[Imported] Scanner Command (Primary Poll) Timeout

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] Scanner Command (Primary Poll) Timeout
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
323
AndrewScott
Admiral AndrewScott
118
BevanWeiss
Spock BevanWeiss
100
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-07 03:38 AM . Last Modified: ‎2023-05-03 12:23 AM

0 Likes
1
1386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-07 03:38 AM . Last Modified: ‎2023-05-03 12:23 AM

[Imported] Scanner Command (Primary Poll) Timeout

>>Message imported from previous forum - Category:ClearSCADA Software<<
User: dialvec, originally posted: 2019-06-25 20:57:28 Id:459
Hello.

I am deploying a M2M network to communicate some remote RTUs. I currently have 3 RTUs connected to a central server.

I am using GPRS modems and I am time-randomly getting the following alarm message:

"Scanner Command (Primary Poll) Timeout"

The network has been configured to communicate every 5 minutes and modems transmit to each other via serial .

Also, network's connection is intermittent, so I get communications state Fail messages.

What kind of parameters should I check in order to detect the system's fault?

Thank you so much

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-07 03:38 AM

0 Likes
0
1383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-07 03:38 AM

>>Responses imported from previous forum


Reply From User: JesseChamberlain, posted: 2019-06-26 03:40:11
Sounds like you're doing the primary poll for all three at the same time, likely the time it takes to complete two of them is more than the timeout (30s) sometimes. Try offsetting the polls.

You should also review your polling regime, doing a primary poll every 5mins is very inefficient and doesn't take advantage of DNP3's features - your current setup is probably less efficient than modbus!


Reply From User: dialvec, posted: 2019-06-26 12:36:51
Hi Jesse.

Thank you so much for your answer.

Could you please explain more about what settings could I use in order to take advantage of DNP3?

Once again, thank you


Reply From User: JesseChamberlain, posted: 2019-06-27 05:36:42
It's a bit of a big topic for detail on the forum, we run multiple day training sessions on DNP3! It will also depend on the feature set of the RTUs.

You will want to analyse the data you're gathering, how much it changes and how often you need to know. On the RTU, set event deviations based on how much of a change you want to know about. Classify your points into classes so you can poll or get unsoliciteds at different rates.

You might have Class 1 points set to send an unsolicited as soon as they deviate by 0.1 and a class poll of 5mins, but Class 2 points set to create events when they deviate by 10 and to only gather the event data hourly. It's a combination of the config on the device and the CS outstation config.


Reply From User: dialvec, posted: 2019-06-27 12:40:10
Ok. I get the idea.

Thanks again, you have been very helpful

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-07 03:38 AM

0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-07 03:38 AM

>>Responses imported from previous forum


Reply From User: JesseChamberlain, posted: 2019-06-26 03:40:11
Sounds like you're doing the primary poll for all three at the same time, likely the time it takes to complete two of them is more than the timeout (30s) sometimes. Try offsetting the polls.

You should also review your polling regime, doing a primary poll every 5mins is very inefficient and doesn't take advantage of DNP3's features - your current setup is probably less efficient than modbus!


Reply From User: dialvec, posted: 2019-06-26 12:36:51
Hi Jesse.

Thank you so much for your answer.

Could you please explain more about what settings could I use in order to take advantage of DNP3?

Once again, thank you


Reply From User: JesseChamberlain, posted: 2019-06-27 05:36:42
It's a bit of a big topic for detail on the forum, we run multiple day training sessions on DNP3! It will also depend on the feature set of the RTUs.

You will want to analyse the data you're gathering, how much it changes and how often you need to know. On the RTU, set event deviations based on how much of a change you want to know about. Classify your points into classes so you can poll or get unsoliciteds at different rates.

You might have Class 1 points set to send an unsolicited as soon as they deviate by 0.1 and a class poll of 5mins, but Class 2 points set to create events when they deviate by 10 and to only gather the event data hourly. It's a combination of the config on the device and the CS outstation config.


Reply From User: dialvec, posted: 2019-06-27 12:40:10
Ok. I get the idea.

Thanks again, you have been very helpful

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore