>>Message imported from previous forum - Category:Scripts and Tips<<
User: lecadi, originally posted: 2019-01-11 20:46:48 Id:347
Dear all
We need to import the information of some variables from a database MySQL to points in ClearSCADA.
You could see in the image the dispnibility of information
For one point I could read the the value of variable, but we have an historical information for every single variable, so we need to import all historical to the historian to monitor in CLearSCADA the information.
 ol/vd7tsw3k9c2h.png "")
So we would like you help us with this issue
Attached file: (editor/ol/vd7tsw3k9c2h.png), imagen.png File size: 6212
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-11-06 06:30 AM
>>Responses imported from previous forum
Reply From User: BevanWeiss, posted: 2019-01-13 21:12:27
Have you looked at ODBC Points?
Look in the ClearSCADA help...
Reply From User: lecadi, posted: 2019-01-17 12:43:10
Thanks, it worked for me, but I have another question, the timestamp value in ClearSCADA its diferent from the original database, (there is a diferent of 5 hours). It looks like ClearSCADA assume the timestamp from original database were in another time zone. But in my case both server are in the same time zone
Reply From User: sbeadle, posted: 2019-01-17 12:57:56
ClearSCADA works in UTC/GMT, so timestamps need to be converted before the driver sees them (e.g. alter the query to add a function/expression to convert). Client settings control what you see, so you may not realise that underneath it's all UTC.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-11-06 06:30 AM
>>Responses imported from previous forum
Reply From User: BevanWeiss, posted: 2019-01-13 21:12:27
Have you looked at ODBC Points?
Look in the ClearSCADA help...
Reply From User: lecadi, posted: 2019-01-17 12:43:10
Thanks, it worked for me, but I have another question, the timestamp value in ClearSCADA its diferent from the original database, (there is a diferent of 5 hours). It looks like ClearSCADA assume the timestamp from original database were in another time zone. But in my case both server are in the same time zone
Reply From User: sbeadle, posted: 2019-01-17 12:57:56
ClearSCADA works in UTC/GMT, so timestamps need to be converted before the driver sees them (e.g. alter the query to add a function/expression to convert). Client settings control what you see, so you may not realise that underneath it's all UTC.