[Imported] Duty Mode and a custom driver

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] Duty Mode and a custom driver
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
307
AndrewScott
Admiral AndrewScott
96
BevanWeiss
Spock BevanWeiss
90
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
37
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 12:09 PM . Last Modified: ‎2023-05-03 12:28 AM

0 Likes
1
819
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 12:09 PM . Last Modified: ‎2023-05-03 12:28 AM

[Imported] Duty Mode and a custom driver

>>Message imported from previous forum - Category:ClearSCADA Software<<
User: geoffpatton, originally posted: 2019-02-01 00:37:27 Id:357
I have a customer that encountered a Main - Main situation and their servers are in two locations so they lost the data from one when they synced.
So they enable Duty Mode and it worked fine for everything but a custom driver that we created. The object that we are using contains Tag Out information in it and that information was still lost. I am suspecting that since it is a custom driver ClearSCADA doesn't know what to do with it.

Just curious if anyone has encountered this before?

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 12:10 PM

0 Likes
0
818
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 12:10 PM

>>Responses imported from previous forum


Reply From User: adamwoodland, posted: 2019-02-01 04:03:04
What is this Tag Out info? Duty-Duty only cross-syncs a subset of the database data, what it doesn't cross sync is sourced from the Main only (i.e. like normal Main-Standby). Some advanced drivers can do current data if enabled but the DDK is using the simple driver architecture.

I couldn't find any information in the help, but I'm sure it'll be there somewhere. From internal dev notes, so may not be 100% accurate in the latest versions, the following are merged following a Main-Main with Duty-Duty enabled:

* Raw data
* Modified data
* Annotation
* Suppression
* Event journal
* Alarm summary
* Configuration changes

Current data for advanced driver points can optionally be merged (must be enabled on outstation).

Historic files (Crystal Reports etc.) are merged.

No other data is merged.

 

Reply From User: geoffpatton, posted: 2019-02-01 11:51:15
The Tag Out is Tagging Electrical Utility Circuit Breakers that are being worked on.
They do have a log of Tag Outs so they can rebuild it. Just not ideal.
Thanks For the info Adam.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 12:10 PM

0 Likes
0
819
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 12:10 PM

>>Responses imported from previous forum


Reply From User: adamwoodland, posted: 2019-02-01 04:03:04
What is this Tag Out info? Duty-Duty only cross-syncs a subset of the database data, what it doesn't cross sync is sourced from the Main only (i.e. like normal Main-Standby). Some advanced drivers can do current data if enabled but the DDK is using the simple driver architecture.

I couldn't find any information in the help, but I'm sure it'll be there somewhere. From internal dev notes, so may not be 100% accurate in the latest versions, the following are merged following a Main-Main with Duty-Duty enabled:

* Raw data
* Modified data
* Annotation
* Suppression
* Event journal
* Alarm summary
* Configuration changes

Current data for advanced driver points can optionally be merged (must be enabled on outstation).

Historic files (Crystal Reports etc.) are merged.

No other data is merged.

 

Reply From User: geoffpatton, posted: 2019-02-01 11:51:15
The Tag Out is Tagging Electrical Utility Circuit Breakers that are being worked on.
They do have a log of Tag Outs so they can rebuild it. Just not ideal.
Thanks For the info Adam.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of