can think of is you're installed the DNP3-WITS driver which will stop any DNP3 from working. If you have installed that driver, you'll need to uninstall the DNP3-WITS driver and the generic DNP3 driver then should jump into life for the trial.

 

ahmaddiab1ahmaddiab1
October 31 Flag83.110.92.57
It is already disabled in the security tab and I still get a configuration error as per the attached screenshot. Could you please advise?

Thanks.
image.png
164.3K


adamwoodlandadamwoodland
October 31 Flag165.225.114.71
That error relates to the RTU address already assigned to another RTU on the set. Nothing to do with DNP3Secure.

If you double-click the error it takes you to (or should!) the field which is causing the problem.

 

ahmaddiab1ahmaddiab1
November 2 Flag94.97.125.117
What I am trying to test is to set an FTP service in the ClearSCADA and send data from an email to the email assigned to the ClearSCADA. Can this be tested from the trial version of ClearSCADA? If yes, could you guide me through the steps?

 

adamwoodlandadamwoodland
November 3 Flag165.225.114.71
Ok, that DNP3 FTP configuration is the functionality to configure at the RTU, nothing to do with ClearSCADA other than using it to define the configuration.

ClearSCADA doesn't have an FTP server, you'll need to use Windows IIS or some third party provider of FTP.

If you need to send emails look at alarm redirections, or Crystal Reports used to be able to send emails (I haven't checked recently to ensure it still can).

Could you clarify the link between FTP and sending emails? They're different protocols using different services so I'm a little confused as to what exactly you're trying to do.

 

ahmaddiab1ahmaddiab1
November 4 Flag94.97.125.117
I'm referring to the below link to enable FTP in ClearSCADA:

https://www.citect.schneider-electric.com/scada/clearscada/help/2015r2/Content/DNP3SCADAPackDriverGu...

Now you are saying there is no way to enable this on ClearSCADA alone and it needs to be configured on a third-party device and the configuration on clearSCADA needs to match the configuration on a third-party device, am I right?

 

adamwoodlandadamwoodland
November 4 edited November 5 Flag165.225.114.71
That is what I'm clarifying. That configuration you point to is to define the configuration of the SCADPack RTU centrally and allow that configuration to be downloaded to the RTU. Once downloaded the SCADAPack RTU will be an FTP server allowing FTP clients to connect.

That configuration you reference has no impact to the services provided by the ClearSCADA server to its connecting clients, which appears to be what you're trying to do based on your comments, such as:

"I want to configure an FTP service for sending data to clearscada as a test"

"What I am trying to test is to set an FTP service in the ClearSCADA and send data from an email to the email assigned to the ClearSCADA"

If you are trying to send emails to a SCADAPack then it has no email client so that won't work. You can send files to the SCADAPack RTU via FTP but then you have to do something with them within the scope of functionality on the SCADAPack RTU, which is limited.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore