[Imported] Invalid Internal Alarm State!

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] Invalid Internal Alarm State!
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxureβ„’ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: β€Ž2019-11-06 09:38 AM . Last Modified: β€Ž2023-05-03 12:28 AM

0 Likes
1
1227
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2019-11-06 09:38 AM . Last Modified: β€Ž2023-05-03 12:28 AM

[Imported] Invalid Internal Alarm State!

>>Message imported from previous forum - Category:ClearSCADA Software<<
User: yasinnajib, originally posted: 2019-01-28 05:37:35 Id:354
Dear Friends,
Can you please tell me how I can interpret this alarm?
![]((see attachments below) a3/7t5lvo4qmjgu.jpg "")
Every time I acknowledge this alarm, the server crashes. I am unable to delete the template instance as this crashes the server.

Thanks in advance for your comments!

Attached file: (editor/a3/7t5lvo4qmjgu.jpg), ClearSCADA invalid state alarm.jpg File size: 174398

Attachments
Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: β€Ž2019-11-06 09:39 AM

0 Likes
0
1225
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2019-11-06 09:39 AM

>>Responses imported from previous forum


Reply From User: Omar_Gadallah, posted: 2019-01-28 11:07:52
Hello,

Have a look In: Server Configuration Database Configuration Severities

You have to define the same serverities used in your points as configured on your database projects.

 

 

 


Reply From User: yasinnajib, posted: 2019-01-28 12:01:28
[at]Omar_Gadallah Thank you for your kind reply. The severities match. 😞

 

Reply From User: BevanWeiss, posted: 2019-01-28 20:28:31
[at]yasinnajib I'd recommend that you raise this with your local Technical Support contact. They would be in the best position to assist with this.

I'm intrigued however, I'm not sure I've seen this 'State Alarm' before. And the Alarm State is Normal, so there doesn't appear to be an alarm on this object.
Can you please show an image of the alarm from the alarm banner?

Have you looked through the ClearSCADA log file to identify anything else about the exception?


Reply From User: yasinnajib, posted: 2019-01-29 02:07:54
[at]BevanWeiss Thank you for your support.
I've gone through the log file and sent it to Schneider as well.
They suggested the same fixes you and Omar have suggested. In the end, they agreed to remotely connect and check the error by themselves.
I'll post the prognosis, whatever it may be.


Reply From User: adamwoodland, posted: 2019-01-29 03:21:54
Can you post a screenshot of your Server Configuration - Database Configuration - Point State Alarms. Curious if anything is enabled there, I doubt it but may aswell check.

1,811,964,416 doesn't seem 'interesting'. If its some overflow then its a big one, hex is 0x6C006200 which just seems oddly convenient. The string 'lb' perhaps.

Your screenshot shows what I assume are metadata fields you've added ("String that represents the formatted value and quality"). How is that field manipulated? Assuming logic could it be writing to a property it shouldn't be able to (would be a ClearSCADA bug if so).

Maybe also, from the database bar right click and Locate in OPC Explorer, that should highlight the object in the OPC Explorer. Right click and choose Display Values and see if there is anything odd in there (or include a screenshot here). That field could be manipulates by the OPC-DA source (I'm not sure off the top of my head if that is one of the fields that is) and perhaps its dodgy data from the OPC source?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: β€Ž2019-11-06 09:39 AM

0 Likes
0
1226
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2019-11-06 09:39 AM

>>Responses imported from previous forum


Reply From User: Omar_Gadallah, posted: 2019-01-28 11:07:52
Hello,

Have a look In: Server Configuration Database Configuration Severities

You have to define the same serverities used in your points as configured on your database projects.

 

 

 


Reply From User: yasinnajib, posted: 2019-01-28 12:01:28
[at]Omar_Gadallah Thank you for your kind reply. The severities match. 😞

 

Reply From User: BevanWeiss, posted: 2019-01-28 20:28:31
[at]yasinnajib I'd recommend that you raise this with your local Technical Support contact. They would be in the best position to assist with this.

I'm intrigued however, I'm not sure I've seen this 'State Alarm' before. And the Alarm State is Normal, so there doesn't appear to be an alarm on this object.
Can you please show an image of the alarm from the alarm banner?

Have you looked through the ClearSCADA log file to identify anything else about the exception?


Reply From User: yasinnajib, posted: 2019-01-29 02:07:54
[at]BevanWeiss Thank you for your support.
I've gone through the log file and sent it to Schneider as well.
They suggested the same fixes you and Omar have suggested. In the end, they agreed to remotely connect and check the error by themselves.
I'll post the prognosis, whatever it may be.


Reply From User: adamwoodland, posted: 2019-01-29 03:21:54
Can you post a screenshot of your Server Configuration - Database Configuration - Point State Alarms. Curious if anything is enabled there, I doubt it but may aswell check.

1,811,964,416 doesn't seem 'interesting'. If its some overflow then its a big one, hex is 0x6C006200 which just seems oddly convenient. The string 'lb' perhaps.

Your screenshot shows what I assume are metadata fields you've added ("String that represents the formatted value and quality"). How is that field manipulated? Assuming logic could it be writing to a property it shouldn't be able to (would be a ClearSCADA bug if so).

Maybe also, from the database bar right click and Locate in OPC Explorer, that should highlight the object in the OPC Explorer. Right click and choose Display Values and see if there is anything odd in there (or include a screenshot here). That field could be manipulates by the OPC-DA source (I'm not sure off the top of my head if that is one of the fields that is) and perhaps its dodgy data from the OPC source?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore