Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

[Imported] Colour Coding Embedded List Rows Based on Name

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] Colour Coding Embedded List Rows Based on Name
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
sbeadle Champion
335
AndrewScott
AndrewScott
125
BevanWeiss
BevanWeiss
104
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
sbeadle
sbeadle Champion
Champion

Posted: ‎2019-11-26 01:45 PM . Last Modified: ‎2023-05-03 12:22 AM

0 Likes
1
1339
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-26 01:45 PM . Last Modified: ‎2023-05-03 12:22 AM

[Imported] Colour Coding Embedded List Rows Based on Name

>>Message imported from previous forum - Category:General Items<<
User: kvacola, originally posted: 2019-09-13 21:38:57 Id:513
I have an embedded list that has a SQL query bringing back a number of items like name, various values, datetime, etc. The embedded list relies on a custom function in the mimic script to fill the list. I need to colour code the background of the rows 3 different colours based on the following conditions: colour 1 if it is well_1, colour 2 if it is well_2, and white for all other wells.

Here is the code I have so far - it only codes the first column:

SQLString = _
" SELECT " & vbCrLf &_
" DISTINCT REPORTDATETIMEUTC AS ""_RECORDTIME"", " & vbCrLf &_
" CASE WELL WHEN 'Well_1' THEN 10001389 WHEN 'Well_2' THEN 15571864 ELSE 16777215 END AS ""{Background}"", CASE WELL WHEN 'Well_1' THEN 'Well_1' WHEN 'Well_2' THEN 'Well_2' ELSE WELL END AS ""Well Tested"", " & vbCrLf &_
" MODE AS ""Well Mode"", " & vbCrLf &_
" STARTDATETIMEUTC AS ""Start Test Time"", " & vbCrLf &_
" FORMATVALUE(HOURS using '#0.00') AS ""Test Flow Hours"", " & vbCrLf &_
" FORMATVALUE(VOLUME using '#0.00') as ""Volume on 24h"", " & vbCrLf &_
" TESTSTATUS AS ""Test Status"", " & vbCrLf &_
" COMMENT, " & vbCrLf &_
" ID AS ""_LOCN"" " & vbCrLf &_
" FROM " & vbCrLf &_
" TEST_HISTORY " & vbCrLf &_
" WHERE " & vbCrLf &_
" ""_RECORDTIME"" BETWEEN {TS '" & sStartDateTime & "' } AND {TS '" + sEndDateTime + "' } AND " & vbCrLf &_
" ""_LOCN"" = '" + iWell_Id + "' " & vbCrLf &_
" ORDER BY " & vbCrLf &_
" ""_RECORDTIME"" Desc " & vbCrLf

The CASE statement above works perfectly and we get that first column to colour code for those 2 wells. I've looked high and low through the documentation on how to do this, and all it gives me is how to do the columns. I've tried a second CASE on the next time with the following syntax:

CASE MODE WHEN WELL = 'Well_1' THEN 10001389 WHEN WELL = 'Well_2' THEN 15571864 ELSE 16777215 END AS "{Background2}", CASE MODE WHEN WELL = 'Well_1' THEN MODE WHEN WELL = 'Well_2' THEN MODE ELSE MODE AS "Well Mode"

But this doesn't work. The MODE isn't specific to a well name - in fact none of the rest of the columns are either.

Any ideas?

I've spend ages searching through Google ...

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
sbeadle Champion
Champion

Posted: ‎2019-11-26 01:45 PM

0 Likes
0
1338
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-26 01:45 PM

>>Responses imported from previous forum


Reply From User: BevanWeiss, posted: 2019-09-18 21:38:36
The part that is setting the background colour is this..
AS ""{Background}""

If you want to do this for another column, then you will need to use {Background1}, {Background2}, {Background3} etc... you can't use the same reference twice.

 

Reply From User: kvacola, posted: 2019-09-24 14:50:18
So I finally got this working. The resulting query required me to join a dataset where I store the integer code for the background. The resulting query looks something like this:

SQLString = _
" SELECT " & vbCrLf &_
" DISTINCT A.REPORTDATETIME AS ""_RECORDTIME"", " & vbCrLf &_
" B.BACKGROUND AS ""{Background1}"", " & vbCrLf &_
" A.WELL AS ""Well Tested"", " &vbCrLf &_
" B.BACKGROUND AS ""{Background2}"", " & vbCrLf &_
" FORMATVALUE(A.HOURS using '#0.00') AS ""Test Flow Hours"", " & vbCrLf &_
" B.BACKGROUND AS ""{Background3}"", " & vbCrLf &_
" FORMATVALUE(A.VOLUME using '#0.00') AS ""Volume on 24h"", " & vbCrLf &_
" B.BACKGROUND AS ""{Background4}"", " & vbCrLf &_
" A.ID AS ""_LOCN"" " & vbCrLf &_
" FROM "
" TEST_HISTORY AS A " & vbCrLf &_
" LEFT JOIN DSWELLTESTLIST AS B " & vbCrLf &_
" ON A.WELLID = B.SITEID " & vbCrLf &_
" AND A.WELLNUM = B.SITEINDEX " & vbCrLf &_
" WHERE ""_RECORDTIME"" BETWEEN {TS '" & sStartDateTime & "' } " & vbCrLf &_
" AND {TS '" + sEndDateTime + "' } AND " & vbCrLf &_
" ""_LOCN"" = '" + iSiteLocn + "' " & vbCrLf &_
" ORDER BY ""_RECORDTIME"" DESC " & vbCrLf

Which colours the rows perfectly, except when viewed in ViewX. This script is contained in a template and it works for one instance that colours perfectly according to the integer code. Everywhere else in the dsWellTestList the 'Background' is set to white (16777215). I even tried changing it to some other code like bright red (255), but it still shows black in WebX. I don't understand how it's working for one instance of the display and not for the others. I've triple-checked that when I right-click and go to the template it goes to the exact same one.

I have no idea how to get this working. Is this maybe a case to bump up to Schneider?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
sbeadle
sbeadle Champion
Champion

Posted: ‎2019-11-26 01:45 PM

0 Likes
0
1339
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-26 01:45 PM

>>Responses imported from previous forum


Reply From User: BevanWeiss, posted: 2019-09-18 21:38:36
The part that is setting the background colour is this..
AS ""{Background}""

If you want to do this for another column, then you will need to use {Background1}, {Background2}, {Background3} etc... you can't use the same reference twice.

 

Reply From User: kvacola, posted: 2019-09-24 14:50:18
So I finally got this working. The resulting query required me to join a dataset where I store the integer code for the background. The resulting query looks something like this:

SQLString = _
" SELECT " & vbCrLf &_
" DISTINCT A.REPORTDATETIME AS ""_RECORDTIME"", " & vbCrLf &_
" B.BACKGROUND AS ""{Background1}"", " & vbCrLf &_
" A.WELL AS ""Well Tested"", " &vbCrLf &_
" B.BACKGROUND AS ""{Background2}"", " & vbCrLf &_
" FORMATVALUE(A.HOURS using '#0.00') AS ""Test Flow Hours"", " & vbCrLf &_
" B.BACKGROUND AS ""{Background3}"", " & vbCrLf &_
" FORMATVALUE(A.VOLUME using '#0.00') AS ""Volume on 24h"", " & vbCrLf &_
" B.BACKGROUND AS ""{Background4}"", " & vbCrLf &_
" A.ID AS ""_LOCN"" " & vbCrLf &_
" FROM "
" TEST_HISTORY AS A " & vbCrLf &_
" LEFT JOIN DSWELLTESTLIST AS B " & vbCrLf &_
" ON A.WELLID = B.SITEID " & vbCrLf &_
" AND A.WELLNUM = B.SITEINDEX " & vbCrLf &_
" WHERE ""_RECORDTIME"" BETWEEN {TS '" & sStartDateTime & "' } " & vbCrLf &_
" AND {TS '" + sEndDateTime + "' } AND " & vbCrLf &_
" ""_LOCN"" = '" + iSiteLocn + "' " & vbCrLf &_
" ORDER BY ""_RECORDTIME"" DESC " & vbCrLf

Which colours the rows perfectly, except when viewed in ViewX. This script is contained in a template and it works for one instance that colours perfectly according to the integer code. Everywhere else in the dsWellTestList the 'Background' is set to white (16777215). I even tried changing it to some other code like bright red (255), but it still shows black in WebX. I don't understand how it's working for one instance of the display and not for the others. I've triple-checked that when I right-click and go to the template it goes to the exact same one.

I have no idea how to get this working. Is this maybe a case to bump up to Schneider?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore