[Imported] Nouvel utilisateur CS

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] Nouvel utilisateur CS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
319
AndrewScott
Admiral AndrewScott
114
BevanWeiss
Spock BevanWeiss
97
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
39
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 12:35 PM . Last Modified: ‎2023-05-03 12:27 AM

0 Likes
1
928
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 12:35 PM . Last Modified: ‎2023-05-03 12:27 AM

[Imported] Nouvel utilisateur CS

>>Message imported from previous forum - Category:ClearSCADA Software<<
User: ape, originally posted: 2019-03-01 10:28:10 Id:374
Hello everyone I have recently been a new user of clearscada software that I particularly like, and I support demos for existing clients and I need specific features such as mapping with real value display , also the use of table via dream report.
I would also like to know if it is possible in a simple way to import variables en masse?
I do not speak very well but then forgive my mistakes in advance thank you very much and congratulations for this forum mutual aid

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 12:36 PM

0 Likes
0
927
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 12:36 PM

>>Responses imported from previous forum


Reply From User: sbeadle, posted: 2019-03-01 13:56:25
Hi, you're welcome!

Bulk configuration/import - see "Spreadsheet-based Configuration Import Tool" at http://resourcecenter.controlmicrosystems.com/pages/viewpage.action?pageId=40535951

Mapping - read the release notes for ClearSCADA 2017 at: https://schneider-electric.box.com/shared/static/bct2w7pxt6koqfl0tcoxp0fzwzgn55j3.pdf

Best regards.


Reply From User: ape, posted: 2019-03-01 14:21:50
Thank you for this informations.
For cartographie, i can't to display a real value in tooltip? it's possible?
have you ever used dream report for CS 2017R3?


Reply From User: sbeadle, posted: 2019-03-01 14:57:34
Yes, you can use the SQL in the User Query to display values (in colours) in the tooltips. The 2017 version release notes describe how.
Dream Reports can access the ClearSCADA historian - details are in their documentation.

 

Reply From User: ape, posted: 2019-03-02 06:35:19
Do you know why this query doesn 't work? i would like display synthes of active alarme count/acquit alarm count/alarm clean count on one display on tooltip

SELECT FULLNAME, FULLNAME || '
Alarmes : ' || AlarmSetCount(Value)
as "TOOLTIP", GISLOCATION-LATITUDE, GISLOCATION-LONGITUDE,CASE WHEN AlarmSetCount 0 THEN 255 WHEN AlarmAcceptedCount 0 THEN 255
WHEN AlarmClearedCount 0 THEN 150*256 ELSE 0 END AS"Foreground", Background,CASE WHEN AlarmSetCount 0 THEN 1 ELSE 0
END AS "Blink",AlarmSetCount, AlarmAcceptedCount, AlarmClearedCount
FROM CGROUP
WHERE
FULLNAME LIKE '%EU%' AND GISLOCATIONSOURCE = 1
ORDER BY AlarmSetCount, AlarmAcceptedCount, AlarmClearedCount


Reply From User: BevanWeiss, posted: 2019-03-03 21:30:37
What is AlarmSetCount(Value) supposed to be?
Do you instead just mean AlarmSetCount? (i.e. the property on the CGroup object type)

You should include the error message in these situations. In fact, I suspect that the error message would have told you exactly what the problem was.


Reply From User: ape, posted: 2019-03-04 05:44:28
indeed, the error message informs me that the request can not concatenate values of type string or integer. I have the following query on which I can not insert numerical values

SELECT FULLNAME, FULLNAME || '
Active:' || 'Acquitted:' || 'Disappeared:' as "TOOLTIP",
GISLOCATION- LATITUDE, GISLOCATION- LONGITUDE, WHEN CASE AlarmSetCount 0 THEN 255 WHEN AlarmAcceptedCount 0 THEN 255
WHEN AlarmClearedCount 0 THEN 150 * 256 ELSE 0 END AS "Foreground", Background, CASE WHEN AlarmSetCount 0 THEN 1 ELSE 0
END AS "Blink", AlarmSetCount, AlarmAcceptedCount, AlarmClearedCount
FROM CGROUP
WHERE
FULLNAME LIKE '% EU%' AND GISLOCATIONSOURCE = 1
ORDER BY AlarmSetCount, AlarmAcceptedCount, AlarmClearedCount


Reply From User: sbeadle, posted: 2019-03-04 08:50:26
look at FORMATVALUE in the SQL help


Reply From User: ape, posted: 2019-03-04 09:20:16
Thank you very much it's ok !!!!


Reply From User: ape, posted: 2019-03-04 09:28:14
But i dont't understand this example query in the note.
i would like display on map synthese "Niveaux" of a group "EP" with 2 sites but it doesn't work. i dont find my error...

SELECT g.Id as "Id", g.FullName as "FullName",g.FullName || '
|| FormatValue (r.Niveaux '0.00') as"Tooltip",
g.GISLOCATION-LATITUDE as "GISLOCATION-LATITUDE", g.GISLOCATION-
LONGITUDE as "GISLOCATION-LONGITUDE",
case
when Niveaux 50 then (255 + cast( (100-Niveaux)/100*2*255 as INT)*256)
end as "Foreground",255+256*255+256*256*255 as "Background", 0 as "Blink"
FROM CGROUP AS g left join CRandom as r on r.ParentGroupId = g.Id
WHERE g.FULLNAME LIKE 'EP.%'

 

Reply From User: sbeadle, posted: 2019-03-04 09:30:19
I think formatting messed that post up. Try the code format.


Reply From User: ape, posted: 2019-03-04 09:31:35
voir le code plus bas ......


Reply From User: ape, posted: 2019-03-04 11:04:01
i try to simplify the query but display doesn't work (identifier unknow).
This group for measure is local/EP/Site/variables/mesures/niveau

SELECT FULLNAME, FULLNAME ||'
' || FormatValue (Niveau.Currentvalue using '0.00') as "TOOLTIP",
GISLOCATION-LATITUDE, GISLOCATION-LONGITUDE,
FROM CGROUP
WHERE
FULLNAME LIKE '%EU%' AND GISLOCATIONSOURCE = 1


Reply From User: ape, posted: 2019-03-04 09:32:15
view code lower......


Reply From User: sbeadle, posted: 2019-03-04 10:17:16

Try testing your query in querypad (search in the help).
'
' || FormatValue (r.Niveau USING '0.00')
Quotes around

Add USING
What is r.Niveau - no field with this name exists
The JOIN links a point within the group


Reply From User: ape, posted: 2019-03-04 09:41:42
Sorry, i don't have seen that we can get a preview for the message..


Reply From User: ape, posted: 2019-03-04 10:03:50
SELECT g.Id as "Id", g.FullName as "FullName",g.FullName ||
|| FormatValue (r.Niveau '0.00') as"Tooltip",
g.GISLOCATION-LATITUDE as "GISLOCATION-LATITUDE", g.GISLOCATION-
LONGITUDE as "GISLOCATION-LONGITUDE",case
when r.Niveau 50 then (255 + cast( (100-r.Niveau)/100*2*255 as INT)*256)
end as "Foreground",255+256*255+256*256*255 as "Background", 0 as "Blink"
FROM CGROUP AS g left join CRandom as r on r.ParentGroupId = g.Id
WHERE g.FULLNAME LIKE 'EU.%'


Reply From User: sbeadle, posted: 2019-03-04 13:52:31
Your query is from the table CGroup (an object folder), but you are selecting a field (currentvalue) valid only on points, and with a table alias (Niveau) which does not exist. Is your point called Niveau and the top level group is EU?
Maybe try
`SELECT FULLNAME, FULLNAME ||'
' || FormatValue (p.Currentvalue using '0.00') as "TOOLTIP",
GISLOCATION-LATITUDE, GISLOCATION-LONGITUDE,
FROM CDBPoint p
WHERE
FULLNAME LIKE 'EU.%.Niveau' AND GISLOCATIONSOURCE = 1`


Reply From User: ape, posted: 2019-03-04 14:06:19
Ok i understand a little more...
What is "p." front of field currentvalue?
What is " p after CDBPoint?
I try this query but she doesn't work (unexpected identifier)

thank you for your patience ; i'm beginner and great opportunity comes with this software


Reply From User: ape, posted: 2019-03-05 16:02:19
It's OK!!!! so i can't to display 2 values on one tootlip..it's possible for


Reply From User: ape, posted: 2019-03-05 16:07:03
`SELECT FULLNAME, FULLNAME||'
' || Formatvalue (CurrentValueFormatted using '0.00') AS "TOOLTIP",
GISLOCATION-LATITUDE, GISLOCATION-LONGITUDE
FROM CDBPoint
Where fullname LIKE '%.Niveau%'`


Reply From User: sbeadle, posted: 2019-03-06 13:13:52
p is a table alias: https://www.sqlteaching.com/#!table_alias

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 12:36 PM

0 Likes
0
928
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 12:36 PM

>>Responses imported from previous forum


Reply From User: sbeadle, posted: 2019-03-01 13:56:25
Hi, you're welcome!

Bulk configuration/import - see "Spreadsheet-based Configuration Import Tool" at http://resourcecenter.controlmicrosystems.com/pages/viewpage.action?pageId=40535951

Mapping - read the release notes for ClearSCADA 2017 at: https://schneider-electric.box.com/shared/static/bct2w7pxt6koqfl0tcoxp0fzwzgn55j3.pdf

Best regards.


Reply From User: ape, posted: 2019-03-01 14:21:50
Thank you for this informations.
For cartographie, i can't to display a real value in tooltip? it's possible?
have you ever used dream report for CS 2017R3?


Reply From User: sbeadle, posted: 2019-03-01 14:57:34
Yes, you can use the SQL in the User Query to display values (in colours) in the tooltips. The 2017 version release notes describe how.
Dream Reports can access the ClearSCADA historian - details are in their documentation.

 

Reply From User: ape, posted: 2019-03-02 06:35:19
Do you know why this query doesn 't work? i would like display synthes of active alarme count/acquit alarm count/alarm clean count on one display on tooltip

SELECT FULLNAME, FULLNAME || '
Alarmes : ' || AlarmSetCount(Value)
as "TOOLTIP", GISLOCATION-LATITUDE, GISLOCATION-LONGITUDE,CASE WHEN AlarmSetCount 0 THEN 255 WHEN AlarmAcceptedCount 0 THEN 255
WHEN AlarmClearedCount 0 THEN 150*256 ELSE 0 END AS"Foreground", Background,CASE WHEN AlarmSetCount 0 THEN 1 ELSE 0
END AS "Blink",AlarmSetCount, AlarmAcceptedCount, AlarmClearedCount
FROM CGROUP
WHERE
FULLNAME LIKE '%EU%' AND GISLOCATIONSOURCE = 1
ORDER BY AlarmSetCount, AlarmAcceptedCount, AlarmClearedCount


Reply From User: BevanWeiss, posted: 2019-03-03 21:30:37
What is AlarmSetCount(Value) supposed to be?
Do you instead just mean AlarmSetCount? (i.e. the property on the CGroup object type)

You should include the error message in these situations. In fact, I suspect that the error message would have told you exactly what the problem was.


Reply From User: ape, posted: 2019-03-04 05:44:28
indeed, the error message informs me that the request can not concatenate values of type string or integer. I have the following query on which I can not insert numerical values

SELECT FULLNAME, FULLNAME || '
Active:' || 'Acquitted:' || 'Disappeared:' as "TOOLTIP",
GISLOCATION- LATITUDE, GISLOCATION- LONGITUDE, WHEN CASE AlarmSetCount 0 THEN 255 WHEN AlarmAcceptedCount 0 THEN 255
WHEN AlarmClearedCount 0 THEN 150 * 256 ELSE 0 END AS "Foreground", Background, CASE WHEN AlarmSetCount 0 THEN 1 ELSE 0
END AS "Blink", AlarmSetCount, AlarmAcceptedCount, AlarmClearedCount
FROM CGROUP
WHERE
FULLNAME LIKE '% EU%' AND GISLOCATIONSOURCE = 1
ORDER BY AlarmSetCount, AlarmAcceptedCount, AlarmClearedCount


Reply From User: sbeadle, posted: 2019-03-04 08:50:26
look at FORMATVALUE in the SQL help


Reply From User: ape, posted: 2019-03-04 09:20:16
Thank you very much it's ok !!!!


Reply From User: ape, posted: 2019-03-04 09:28:14
But i dont't understand this example query in the note.
i would like display on map synthese "Niveaux" of a group "EP" with 2 sites but it doesn't work. i dont find my error...

SELECT g.Id as "Id", g.FullName as "FullName",g.FullName || '
|| FormatValue (r.Niveaux '0.00') as"Tooltip",
g.GISLOCATION-LATITUDE as "GISLOCATION-LATITUDE", g.GISLOCATION-
LONGITUDE as "GISLOCATION-LONGITUDE",
case
when Niveaux 50 then (255 + cast( (100-Niveaux)/100*2*255 as INT)*256)
end as "Foreground",255+256*255+256*256*255 as "Background", 0 as "Blink"
FROM CGROUP AS g left join CRandom as r on r.ParentGroupId = g.Id
WHERE g.FULLNAME LIKE 'EP.%'

 

Reply From User: sbeadle, posted: 2019-03-04 09:30:19
I think formatting messed that post up. Try the code format.


Reply From User: ape, posted: 2019-03-04 09:31:35
voir le code plus bas ......


Reply From User: ape, posted: 2019-03-04 11:04:01
i try to simplify the query but display doesn't work (identifier unknow).
This group for measure is local/EP/Site/variables/mesures/niveau

SELECT FULLNAME, FULLNAME ||'
' || FormatValue (Niveau.Currentvalue using '0.00') as "TOOLTIP",
GISLOCATION-LATITUDE, GISLOCATION-LONGITUDE,
FROM CGROUP
WHERE
FULLNAME LIKE '%EU%' AND GISLOCATIONSOURCE = 1


Reply From User: ape, posted: 2019-03-04 09:32:15
view code lower......


Reply From User: sbeadle, posted: 2019-03-04 10:17:16

Try testing your query in querypad (search in the help).
'
' || FormatValue (r.Niveau USING '0.00')
Quotes around

Add USING
What is r.Niveau - no field with this name exists
The JOIN links a point within the group


Reply From User: ape, posted: 2019-03-04 09:41:42
Sorry, i don't have seen that we can get a preview for the message..


Reply From User: ape, posted: 2019-03-04 10:03:50
SELECT g.Id as "Id", g.FullName as "FullName",g.FullName ||
|| FormatValue (r.Niveau '0.00') as"Tooltip",
g.GISLOCATION-LATITUDE as "GISLOCATION-LATITUDE", g.GISLOCATION-
LONGITUDE as "GISLOCATION-LONGITUDE",case
when r.Niveau 50 then (255 + cast( (100-r.Niveau)/100*2*255 as INT)*256)
end as "Foreground",255+256*255+256*256*255 as "Background", 0 as "Blink"
FROM CGROUP AS g left join CRandom as r on r.ParentGroupId = g.Id
WHERE g.FULLNAME LIKE 'EU.%'


Reply From User: sbeadle, posted: 2019-03-04 13:52:31
Your query is from the table CGroup (an object folder), but you are selecting a field (currentvalue) valid only on points, and with a table alias (Niveau) which does not exist. Is your point called Niveau and the top level group is EU?
Maybe try
`SELECT FULLNAME, FULLNAME ||'
' || FormatValue (p.Currentvalue using '0.00') as "TOOLTIP",
GISLOCATION-LATITUDE, GISLOCATION-LONGITUDE,
FROM CDBPoint p
WHERE
FULLNAME LIKE 'EU.%.Niveau' AND GISLOCATIONSOURCE = 1`


Reply From User: ape, posted: 2019-03-04 14:06:19
Ok i understand a little more...
What is "p." front of field currentvalue?
What is " p after CDBPoint?
I try this query but she doesn't work (unexpected identifier)

thank you for your patience ; i'm beginner and great opportunity comes with this software


Reply From User: ape, posted: 2019-03-05 16:02:19
It's OK!!!! so i can't to display 2 values on one tootlip..it's possible for


Reply From User: ape, posted: 2019-03-05 16:07:03
`SELECT FULLNAME, FULLNAME||'
' || Formatvalue (CurrentValueFormatted using '0.00') AS "TOOLTIP",
GISLOCATION-LATITUDE, GISLOCATION-LONGITUDE
FROM CDBPoint
Where fullname LIKE '%.Niveau%'`


Reply From User: sbeadle, posted: 2019-03-06 13:13:52
p is a table alias: https://www.sqlteaching.com/#!table_alias

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore