[Imported] Call method Disable alarms

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] Call method Disable alarms
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
307
AndrewScott
Admiral AndrewScott
95
BevanWeiss
Spock BevanWeiss
89
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
36
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 02:12 AM . Last Modified: ‎2023-05-03 12:30 AM

0 Likes
1
1052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 02:12 AM . Last Modified: ‎2023-05-03 12:30 AM

[Imported] Call method Disable alarms

>>Message imported from previous forum - Category:Scripts and Tips<<
User: ROVSCADAENGINEER, originally posted: 2018-11-08 21:17:13 Id:314
I am trying to set up a code which inhibits ** (Disables alarms)** of an object folder based on the folder directory. I understand that you can disable alarms through creating a click button with pick action as method/Disable alarms and specifying that the object is relative with say for example location **SCX:////CTemplate/..**

I have created a logic timer which re-enables the alarms after a certain time and based on the logic I want the script to call the method based on the Boolean value of the inhibit alarm digital point. Is there a way you can call a method to a digital point? this would save time also. but I still need the folder to be relative so I can deploy the script and logic on several sites.

I understand that there is a server option for enable timed disable alarms, this is not what I want as this is a global server action. I just need it to run on a timer for specified folders.

the code is inserted below:

****PROGRAM NewStructuredTextProgram

VAR
InhibitAlarm AT %I(.inhibit alrm):BOOL;
END_VAR

METHOD

(*DisableAlarms AT %M(SCX:////CTemplate/MackayRC.AlarmDisabled):BOOL;*)

DIS AT %M(SCX:////CTemplate/MackayRC.Alarm Disabled):BOOL;

(* The path for the PSTNOS database item includes the PSTN aggregate aswell as the PromoteDialOut method. For methods that are associated with arguments rather than the database item, you need to define the method in this format:

AT %M(..):,, ;
*)

END_METHOD

IF (InhibitAlarm = 0) THEN
DIS(0);
ELSE
DIS(1);


END_IF;

END_PROGRAM****

I keep getting this problem with the code


Compile...

Method error: SCX:////CTemplate/MackayRC.Alarm Disabled not found

No matter how establish the location it does not want to establish the method in my method declaration section.

ANY help is appreciated with this script. I cannot seem to find any method call references to the disable alarm function.

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 02:13 AM

0 Likes
0
1051
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 02:13 AM

>>Responses imported from previous forum


Reply From User: adamwoodland, posted: 2018-11-08 22:21:17
Check the schema, i.e. https://localhost/schema/cgroup from the server itself may work, and that explains the method calls available to you.

In the logic you probably just want:

DIS AT %M(MackayRC.DisableAlarms):DINT;
ENA AT %M(MackayRC.EnableAlarms);

To disable the alarms call DIS() and to enable alarms call ENA()

You may need to pass a integer to DIS() depending on your server config for the disabling duration.


Reply From User: ROVSCADAENGINEER, posted: 2018-11-08 23:24:53
thanks adam! that worked. However I just need to do one more thing. I need to make sure that the script is disabling the alarms relevant to 2 steps up from the folder it is stored in. Do you know how I could implement this? it does not allow me to specify the folder directly like,

DIS AT %M(MackayRC.Sewer System. Avocado Ct SPS.DisableAlarms):DINT;

this is the folder directory yet it does not recognise the method strored here, I think this is because maybe the folder runs from a template, or what they call an aggregate. not to sure.

The purpose is to inhibit alarms just for that group. I am afraid this script will inhibit alarms for the whole group. is there a way to inhibit alarms for a group with relevant spacing to the scripts location?

 

Reply From User: ROVSCADAENGINEER, posted: 2018-11-08 23:42:54
I got it working. just not sure how to specify relative folders from the script file.


Reply From User: adamwoodland, posted: 2018-11-09 03:05:38
You use . to specify relative addressing, you probably want the following to go two levels up:

DIS AT %M(...DisableAlarms):DINT;


Reply From User: ROVSCADAENGINEER, posted: 2018-11-14 23:53:49
thanks Adam. your help is appreciated


Reply From User: ROVSCADAENGINEER, posted: 2018-12-18 00:56:48
So after running this code inserted here below, there were some issues with the server as when the code runs every (x) set amount of time due to this section of code at the end:


****IF (inhibitalrms = 0) THEN
ENA();
ELSE
DIS(1);
END_IF;****

This resulted in a event logging storm as it was actuating the enable alarms method constantly with every time the code ran. What I am thinking may work as a way around this would be to write the code so that it only actuates the call method on a state change from high to low on the digital point. We ended up using clear SCADA's built in timer on the server settings for alarm inhibit options. the interface is not as flash but it still works.

I hope this prevents anyone having the same issue and maybe they make the code better! as this can be used for interactive interfaces like so! if you find a way to prevent this let me know!

...![]((see attachments below) pz/syjebt2vwypn.png "")

 

****
The Final code is here below****

PROGRAM NewStructuredTextProgram

METHOD


DIS AT %M(Test mimics.Mitch latch logic test.DisableAlarms):BOOL;
ENA AT %M(Test mimics.Mitch latch logic test.EnableAlarms);


END_METHOD

VAR
Inhibitalarmstime AT %I(.Inhibit alarms time) : TIME;
Timeinhibited AT %M(.Time inhibited) : TIME;
inhibitalrm AT %I(.inhibit alrm) : BOOL;
inhibitalrms AT %M(.inhibit alrm) : BOOL;
END_VAR

(*This section compiles the blocks that are going to be used in building the logic program*)
VAR
TIMER : TON;
LATCH : SR;
RISETRIGGER : R_TRIG;
FALLTRIGGER : F_TRIG;
END_VAR

(*This section classifies the false state for each block allowing it
to be called later on in functions, it may be only necessery for the
false functions of blocks where readable outputs are required in order
for the code to work propperly*)
VAR
FALLTRIGGER_ENO : BOOL := FALSE;
RISETRIGGER_ENO : BOOL := FALSE;
TimeToReal_ENO : BOOL := FALSE;
TimeToReal : REAL;
MinToMilliseconds_ENO : BOOL := FALSE;
MinToMilliseconds : REAL;
OperatorMillisecondsToTime_ENO : BOOL := FALSE;
OperatorMillisecondsToTime : TIME;
TIMER_ENO : BOOL := FALSE;
LATCH_ENO : BOOL := FALSE;
ElapsedTimeToReal_ENO : BOOL := FALSE;
ElapsedTimeToReal : REAL;
ETmsToSeconds_ENO : BOOL := FALSE;
ETmsToSeconds : REAL;
ConvertedETtoTime_ENO : BOOL := FALSE;
ConvertedETtoTime : TIME;
END_VAR

(*ESTABLISHING INPUTS TO RISE AND FALL TRIGGERS FROM OPERATOR BUTTON*)
FALLTRIGGER( CLK := inhibitalrm, ENO = FALLTRIGGER_ENO );
RISETRIGGER( CLK := inhibitalrm, ENO = RISETRIGGER_ENO );

(*SPECIFYING THE INPUTS AND OUTPUTS OF THE LATCH FOR ALARM SETTINGS*)
LATCH( S1 := RISETRIGGER.Q, R := OR( TIMER.Q, FALLTRIGGER.Q ), ENO = LATCH_ENO );

(*Converts the Operators input of Miutes to milliseconds through Time to Real, convert then back to time. *)
TimeToReal := TIME_TO_REAL( IN := Inhibitalarmstime, ENO = TimeToReal_ENO );
MinToMilliseconds := MUL( IN1 := TimeToReal, IN2 := 60000, ENO = MinToMilliseconds_ENO );
OperatorMillisecondsToTime := REAL_TO_TIME( IN := MinToMilliseconds, ENO = OperatorMillisecondsToTime_ENO );

(*Establishing the Timer Block with correct time format*)
TIMER( IN := inhibitalrm, PT := OperatorMillisecondsToTime, ENO = TIMER_ENO );

(*Converts the output time of the elapsed time into correct units Seconds for operator*)
ElapsedTimeToReal := TIME_TO_REAL( IN := TIMER.ET, ENO = ElapsedTimeToReal_ENO );
ETmsToSeconds := DIV( IN1 := ElapsedTimeToReal, IN2 := 1000, ENO = ETmsToSeconds_ENO );
ConvertedETtoTime := REAL_TO_TIME( IN := ETmsToSeconds, ENO = ConvertedETtoTime_ENO );

(*Calls the inhibit alrm digital point as the LATCH output*)
IF LATCH_ENO THEN
inhibitalrms := LATCH.Q1;
END_IF;

(*Calls the converted ET output as the digital point Timeinhibited*)
IF ConvertedETtoTime_ENO THEN
Timeinhibited := ConvertedETtoTime;
END_IF;


IF (inhibitalrms = 0) THEN
ENA();
ELSE
DIS(1);
END_IF;

END_PROGRAM

 


Attached file: (editor/pz/syjebt2vwypn.png), inhibit alarms option.PNG File size: 2020


Reply From User: geoffpatton, posted: 2018-12-18 01:23:04
You could have used the Alarm State of the group you are disabling.
GroupName.AlarmState

IF (inhibitalrms = 0) and (GroupAlarmState = 1) THEN
ENA();
END_IF

IF (inhibitalrms = 1) and (GroupAlarmState 1) THEN
DIS(1);
END_IF;

END_PROGRAM


Reply From User: BevanWeiss, posted: 2019-01-03 22:41:16
I would recommend not having just logic re-enabling the alarms if you can avoid it, but instead using the option to Disable Alarms to provide a duration of the alarm disablement.
This way the alarm will automatically be re-enabled at the appropriate time, even if your logic stops working.

It does look although what you are kind of trying to do is a Consequential Alarm Suppression however, so it might be worth you looking more into how this is configured in ClearSCADA.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 02:13 AM

0 Likes
0
1052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 02:13 AM

>>Responses imported from previous forum


Reply From User: adamwoodland, posted: 2018-11-08 22:21:17
Check the schema, i.e. https://localhost/schema/cgroup from the server itself may work, and that explains the method calls available to you.

In the logic you probably just want:

DIS AT %M(MackayRC.DisableAlarms):DINT;
ENA AT %M(MackayRC.EnableAlarms);

To disable the alarms call DIS() and to enable alarms call ENA()

You may need to pass a integer to DIS() depending on your server config for the disabling duration.


Reply From User: ROVSCADAENGINEER, posted: 2018-11-08 23:24:53
thanks adam! that worked. However I just need to do one more thing. I need to make sure that the script is disabling the alarms relevant to 2 steps up from the folder it is stored in. Do you know how I could implement this? it does not allow me to specify the folder directly like,

DIS AT %M(MackayRC.Sewer System. Avocado Ct SPS.DisableAlarms):DINT;

this is the folder directory yet it does not recognise the method strored here, I think this is because maybe the folder runs from a template, or what they call an aggregate. not to sure.

The purpose is to inhibit alarms just for that group. I am afraid this script will inhibit alarms for the whole group. is there a way to inhibit alarms for a group with relevant spacing to the scripts location?

 

Reply From User: ROVSCADAENGINEER, posted: 2018-11-08 23:42:54
I got it working. just not sure how to specify relative folders from the script file.


Reply From User: adamwoodland, posted: 2018-11-09 03:05:38
You use . to specify relative addressing, you probably want the following to go two levels up:

DIS AT %M(...DisableAlarms):DINT;


Reply From User: ROVSCADAENGINEER, posted: 2018-11-14 23:53:49
thanks Adam. your help is appreciated


Reply From User: ROVSCADAENGINEER, posted: 2018-12-18 00:56:48
So after running this code inserted here below, there were some issues with the server as when the code runs every (x) set amount of time due to this section of code at the end:


****IF (inhibitalrms = 0) THEN
ENA();
ELSE
DIS(1);
END_IF;****

This resulted in a event logging storm as it was actuating the enable alarms method constantly with every time the code ran. What I am thinking may work as a way around this would be to write the code so that it only actuates the call method on a state change from high to low on the digital point. We ended up using clear SCADA's built in timer on the server settings for alarm inhibit options. the interface is not as flash but it still works.

I hope this prevents anyone having the same issue and maybe they make the code better! as this can be used for interactive interfaces like so! if you find a way to prevent this let me know!

...![]((see attachments below) pz/syjebt2vwypn.png "")

 

****
The Final code is here below****

PROGRAM NewStructuredTextProgram

METHOD


DIS AT %M(Test mimics.Mitch latch logic test.DisableAlarms):BOOL;
ENA AT %M(Test mimics.Mitch latch logic test.EnableAlarms);


END_METHOD

VAR
Inhibitalarmstime AT %I(.Inhibit alarms time) : TIME;
Timeinhibited AT %M(.Time inhibited) : TIME;
inhibitalrm AT %I(.inhibit alrm) : BOOL;
inhibitalrms AT %M(.inhibit alrm) : BOOL;
END_VAR

(*This section compiles the blocks that are going to be used in building the logic program*)
VAR
TIMER : TON;
LATCH : SR;
RISETRIGGER : R_TRIG;
FALLTRIGGER : F_TRIG;
END_VAR

(*This section classifies the false state for each block allowing it
to be called later on in functions, it may be only necessery for the
false functions of blocks where readable outputs are required in order
for the code to work propperly*)
VAR
FALLTRIGGER_ENO : BOOL := FALSE;
RISETRIGGER_ENO : BOOL := FALSE;
TimeToReal_ENO : BOOL := FALSE;
TimeToReal : REAL;
MinToMilliseconds_ENO : BOOL := FALSE;
MinToMilliseconds : REAL;
OperatorMillisecondsToTime_ENO : BOOL := FALSE;
OperatorMillisecondsToTime : TIME;
TIMER_ENO : BOOL := FALSE;
LATCH_ENO : BOOL := FALSE;
ElapsedTimeToReal_ENO : BOOL := FALSE;
ElapsedTimeToReal : REAL;
ETmsToSeconds_ENO : BOOL := FALSE;
ETmsToSeconds : REAL;
ConvertedETtoTime_ENO : BOOL := FALSE;
ConvertedETtoTime : TIME;
END_VAR

(*ESTABLISHING INPUTS TO RISE AND FALL TRIGGERS FROM OPERATOR BUTTON*)
FALLTRIGGER( CLK := inhibitalrm, ENO = FALLTRIGGER_ENO );
RISETRIGGER( CLK := inhibitalrm, ENO = RISETRIGGER_ENO );

(*SPECIFYING THE INPUTS AND OUTPUTS OF THE LATCH FOR ALARM SETTINGS*)
LATCH( S1 := RISETRIGGER.Q, R := OR( TIMER.Q, FALLTRIGGER.Q ), ENO = LATCH_ENO );

(*Converts the Operators input of Miutes to milliseconds through Time to Real, convert then back to time. *)
TimeToReal := TIME_TO_REAL( IN := Inhibitalarmstime, ENO = TimeToReal_ENO );
MinToMilliseconds := MUL( IN1 := TimeToReal, IN2 := 60000, ENO = MinToMilliseconds_ENO );
OperatorMillisecondsToTime := REAL_TO_TIME( IN := MinToMilliseconds, ENO = OperatorMillisecondsToTime_ENO );

(*Establishing the Timer Block with correct time format*)
TIMER( IN := inhibitalrm, PT := OperatorMillisecondsToTime, ENO = TIMER_ENO );

(*Converts the output time of the elapsed time into correct units Seconds for operator*)
ElapsedTimeToReal := TIME_TO_REAL( IN := TIMER.ET, ENO = ElapsedTimeToReal_ENO );
ETmsToSeconds := DIV( IN1 := ElapsedTimeToReal, IN2 := 1000, ENO = ETmsToSeconds_ENO );
ConvertedETtoTime := REAL_TO_TIME( IN := ETmsToSeconds, ENO = ConvertedETtoTime_ENO );

(*Calls the inhibit alrm digital point as the LATCH output*)
IF LATCH_ENO THEN
inhibitalrms := LATCH.Q1;
END_IF;

(*Calls the converted ET output as the digital point Timeinhibited*)
IF ConvertedETtoTime_ENO THEN
Timeinhibited := ConvertedETtoTime;
END_IF;


IF (inhibitalrms = 0) THEN
ENA();
ELSE
DIS(1);
END_IF;

END_PROGRAM

 


Attached file: (editor/pz/syjebt2vwypn.png), inhibit alarms option.PNG File size: 2020


Reply From User: geoffpatton, posted: 2018-12-18 01:23:04
You could have used the Alarm State of the group you are disabling.
GroupName.AlarmState

IF (inhibitalrms = 0) and (GroupAlarmState = 1) THEN
ENA();
END_IF

IF (inhibitalrms = 1) and (GroupAlarmState 1) THEN
DIS(1);
END_IF;

END_PROGRAM


Reply From User: BevanWeiss, posted: 2019-01-03 22:41:16
I would recommend not having just logic re-enabling the alarms if you can avoid it, but instead using the option to Disable Alarms to provide a duration of the alarm disablement.
This way the alarm will automatically be re-enabled at the appropriate time, even if your logic stops working.

It does look although what you are kind of trying to do is a Consequential Alarm Suppression however, so it might be worth you looking more into how this is configured in ClearSCADA.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of