[Imported] Multiple Pick Actions from a single Button click?

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] Multiple Pick Actions from a single Button click?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-10-25 03:38 PM . Last Modified: ‎2023-05-03 12:39 AM

0 Likes
0
1206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-25 03:38 PM . Last Modified: ‎2023-05-03 12:39 AM

[Imported] Multiple Pick Actions from a single Button click?

>>Message imported from previous forum - Category:ClearSCADA Software<<
User: florian, originally posted: 2018-10-24 19:38:40 Id:193
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.

------------------

**_neilj:_**
**_I have 7 Crystal Reports to Export when the user clicks a button. However, a Button can only have one Pick Action method (which was how the CR Training Course did it), so I'm thinking of using Structured Text logic to call the Export method for each report.Can anyone give an example of the code required to declare each of the Crystal Report objects and call the Export method?_**

**_...or is there an easier way? (i.e. not using a script/logic)_**

--------------------

AWoodland:
Logic is probably best, less to worry about about what happens if your client connection goes down mid way through the process. Some example code:

PROGRAM GenerateReport
METHOD
Report1 AT %M(.Crystal Report 1.Export);
Report2 AT %M(.Crystal Report 2.Export);
END_METHOD

Report1();
Report2();

END_PROGRAM

What you want to do after all 7 are generated might make it somewhat easier to do in scripting...

----------------------------

**_neilj:_**
**_Thanks for the pointers Adam.The final code I created, with "Date From" and "Date To" values that all the Crystal Reports will use, is:_**

**_PROGRAM ExportReports_**
**_METHOD_**

**_Report_01 AT %M(.DV01 - Inflow Vol.Export) : DATE, DATE;_**
**_Report_02 AT %M(.DV02 - Total Inflow Vol.Export) : DATE, DATE;_**
**_Report_03 AT %M(.DV03 - Target Discharge Vol.Export) : DATE, DATE;_**
**_Report_04 AT %M(.DV04 - Actual Discharge Vol.Export) : DATE, DATE;_**
**_Report_05 AT %M(.DV05 - Discharge Vol Diff.Export) : DATE, DATE;_**
**_Report_06 AT %M(.DV06 - Discharge Vol Breach.Export) : DATE, DATE;_**

**_END_METHOD_**

**_VAR_**

**_start_date AT %M(...Report Start Date.CurrentValue) : DATE;_**

**_end_date AT %M(...Report End Date.CurrentValue) : DATE;_**

**_END_VAR_**

 

**_Report_01(start_date,end_date);_**
**_Report_02(start_date,end_date);_**
**_Report_03(start_date,end_date);_**
**_Report_04(start_date,end_date);_**
**_Report_05(start_date,end_date);_**
**_Report_06(start_date,end_date);_**

**_END_PROGRAM_**

-------------------

ejme:
Can you generate more than four crystal repots using logic?

I seem to have hit a limitation and can only successfully generate 4 reports in a structured text logic program, is there are reason for this?
Note: I am using ClearSCADA 2015 R2

-------------------

AWoodland:
How long do those four reports take to execute? If they take too long then anything else on the stack (they all get added at the same time) will be canned.

I think the time is 15 mins before they get cancelled

----------------

trantereng:
Did you get this ST program to work correctly? I am trying something similar - using an aggregate Control method to write a MODBUS register to multiple devices based on a button click.

But I am getting a compile error with my ST program?

Compile error: at line: 8, column: 9; unique expected

The program compiles and runs correctly when I declare and call a single method but not when I have multiple?


PROGRAM AlarmReset

METHOD


(*declare Alarm Reset Command Methods for Comap, PowerStore and Solar Inverters*)


COMAP_RST AT %M(BSS.STAT.Cmd_Alarm_Reset.Control.Control):BYTE;

6_E01_RST AT %M(BSS.6.E01.Cmd_Alarm_Reset.Control.Control):BYTE;

6_E02_RST AT %M(BSS.6.E02.Cmd_Alarm_Reset.Control.Control):BYTE;

1_E01_RST AT %M(SPS.1.E01.Cmd_Alarm_Reset.Control.Control):BYTE;

1_E02_RST AT %M(SPS.1.E02.Cmd_Alarm_Reset.Control.Control):BYTE;

2_E03_RST AT %M(SPS.2.E03.Cmd_Alarm_Reset.Control.Control):BYTE;

2_E04_RST AT %M(SPS.2.E04.Cmd_Alarm_Reset.Control.Control):BYTE;

3_E05_RST AT %M(SPS.3.E05.Cmd_Alarm_Reset.Control.Control):BYTE;

3_E06_RST AT %M(SPS.3.E06.Cmd_Alarm_Reset.Control.Control):BYTE;

4_E07_RST AT %M(SPS.4.E07.Cmd_Alarm_Reset.Control.Control):BYTE;

4_E08_RST AT %M(SPS.4.E08.Cmd_Alarm_Reset.Control.Control):BYTE;

5_E09_RST AT %M(SPS.5.E09.Cmd_Alarm_Reset.Control.Control):BYTE;

5_E10_RST AT %M(SPS.5.E10.Cmd_Alarm_Reset.Control.Control):BYTE;


(*declare Start Command Methods for PowerStore and Solar Inverters*)


6_E01_START AT %M(BSS.6.E01.Cmd_Start.Control.Control):BYTE;

6_E02_START AT %M(BSS.6.E02.Cmd_Start.Control.Control):BYTE;

1_E01_START AT %M(SPS.1.E01.Cmd_Start.Control.Control):BYTE;

1_E02_START AT %M(SPS.1.E02.Cmd_Start.Control.Control):BYTE;

2_E03_START AT %M(SPS.2.E03.Cmd_Start.Control.Control):BYTE;

2_E04_START AT %M(SPS.2.E04.Cmd_Start.Control.Control):BYTE;

3_E05_START AT %M(SPS.3.E05.Cmd_Start.Control.Control):BYTE;

3_E06_START AT %M(SPS.3.E06.Cmd_Start.Control.Control):BYTE;

4_E07_START AT %M(SPS.4.E07.Cmd_Start.Control.Control):BYTE;

4_E08_START AT %M(SPS.4.E08.Cmd_Start.Control.Control):BYTE;

5_E09_START AT %M(SPS.5.E09.Cmd_Start.Control.Control):BYTE;

5_E10_START AT %M(SPS.5.E10.Cmd_Start.Control.Control):BYTE;

 

END_METHOD


(*call Alarm Reset Methods for Comap, PowerStore and Solar Inverters with 500 ms delay between each method call*)

 

COMAP_RST(1);
SLEEP(500);
6_E01_RST(1);
SLEEP(500);
6_E02_RST(1);
SLEEP(500);
1_E01_RST(1);
SLEEP(500);
1_E02_RST(1);
SLEEP(500);
2_E03_RST(1);
SLEEP(500);
2_E04_RST(1);
SLEEP(500);
3_E05_RST(1);
SLEEP(500);
3_E06_RST(1);
SLEEP(500);
4_E07_RST(1);
SLEEP(500);
4_E08_RST(1);
SLEEP(500);
5_E09_RST(1);
SLEEP(500);
5_E10_RST(1);
SLEEP(500);

(*call Start Command Methods for PowerStore and Solar Inverters with 500 ms delay between each method call*)

6_E01_START(1);

 

SLEEP(500);

 

6_E02_START(1);

 

SLEEP(500);

 

1_E01_START(1);

 

SLEEP(500);

 

1_E02_START(1);

 

SLEEP(500);

 

2_E03_START(1);

 

SLEEP(500);

 

2_E04_START(1);

 

SLEEP(500);

 

3_E05_START(1);

 

SLEEP(500);

 

3_E06_START(1);

 

SLEEP(500);

 

4_E07_START(1);

 

SLEEP(500);

 

4_E08_START(1);

 

SLEEP(500);

 

5_E09_START(1);

 

SLEEP(500);

 

5_E10_START(1);

END_PROGRAM

-------------------------------

AWoodland:
It doesn't like the number as the first character of the method name, change that and it should compile.

The error message is perhaps unhelpful in this case 🙂

--------------------------

trantereng:
Ok awesome thanks very much!

 

 

 

 

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore