[Imported] [Solved] Modbus Shared Outstation comms issues

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] [Solved] Modbus Shared Outstation comms issues
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
323
AndrewScott
Admiral AndrewScott
118
BevanWeiss
Spock BevanWeiss
100
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-05 02:01 PM . Last Modified: ‎2023-05-03 12:33 AM

0 Likes
0
1619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-05 02:01 PM . Last Modified: ‎2023-05-03 12:33 AM

[Imported] [Solved] Modbus Shared Outstation comms issues

>>Message imported from previous forum - Category:ClearSCADA Software<<
User: florian, originally posted: 2018-10-25 19:26:09 Id:279
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.

-------------------------------

**_hardin4019:_**
**_I am wondering if anyone has any experience with Modbus Shared Outstations?_**

**_I have a situation where Channel A is setup to communicate via Satellite and is the primary, Channel B is setup to communicate via Pepwave BRCellular modem and is the secondary which also acts as the Router with the Satellite going into the WAN port on the Pepwave. Heartbeat is turned on, use preferred Channel (A) is turned on with a delay of 60 seconds, and the Inbound Connections is set to "Accept Inbound Connections on Both Lines". Right now I am using CS 2017 R2, and I am connecting to a Red Lion DSPLE000 that supports multiple connections, and I am polling from the DSP as Modbus TCP. I am using the Heartbeat function to check register 40200, which is a floating point containing a pressure. The Red Lion DSP is polling Modbus TCP from a ROC 800._**

**_For testing purposes, I have 2 cellular modems, a Red Lion DSPLE000, a SCADAPack 330, and a Linksys LRT224 dual WAN router, all setup on my desk and I am seeing the same thing. Both cellular modems are on, connected, and have good communications._**

**_I am seeing lots of communications failures on whichever channel is inactive, even preventing the communications line to switch back to the preffered channel after it has come back up. Looking at the event log, I can see that once both channels are connected, the next Heartbeat is happening roughly 30 seconds later, the inactive channel fails, next Heartbeat it reconnects. Other times, the Heartbeat fails 30 seconds after the channel connects, then within 2 seconds of failing, it reconnects without waiting until the next heartbeat._**

**_Is there a specfic delay I shoud adjust to compensate for a delay in response to the Heartbeat?_**

---------------------

**_hardin4019:_**
**_Something I hadn't tried is using the test setup on my desk, is removing the Red Lion DSP out of the picture and just trying to poll data from the SCADAPack 330. This works perfectly fine and I'm not getting the comms failure on the inactive channel. I will continue to investigate further, but it looks like the Red Lion may not be responding fast enough, be keeping connections open, or allowing enough connections._**


----------------

AFarooq:
You might be confusing the shared with the switched setup. Shared allows for both channels to be used like a load balance concept. Switched uses only one with the choice of a prefered option. Maybe you intended to have a swtiched set up and not a shared setup?

--------------

**_hardin4019:_**
**_I figured it out and have been letting it run for a while. It is "Shared Outstation" and "Shared Outstation Set" for sure. My problem ended up being a connection timeout in the Red Lion DSP. It was set to 10 seconds, an the Heartbeat was only happening every 30 seconds. I increased the timeout to 60 seconds, and all of the issues went away._**

--------------

bevanweiss:
Yeah, I was going to say Wireshark logs or it didn't happen 😛

I think the Wireshark logs would have shown the RedLion issuing a TCP RST (drop connection) which would have caused the ClearSCADA to complain.. it wants to be the one doing the dropping.

You might want to do some testing to see how many concurrent connections the RedLion supports however, we have seen in the past some issues where the slave device only handled two connections. On a redundancy swap there may be up to 4 connections still 'present'.. two from the old server, and two from the new server.

If the new server connections are refused then you will get annoying alarms until the old connections timeout.

----------------

**_hardin4019:_**
**_So far, we have the Red Lion for 2 sessions and it hasn't been an issue. The sites we are polling aren't super critical and a few second or a minute outage isn't going to hurt anything._**

**_Since the original post, I seen an actual outage occur with the test setup on my desk. One AT&T cellular modem, and one Verizon Wireless cellular modem. Something happened in the network and we lost Verizon. The test setup showed the loss of the VZW modem and one or two failed attempts to get it back, but overall, I still had a healthy connection that was updating with "Healthy, B Failed" and when the network issues were resolved, the VZW modem on channel B came back and everything was good and the status changed back to "Healthy, Multidrop"._**

**_The two major issues I was having were having the Red Lion have a single ethernet connection using a single gateway addres, but having two physical gateway modems with two different IP addresses. I tried adding an expansion Ethernet card and IP address to the Red Lion, only one modem would sucessfuly respond to ClearSCADA at a time, and it was only the modem whos IP address was programed as the gateway address of the Red Lion. The Red Lion support was contacted and the Red Lion doesn't support multiple gateway addresses, in fact it stops responding all together if you put in a second gateway address._**

**_Once it was decided I needed a Router with Dual/Multi WAN port capability, the gateway of the Red Lion was switched to the IP of the Router, both modems were responding to ClearSCADA with data from the Red Lion, but the secondary channel was only pulling a heartbeat at the restablis interval and would not stay connected. I now know that the restablish interval was longer than the connection timeout of the Red Lion. The Red Lion was dropping the connection to the second modem because of this, then it would restablish the connection on the next poll._**

**_I guess now I am kind of curious, with all that I have learned, if I can remove the Router and get the second Ethernet port on the Red Lion to work._**

 

 

 

 

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore