Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

[Imported] Absolute date/time query format

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] Absolute date/time query format
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
sbeadle Champion
335
AndrewScott
AndrewScott
125
BevanWeiss
BevanWeiss
104
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
sbeadle
sbeadle Champion
Champion

Posted: ‎2019-11-06 02:46 PM . Last Modified: ‎2023-05-03 12:26 AM

0 Likes
1
2182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 02:46 PM . Last Modified: ‎2023-05-03 12:26 AM

[Imported] Absolute date/time query format

>>Message imported from previous forum - Category:Scripts and Tips<<
User: JayB, originally posted: 2019-04-03 13:25:55 Id:393
I can write queries with a WHERE clause that uses the relative OPC date/time format (e.g. {OPC 'MO-1MO'}) and an absolute data format (e.g. {D '2019-03-11'}), but I can't figure out how to specify an exact date PLUS time format e.g. something like '2019-03-11 12:00:00'. What is that syntax? And is there a Help page somewhere that explains it, as I haven't found any examples online. Thanks.

Attached file: (editor/5n/jtdczfry5n5q.png), image.png File size: 1080

Attachments
Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
sbeadle Champion
Champion

Posted: ‎2019-11-06 02:47 PM

0 Likes
0
2181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 02:47 PM

>>Responses imported from previous forum


Reply From User: hardin4019, posted: 2019-04-03 20:20:11
I pulled up a historic list for a point and set the time range to "specific time" and then looked at the filter and saw ("~Time" BETWEEN TIMESTAMP '2019-04-03 01:00:00' AND TIMESTAMP '2019-04-04 01:00:00') so hopefully that helps.


Reply From User: JayB, posted: 2019-04-03 20:31:43
Great idea. I just tried exactly that syntax and it worked. Thanks for your help!


Reply From User: hardin4019, posted: 2019-04-03 22:15:26
No problem! Glad my method works!


Reply From User: jozzburn, posted: 2019-07-16 18:43:41
I'm doing the same. However, I want to put the query in the animation for the list and pull the between times from two internal time points. The working static query is

SELECT TOP( 1000 )
*
FROM
HISHOURLYAVERAGE
WHERE
( SUMMARY = 'Average' ) AND ( ID = 13027 ) AND ( "HISHOURLYAVERAGE"."Time" BETWEEN TIMESTAMP '2019-06-01 07:00:00' AND TIMESTAMP '2019-07-01 07:00:00' )
ORDER BY
"Id" ASC

The working animation generated for this is

'SELECT TOP( 1000 ) * FROM HISHOURLYAVERAGE WHERE ( SUMMARY = ''Average'' ) AND ( ID = 13027 ) AND ( "HISHOURLYAVERAGE"."Time" BETWEEN TIMESTAMP ''2019-06-01 07:00:00'' AND TIMESTAMP ''2019-07-01 07:00:00'' ) ORDER BY "Id" ASC'

How do i tell it to pull start from
"....~Config 1.Reports.~Date Parameters.Start.CurrentValue"

Tried replacing ''2019-06-01 07:00:00'' with "....~Config 1.Reports.~Date Parameters.Start.CurrentValue" and {OPC "....~Config 1.Reports.~Date Parameters.Start.CurrentValue"}

I think i'm close. Any ideas?


Reply From User: BevanWeiss, posted: 2019-07-16 23:45:03
This will get confusing with quotes..

So. You need to substitute the current static time (i.e. every BETWEEN the double single quotes) with a similarly FORMATted string. And of course because it's another string now, you'll need to 'add' it to the existing string.

i.e.
'SELECT blah blah ' +
'FROM blah blah ' +
'WHERE Time BETWEEN ' +
'TIMESTAMP ''' + FORMAT( TimeFormatRequired, "~Config.Reports.~Date Parameters.Start.CurrentValue") + '''' ' +
'AND TIMESTAMP ''' + FORMAT( TimeFormatRequired, "~Config.Reports.~Date Parameters.End.CurrentValue") + ''''

 

Reply From User: jozzburn, posted: 2019-07-17 16:40:56
Ahhh. Now i realize i needed to be closing the text with the ' , getting my values like i would normally do in an expression, then starting the text construction again. I was trying to get values from inside the ' '. Thanks for the help!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
sbeadle
sbeadle Champion
Champion

Posted: ‎2019-11-06 02:47 PM

0 Likes
0
2182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 02:47 PM

>>Responses imported from previous forum


Reply From User: hardin4019, posted: 2019-04-03 20:20:11
I pulled up a historic list for a point and set the time range to "specific time" and then looked at the filter and saw ("~Time" BETWEEN TIMESTAMP '2019-04-03 01:00:00' AND TIMESTAMP '2019-04-04 01:00:00') so hopefully that helps.


Reply From User: JayB, posted: 2019-04-03 20:31:43
Great idea. I just tried exactly that syntax and it worked. Thanks for your help!


Reply From User: hardin4019, posted: 2019-04-03 22:15:26
No problem! Glad my method works!


Reply From User: jozzburn, posted: 2019-07-16 18:43:41
I'm doing the same. However, I want to put the query in the animation for the list and pull the between times from two internal time points. The working static query is

SELECT TOP( 1000 )
*
FROM
HISHOURLYAVERAGE
WHERE
( SUMMARY = 'Average' ) AND ( ID = 13027 ) AND ( "HISHOURLYAVERAGE"."Time" BETWEEN TIMESTAMP '2019-06-01 07:00:00' AND TIMESTAMP '2019-07-01 07:00:00' )
ORDER BY
"Id" ASC

The working animation generated for this is

'SELECT TOP( 1000 ) * FROM HISHOURLYAVERAGE WHERE ( SUMMARY = ''Average'' ) AND ( ID = 13027 ) AND ( "HISHOURLYAVERAGE"."Time" BETWEEN TIMESTAMP ''2019-06-01 07:00:00'' AND TIMESTAMP ''2019-07-01 07:00:00'' ) ORDER BY "Id" ASC'

How do i tell it to pull start from
"....~Config 1.Reports.~Date Parameters.Start.CurrentValue"

Tried replacing ''2019-06-01 07:00:00'' with "....~Config 1.Reports.~Date Parameters.Start.CurrentValue" and {OPC "....~Config 1.Reports.~Date Parameters.Start.CurrentValue"}

I think i'm close. Any ideas?


Reply From User: BevanWeiss, posted: 2019-07-16 23:45:03
This will get confusing with quotes..

So. You need to substitute the current static time (i.e. every BETWEEN the double single quotes) with a similarly FORMATted string. And of course because it's another string now, you'll need to 'add' it to the existing string.

i.e.
'SELECT blah blah ' +
'FROM blah blah ' +
'WHERE Time BETWEEN ' +
'TIMESTAMP ''' + FORMAT( TimeFormatRequired, "~Config.Reports.~Date Parameters.Start.CurrentValue") + '''' ' +
'AND TIMESTAMP ''' + FORMAT( TimeFormatRequired, "~Config.Reports.~Date Parameters.End.CurrentValue") + ''''

 

Reply From User: jozzburn, posted: 2019-07-17 16:40:56
Ahhh. Now i realize i needed to be closing the text with the ' , getting my values like i would normally do in an expression, then starting the text construction again. I was trying to get values from inside the ' '. Thanks for the help!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore