Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

[Imported] Query List of Template Values

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] Query List of Template Values
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
sbeadle Champion
337
AndrewScott
AndrewScott
128
BevanWeiss
BevanWeiss
104
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
sbeadle
sbeadle Champion
Champion

Posted: ‎2019-11-26 09:10 AM . Last Modified: ‎2023-05-03 12:22 AM

0 Likes
1
2316
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-26 09:10 AM . Last Modified: ‎2023-05-03 12:22 AM

[Imported] Query List of Template Values

>>Message imported from previous forum - Category:ClearSCADA Software<<
User: Tanquen, originally posted: 2019-07-17 00:43:50 Id:473
Like if you had a pump template with pump speed and wanted to list all the pumps speeds.

I have a list object on a screen and can query some values but not all.

This gives me a list of some of the tags in the group, Variables tags but not Internal tags in a template instance in the same group.

SELECT
"FullName" AS "~FullName", "Id", "Foreground", "Blink", "Background", "ValueFormatted", "LastUpdated", "TypeDesc", "MemoryUsage"
FROM
CVARIABLE
WHERE
"FullName" LIKE '%C-01%'
ORDER BY
"~FullName" ASC

The original template:
~Config.~ RTU Site.Direct eNET Outstation


If I use From CDBPOINT it will list the Internal tags I want **but no values**.

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
sbeadle Champion
Champion

Posted: ‎2019-11-26 09:11 AM

0 Likes
0
2314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-26 09:11 AM

>>Responses imported from previous forum


Reply From User: BevanWeiss, posted: 2019-07-17 00:49:02
This is a limitation of the ClearSCADA Schema. If you're putting together queries like this, then you should get familiar with it 🙂

What you'll need is a UNION for what you want.

SELECT FullName, Id, Foreground, Blink, Background, ValueFormatted, LastUpdated, TypeDesc
FROM CVariable
UNION CDBPoint
Where FullName LIKE '%C-01%%
ORDER By FullName ASC

If you're looking in a template, then it will have no values. It's a template (an 'abstract' thing, not a representation of anything in the real world).


Reply From User: Tanquen, posted: 2019-07-17 00:59:44
This gives me the two types of tags but only if I remove the ValueFormatted and LastUpdated columns. Both tag types are part of the same template but I can only see the values of the Variables (yellow) and not the Internal (Dark Blue)?

Don't need to even see the Variable type I just noticed an example that would let me see the Variable type tags and their values.
____________________________________________
Looks like CurrentValueFormatted works. 🙂


Reply From User: BevanWeiss, posted: 2019-07-17 03:16:32
I didn't have the schema infront of me, I was hoping that ValueFormatted would exist for CDBPoint also (and would have mapped to CurrentValueFormatted internally).

If you want them both then you may have to do sub-queries.
SELECT Id, FullName, ValueFormatted
FROM
CVariable
UNION
SELECT Id, FullName, CurrentValueFormatted As "ValueFormatted"
FROM CDBPoint

^^ untested, there may be ClearSCADA QP limitation which makes this not so workable (I can't remember if I've tried using the SELECT beneath a UNION... I would have thought so, but memory and old age 👅 ).

 

Reply From User: sbeadle, posted: 2019-07-17 08:04:29
Check the SQL guide. You'll see that UNION can be done in two ways. One as a list of tables, the other as a list of queries - each separated by UNION.


Reply From User: Tanquen, posted: 2019-07-17 15:37:00
I'll keep the UNION option in mind if I need to list the different types together.

Any idea why the different tables (CVARIABLE or CDBPOINT) show in different colors in the list object? Can I just make them all black text?

 

Reply From User: BevanWeiss, posted: 2019-07-19 09:10:16
The different colours are because in your query your telling it to use different colours (with Foreground, Background, Blink). Leave them out and they will be black on white (default). You can set these to any RGB number you want (R*256*256+G*256+B) [R,G,B between 0 and 255]


Reply From User: Tanquen, posted: 2019-07-19 15:18:19
Thanks. I had taken those out but it just went from pink to red. I'll see if I can find how to add the RGB number in.

Ok, removed the "Foreground, Background, Blink" and then set the TextColour to black in the list objects animation. Not sure why "Foreground, Background," make different stuff different colors or why removing them still gets you red but oh well.


Reply From User: BevanWeiss, posted: 2019-08-06 02:51:41
Foreground and Background make stuff different colours because it's the special way ViewX handles query results with these column labels.
This is detailed within the help.
It makes sense if you want to easily animate the list colours (which I normally do) for objects. It's very handy to show if an outstation in a list is disconnected, or has a certain alarm against it etc etc. With the 'native' colour from the CS database configuration (i.e. Colour Palette, and Alarm Severities).


Reply From User: Tanquen, posted: 2019-08-08 23:40:18
Ok, it's a bit more complicated. It was very hard to find everything but'

The sites have a screen that they all use and it's linked to a set of real or indirect tags. So when you select a certain site a script in that sites object runs and gets the values from the correct PLC and puts them into retentive script variables that are then temporally linked to the real tags that are linked on the screen.

Variables like these:
VAR RETAIN
AO_ConfigID1: REAL;

End up in something like this:
CFG_AI_01_Eng_Max

I spoke with the guy that setup this craziness and he doesn't think you can query the script variables. He said they did this because of some kind of limitation on the total number of tags. I'm guessing you would need to add a real tag into each of the site objects if you wanted to be able to query all the sites and see the value?

I was able to find all the objects with these tags using this query but have no idea how to get at the retentive script variables in each.

SELECT
"FullName" AS "~FullName", "Id", "Foreground", "Blink", "Background", "ValueFormatted", "LastUpdated", "TypeDesc", "MemoryUsage"
FROM
CVARIABLE
WHERE
( "~FullName" LIKE '%.CFG\\_VENTURI%' ) AND ( "ValueFormatted" = 'True' )
ORDER BY
"~FullName" ASC


Reply From User: Tanquen, posted: 2019-08-12 01:42:17
"Your terminology of 'retentive script variables' is incorrect. You are refering to a RETAINed variable within a Logic Program. Logic != Script."

I could not disagree less. Why do you do stuff like this?


Reply From User: BevanWeiss, posted: 2019-08-12 04:22:27
[at]Tanquen said:
I could not disagree less....

What do you disagree with?
You understand the difference between 'script' and 'logic' within the ClearSCADA system right?
![]((see attachments below) pn/e8zo9xejd3u0.png "")
![]((see attachments below) km/acvnkw1i7tsh.png "")

They behave very differently, and there are a number of critical differences to them.
The distinction between them is very important.

Attached file: (editor/pn/e8zo9xejd3u0.png), Logic.png File size: 9177

Attached file: (editor/km/acvnkw1i7tsh.png), Script.png File size: 9297


Reply From User: du5tin, posted: 2019-09-27 14:15:23
Ick... sounds like they tried to save a few dollars on the point license or support and spent way more on configuration.

Definitely look into setting things up with proper points and not variables.

The DataSets/DataRows do work wonders! You can combine data from different sources and put it in a custom table that is easy to query and work with. This includes values from variables, parameters, points, configuration and more! If there is any list style navigation we use DataSets/DataRows.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
sbeadle
sbeadle Champion
Champion

Posted: ‎2019-11-26 09:11 AM

0 Likes
0
2315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-26 09:11 AM

>>Responses imported from previous forum


Reply From User: BevanWeiss, posted: 2019-07-17 00:49:02
This is a limitation of the ClearSCADA Schema. If you're putting together queries like this, then you should get familiar with it 🙂

What you'll need is a UNION for what you want.

SELECT FullName, Id, Foreground, Blink, Background, ValueFormatted, LastUpdated, TypeDesc
FROM CVariable
UNION CDBPoint
Where FullName LIKE '%C-01%%
ORDER By FullName ASC

If you're looking in a template, then it will have no values. It's a template (an 'abstract' thing, not a representation of anything in the real world).


Reply From User: Tanquen, posted: 2019-07-17 00:59:44
This gives me the two types of tags but only if I remove the ValueFormatted and LastUpdated columns. Both tag types are part of the same template but I can only see the values of the Variables (yellow) and not the Internal (Dark Blue)?

Don't need to even see the Variable type I just noticed an example that would let me see the Variable type tags and their values.
____________________________________________
Looks like CurrentValueFormatted works. 🙂


Reply From User: BevanWeiss, posted: 2019-07-17 03:16:32
I didn't have the schema infront of me, I was hoping that ValueFormatted would exist for CDBPoint also (and would have mapped to CurrentValueFormatted internally).

If you want them both then you may have to do sub-queries.
SELECT Id, FullName, ValueFormatted
FROM
CVariable
UNION
SELECT Id, FullName, CurrentValueFormatted As "ValueFormatted"
FROM CDBPoint

^^ untested, there may be ClearSCADA QP limitation which makes this not so workable (I can't remember if I've tried using the SELECT beneath a UNION... I would have thought so, but memory and old age 👅 ).

 

Reply From User: sbeadle, posted: 2019-07-17 08:04:29
Check the SQL guide. You'll see that UNION can be done in two ways. One as a list of tables, the other as a list of queries - each separated by UNION.


Reply From User: Tanquen, posted: 2019-07-17 15:37:00
I'll keep the UNION option in mind if I need to list the different types together.

Any idea why the different tables (CVARIABLE or CDBPOINT) show in different colors in the list object? Can I just make them all black text?

 

Reply From User: BevanWeiss, posted: 2019-07-19 09:10:16
The different colours are because in your query your telling it to use different colours (with Foreground, Background, Blink). Leave them out and they will be black on white (default). You can set these to any RGB number you want (R*256*256+G*256+B) [R,G,B between 0 and 255]


Reply From User: Tanquen, posted: 2019-07-19 15:18:19
Thanks. I had taken those out but it just went from pink to red. I'll see if I can find how to add the RGB number in.

Ok, removed the "Foreground, Background, Blink" and then set the TextColour to black in the list objects animation. Not sure why "Foreground, Background," make different stuff different colors or why removing them still gets you red but oh well.


Reply From User: BevanWeiss, posted: 2019-08-06 02:51:41
Foreground and Background make stuff different colours because it's the special way ViewX handles query results with these column labels.
This is detailed within the help.
It makes sense if you want to easily animate the list colours (which I normally do) for objects. It's very handy to show if an outstation in a list is disconnected, or has a certain alarm against it etc etc. With the 'native' colour from the CS database configuration (i.e. Colour Palette, and Alarm Severities).


Reply From User: Tanquen, posted: 2019-08-08 23:40:18
Ok, it's a bit more complicated. It was very hard to find everything but'

The sites have a screen that they all use and it's linked to a set of real or indirect tags. So when you select a certain site a script in that sites object runs and gets the values from the correct PLC and puts them into retentive script variables that are then temporally linked to the real tags that are linked on the screen.

Variables like these:
VAR RETAIN
AO_ConfigID1: REAL;

End up in something like this:
CFG_AI_01_Eng_Max

I spoke with the guy that setup this craziness and he doesn't think you can query the script variables. He said they did this because of some kind of limitation on the total number of tags. I'm guessing you would need to add a real tag into each of the site objects if you wanted to be able to query all the sites and see the value?

I was able to find all the objects with these tags using this query but have no idea how to get at the retentive script variables in each.

SELECT
"FullName" AS "~FullName", "Id", "Foreground", "Blink", "Background", "ValueFormatted", "LastUpdated", "TypeDesc", "MemoryUsage"
FROM
CVARIABLE
WHERE
( "~FullName" LIKE '%.CFG\\_VENTURI%' ) AND ( "ValueFormatted" = 'True' )
ORDER BY
"~FullName" ASC


Reply From User: Tanquen, posted: 2019-08-12 01:42:17
"Your terminology of 'retentive script variables' is incorrect. You are refering to a RETAINed variable within a Logic Program. Logic != Script."

I could not disagree less. Why do you do stuff like this?


Reply From User: BevanWeiss, posted: 2019-08-12 04:22:27
[at]Tanquen said:
I could not disagree less....

What do you disagree with?
You understand the difference between 'script' and 'logic' within the ClearSCADA system right?
![]((see attachments below) pn/e8zo9xejd3u0.png "")
![]((see attachments below) km/acvnkw1i7tsh.png "")

They behave very differently, and there are a number of critical differences to them.
The distinction between them is very important.

Attached file: (editor/pn/e8zo9xejd3u0.png), Logic.png File size: 9177

Attached file: (editor/km/acvnkw1i7tsh.png), Script.png File size: 9297


Reply From User: du5tin, posted: 2019-09-27 14:15:23
Ick... sounds like they tried to save a few dollars on the point license or support and spent way more on configuration.

Definitely look into setting things up with proper points and not variables.

The DataSets/DataRows do work wonders! You can combine data from different sources and put it in a custom table that is easy to query and work with. This includes values from variables, parameters, points, configuration and more! If there is any list style navigation we use DataSets/DataRows.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore